I am trying to fix a sound system noise problem, and have some questions
that require electrical engineering expertise. I hope that someone here
can shed some light.
Sound and lighting systems are installed in a large church sanctuary.
The lighting dimmers are fed by a 400 amp delta-wye transformer, whose
480v feeders run in slab, under the sound mix position. The 3 phases and
ground are in PVC.
The distance between the transformer and service entrance is about
250-300'.
With all dimmers running at 50%, we get a substantial amount of signal
contamination in the mixer's mic inputs, largely at 180Hz, though other
harmonics are present.
When the dimmers are at 50%, we measure over 50 amps on ground, at the
transformer. The transformer is also bonded to building steel. The
lighting folks say that this in reasonable, and not excessive. I have
read the large amounts of harmonics are byproducts of SCR dimming, and I
know that the draw across phases varies constantly, because lighting
conditions change a great deal through a service.
My questions to you are:
Is 50 + amps on ground, acceptable with regard to code?
Is there a way to remediate the noise?
thanks
that require electrical engineering expertise. I hope that someone here
can shed some light.
Sound and lighting systems are installed in a large church sanctuary.
The lighting dimmers are fed by a 400 amp delta-wye transformer, whose
480v feeders run in slab, under the sound mix position. The 3 phases and
ground are in PVC.
The distance between the transformer and service entrance is about
250-300'.
With all dimmers running at 50%, we get a substantial amount of signal
contamination in the mixer's mic inputs, largely at 180Hz, though other
harmonics are present.
When the dimmers are at 50%, we measure over 50 amps on ground, at the
transformer. The transformer is also bonded to building steel. The
lighting folks say that this in reasonable, and not excessive. I have
read the large amounts of harmonics are byproducts of SCR dimming, and I
know that the draw across phases varies constantly, because lighting
conditions change a great deal through a service.
My questions to you are:
Is 50 + amps on ground, acceptable with regard to code?
Is there a way to remediate the noise?