And now I have to add my favorite rant: I hope you
discussed at some length the fact that every control loop
needs an auditor, a second, independent measurement device
that is not involved in closing the loop. The reason for
this is that once you have closed the loop, you cannot use
that measurement to know anything about what's really going
on in the process over the long term. If the controller is
functioning properly, the measurement (at the controller)
will be forced to track the setpoint no matter what is
actually happening in the real world. Providing such
auditors used to be standard practice in the process control
industry until about 15 years ago when engineers lost
control of their plants and bean counters started
"cost-reducing" everything. In fact, we used to have RTDs
designed with that in mind: one RTD to control and one to
audit in the same probe.
Also, of course, we had the clever E&I technicians.
Operators would complain that the controller measurements
weren't the same as the auditor measurements, so some dork
with a 12-inch screwdriver would "re-calibrate" the
RTD-to-current-loop converters to make the auditors "read
right."