Cable length using r1 and r2

Integrator741

Jun 16, 2013
125
Joined
Jun 16, 2013
Messages
125
Hi. How do I calculate cable length using csa and r1 and r2 reading. (On a dead circuit). Cuz I am trying to calculate voltage drop on elv cable.

So I got a 1.5 cable that will have 24v going through it to 100w device. How do I get voltage drop from this information?

Thanks.
 
Last edited:

BobK

Jan 5, 2010
7,682
Joined
Jan 5, 2010
Messages
7,682
Voltage does not go through a cable, current goes through a cable.

So, first calculate the current: If it is 100W at 24V the current is 100 / 24 = 4.16A.

Next calculate the resistance: For the given size of wire, you can find the resistance / length. For example, 22AWG wire has 0.053 Ohms / meter. Multiply that figure by the length of the wire to get resistance.

Finally, use Ohm's law to calculate the voltage drop: V = I * R

Bob
 

Integrator741

Jun 16, 2013
125
Joined
Jun 16, 2013
Messages
125
Voltage does not go through a cable, current goes through a cable.

So, first calculate the current: If it is 100W at 24V the current is 100 / 24 = 4.16A.

Next calculate the resistance: For the given size of wire, you can find the resistance / length. For example, 22AWG wire has 0.053 Ohms / meter. Multiply that figure by the length of the wire to get resistance.

Finally, use Ohm's law to calculate the voltage drop: V = I * R

Bob
Thanks. Is there a formula to calculate cable length?
 

Minder

Apr 24, 2015
3,478
Joined
Apr 24, 2015
Messages
3,478
Short circuit the destination end and measure resistance at the source end.:confused:
Or use one of the cable charts for your cable.
M.
 

Integrator741

Jun 16, 2013
125
Joined
Jun 16, 2013
Messages
125
Short circuit the destination end and measure resistance at the source end.:confused:
Or use one of the cable charts for your cable.
M.
I did that. I got 0.55 ohm. How would I use that to calculate the length? Also quick question. If I got an ELV circuit (24v) and my equipment takes 100w I get current of 4.16A. Does that mean Extra Low Voltage circuit could actually kill me?
 

BobK

Jan 5, 2010
7,682
Joined
Jan 5, 2010
Messages
7,682
I thought you were trying to calculate voltage drop. If you already know the resistance and the current, why do you need the length?

Anyway, calculating the length is elenentary scool arithmetic.

Divide the resistace of the cable by the resistance per meter of the cable, which you can get from a chart.

Bob
 