Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is connected
to the string and the switches will interrupt the 24V when pressed in and
Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to the
conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks
 
J

Jim

Jan 1, 1970
0
Tube Audio said:
I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks

Typical control cable is 600V. When we used to test the cabling for new
control circuits (I was with a large electrical utility), we always
tested them at 1000VDC. Usually resistance testers ('Meggers') are DC
and 600VAC is pretty close to 1000V peak, so that was our logic.
Certainly a 600V control cable should accept 500VDC and still show
several Megohms, even if it is very old and in in a poor environment.
New cable would be 200+.
 
G

George Vest

Jan 1, 1970
0
Tube Audio said:
Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is
connected to the string and the switches will interrupt the 24V when
pressed in and Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to
the conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why.
The other end of the Hi Pot tester will connect to the conduit.

Thanks

What makes you think it is a short ?

800M is a long run at 24V. If the circuit is holding a contactor in, small
voltage fluctuations will drop it out.

George.
 
A

Archimedes' Lever

Jan 1, 1970
0
Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is connected
to the string and the switches will interrupt the 24V when pressed in and
Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to the
conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks
If normal operation is causing a short either by an arc of not, then a
"hi pot" tester is CERTAINLY going to fire at the short location. You
STILL have the problem of determining WHERE to break in insulation is at.

In an 800 ft run, I cannot imagine that it would be a single piece, so
there has to be break points.

Find one. Preferrably near the center of the run. Open ALL conductors
at that break point. Test both segments. Test each conductor separately.
That will narrow things even better. You should now know which end of
the cable it is on (which segment fails). Go to that segment, and make
another break point disconnection and test. Leave the good segment OUT
of your test runs, and when you find another segment good, leave it out
of all further testing.

After these two breaks and two tests, you should have the fault narrowed
down to a 25% long segment of the whole run.
 
What makes you think it is a short ?

800M is a long run at 24V. If the circuit is holding a contactor in, small
voltage fluctuations will drop it out.

George.


Even with pure silver wire, 800ft pushed by only 24 V will have
significant loss at the other end. Proportionally speaking. That is why
we use HV across long spans. Less loss after conversion.

Could he not use DC-to-DC converters at each load node (or specific
number of feet or loads)that converts 15-14VDC to 24 VDC? Then, he would
have the exact same voltage at each "load node".

Then, we could bluetooth each node and he could operate them all
independently via remote console. tee hee hee :)
 
N

nospam

Jan 1, 1970
0
What makes you think it is a short ?
800M is a long run at 24V. If the circuit is holding a contactor in, small
voltage fluctuations will drop it out.

800m of 18 awg is 17 or 18 ohms. Marginal for a moderately large contactor
maybe but if it was so marginal that voltage fluctuations drop it out he
would never pull it in in the first place.

--
 
B

Bob AZ

Jan 1, 1970
0
I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. �The
other end of the Hi Pot tester will connect to the conduit.

Thanks

After reading the posts I would like to know the current and voltage
ratings of the contactor coil.

18 guage is small for 800 feet with the usual current requirements for
a contactor. With #18 wire and 24VDC you can sink only 1.33 Amps. And
for practical purposes your contactor current is limited to .13 amps.
More than this the voltage across ther contactor coil will be too low
for reliable operation. Not enough current for the contactor.

If you can't replace the wire with 16 or 14 use a transistor as a
driver/switch at the contactor to make the 18 wire a signal conductor
instead of a switch leg. Use the 24VDC for Vcc on the transistor.
There are also Solid State Switch packages for this.

Most technicians should be able to wire this up with no problems with
the switches, connectors and wire. Your switches do need to be
selected for this. Are your switches rated for DC?

Your momentary "short" in this case may be a result of the component
activity consisting of the L of the coil and the RC of the wire and
the conduit. Possibly caused by spiking from an external source. A
diode across the contactor coil will minimize this. 800 feet is a long
way for #18 wire.

My best philosophy at 12:23 AM!

Bob AZ
 
P

PeterD

Jan 1, 1970
0
^^^ ^^^^
800m of 18 awg is 17 or 18 ohms. Marginal for a moderately large contactor
maybe but if it was so marginal that voltage fluctuations drop it out he
would never pull it in in the first place.

800 FEET, not meters...

5.21 ohms total loop resistance. A drop of about 1/2 volts if the coil
drew 100 MA, which it may. Not significant.
 
T

Tim Williams

Jan 1, 1970
0
I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

Get one of those frickin-hot pulse generators from John Larkin and
scope the result. Where it arcs over (from the high voltage impulse)
will reflect voltage back. ;-)

Tim
 
A

Andy

Jan 1, 1970
0
Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is connected
to the string and the switches will interrupt the 24V when pressed in and
Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to the
conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks

Before i would start chasing down a possible short, I would verify
that my coil is getting enough current to stay in, and that my 24VDC
supply is not overloaded. Do you have other loads on the DC supply?
If you have other loads on this supply, especially intermittent ones,
that could be enough to cause the coil to drop out.
1. I would force all other loads on the DC supply to be on, and then
see how the coil in question behaves.
2. If the supply is ruled out, then I would pull the cable off of the
coil and measure the resistance of the cable, including all switches
(bypass the supply). If the supply voltage divided by the system
resistance is marginal, that would be a good place for a problem.
3. If this isn't the problem... 800 feet of conduit will expand in the
sun. And if you have a problem which shows up or goes away with
temperature, the expanding conduit might be pulling on a loose
connection.
4. Then I would check for the short.

Good luck,
Andy
 
F

f825_633

Jan 1, 1970
0
Tube said:
Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is connected
to the string and the switches will interrupt the 24V when pressed in and
Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to the
conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks
Having read all the replies and good suggestions, what ever
the fault is, intermittent ones are the hardest to find.

Assuming all the cable is the same age, the cable is in
conduit, why not simply buy a reel of cable and replace all
of it, not more than a couple of hours work to pull in a new
cable with the old one as a draw wire at the lengths you
describe and then you'd have solved the problem, made your
insurance company happy that you have serviced and renewed
the safety system and saved a lot of time and effort. Not to
mention that in this condition you really shouldn't be using
the equipment the safety system is there to isolate, H&S
will be all over you if they knew - they wont care that the
fault actually is rendering the system safe, they will only
care that you have a fault with it.
 
B

bob

Jan 1, 1970
0
Tube said:
Hello

I have an Industrial Installation of a string of about 20 SPST Emergency
Stop Switches in series, They are wired Normally Closed. 24VDC is connected
to the string and the switches will interrupt the 24V when pressed in and
Emergency.

The wire is 18 GA stranded and the total length of the string is about 800
feet.

The wire runs in conduit.

I believe I have an intermittent short to the conduit, usually the short
occurs just momentarily so troubleshooting is difficult.

I was thinking of Hi Potting the Switch String. I was going to disconnect
each end of the string and Hi Pot the cable run along with the installed E
Stop Switches. To verify if some part of the conductor is very close to the
conduit.

I believe the wire is rated at around 600V.

The question is what Voltage should I set the Hi Pot tester to and why. The
other end of the Hi Pot tester will connect to the conduit.

Thanks
I am a firm believer in cause and effect. When is the fault happening?
day night? machines on? machines off? cold? hot?

If the switches are closed, who's to say you don't have a intermittent
switch contact from temp extremes or vibration? Or a loose wire to
switch contact? Corrosion from water damage or humidity?

I would ohm all the switches for closed contract resistance.
and check and re torque all switch to wire connections.


bob