Mark said:
Sorry about the blue (live) confusion folks, I meant to type neutral but in
my haste to fix the problem I typed it and didn't check afterwards.
The wiring and the element has been fine for 15 years.
I've just reconnected it again and will check in a few days to what it's
like. It never blows the fuse.
******************************************
Good Morning Mark,
You may have a short between the heater element
and Ground on the neutral side, which may be providing a
ground path for some other device on your overall wiring
layout, or, possibly the heater is not grounded, and
there is return to ground path for something else back
through the water heater circuit.
I have seen this in the past when the ground on the main
panel was bad, but the ground through the water pipes
was good, and all the neutral currents went through the
path of least resistance back to ground, the hot water
heater wiring.
Sneak ground paths, and overloaded neutrals are hard
to find, and a very common problem, especially on older wiring systems.
Check this with an Ohmeter, ( with the heater element
disconnected, ) read between the neutral side, ( Blue )
wire and Ground. If you find a short, ( unless the Neutral
is grounded deliberatly at this point ) This is your problem.
But you have another problem that you are not seeing,
and that the Neutral return to ground either at your
main sevice panel, or at your meter is open.
This must be a very small hot water heater, as all
heaters I am used to are 240vac, not 120vac..
Have a great day .