Andrew Swingler suggests thermosyphoning as one form of freeze protection
for evacuated tube collectors above a heat storage tank. This might be the
only form of freeze protection needed for freeze-tolerant heat-pipe tubes
below a pressurized header with some insulation on the header and its supply
and return pipes, and a pipe with minimal elbows and a circulation pump that
doesn't block flow when stopped.
Cool water weighs about 62.67 - 0.003T lb/ft^3, with T in degrees F. The
density difference caused by the temperature difference between up and down
pipes causes a pressure difference proportional to the height of the water
column, making water flow through the resistance of the pipe loop. With 16'
of height and a dT temperature difference, dP = 0.048dT lb/ft^2.
Bill Shurcliff says a pipe with radius r and length L in feet and pressure
diff dP has laminar flow Q = Pir^4dP/(8MuL) ft^3/s. Viscosity Mu is about
6x10^-7 lb-s/ft^2 for 32 F water. With, say, 32' of 1/2" pipe, 16' up and
down, Q = Pi(0.25/12)^4dP/(8x6x10^-7x32') = 0.004dP ft^3/s or 43dT lb/h,
which moves 43dT^2 Btu/h. If the heat pipe collector header is 6"x6"x8' long,
with 16 ft^2 of surface and R4 insulation and a 16/4 = 4 Btu/h-F conductance
from 60 F water temp to outdoor air at, say, -20 F, (60+20)4 = 320 Btu/h
makes dT = sqrt(320/43) = 2.7 F, if I did that right Water goes up at
60 F and returns at 57.3 F, well above 32 F. At -40, with about 400 Btu/h
of heat loss, the water might return at 60-sqrt(400/43) = 57.0 F.
Nick
for evacuated tube collectors above a heat storage tank. This might be the
only form of freeze protection needed for freeze-tolerant heat-pipe tubes
below a pressurized header with some insulation on the header and its supply
and return pipes, and a pipe with minimal elbows and a circulation pump that
doesn't block flow when stopped.
Cool water weighs about 62.67 - 0.003T lb/ft^3, with T in degrees F. The
density difference caused by the temperature difference between up and down
pipes causes a pressure difference proportional to the height of the water
column, making water flow through the resistance of the pipe loop. With 16'
of height and a dT temperature difference, dP = 0.048dT lb/ft^2.
Bill Shurcliff says a pipe with radius r and length L in feet and pressure
diff dP has laminar flow Q = Pir^4dP/(8MuL) ft^3/s. Viscosity Mu is about
6x10^-7 lb-s/ft^2 for 32 F water. With, say, 32' of 1/2" pipe, 16' up and
down, Q = Pi(0.25/12)^4dP/(8x6x10^-7x32') = 0.004dP ft^3/s or 43dT lb/h,
which moves 43dT^2 Btu/h. If the heat pipe collector header is 6"x6"x8' long,
with 16 ft^2 of surface and R4 insulation and a 16/4 = 4 Btu/h-F conductance
from 60 F water temp to outdoor air at, say, -20 F, (60+20)4 = 320 Btu/h
makes dT = sqrt(320/43) = 2.7 F, if I did that right Water goes up at
60 F and returns at 57.3 F, well above 32 F. At -40, with about 400 Btu/h
of heat loss, the water might return at 60-sqrt(400/43) = 57.0 F.
Nick