daestrom" (daestrom@NO_SPAM_HEREtwcny.rr.com) said:
Actually, for heat, you merely connect R and W. There is another
thermo-switch at the furnace (on the heat-exchanger) that will turn on the
blower *after* the burner has warmed up the heat-exchanger. This also keeps
the blower running for a few seconds after the burner shuts off.
IIRC, similar is true for cooling. When you connect R to Y, the A/C starts
and it starts the blower directly.
R to G is only connected when you turn the 'Auto-On' fan switch to 'On'.
The G is open-circuit any time the fan switch is in auto.
daestrom
Other research I did suggests what you say, almost. . In my case I have a
water pump activated with the R to W . It then activates the blower but it
appears that if I had manually set R to G I might change the speed of the
blower (can be wired for dfferent speeds, mine isn't but friend' is).
I read that some thermostats might activate both Heat and Blower for some
applications.
It said that for cooling the thermostat activated both the
compressor and blower. In my case based on wiring I see that as the only way
the blower
could be started for cooling. ie R to Y or compressor and R to G for blower
indicating
again that cooling would be different speed than heating if I had multiple
speeds wired.
Thanks