Greg said:
That is why power factor correction is such a big deal. It fixes most of
the problems you mentioned. Most (if not all) electronic ballasts use
it - if they didn't, imagine what impact a large building full of them
would have. Imagine what the utility bill would be if the building had
a power factor watt-hour meter!
This is a point were there is a lot of misunderstanding. By its very nature,
power factor (PF) correction is frequency selective. The correction capacitor
used if it is provided at all is that which brings the PF of that load
to equal one at the power frequency. Does nothing for the harmonics. They
are all still there. In a simple non-linear load the 3rd harmonic is dominant.
However, there are many other odd order (5th, 7th, Etc) present as well.
In the power system itself there are other PF caps installed, often at
transformer stations (TS), sometimes on poles closer to the load.
You can often see them from outside the fence at a TS.
They are there to minimize the reactive currents in the transformers.
Only the current which is in phase with the fundamental voltage of the power
system does useful work. The rest, including that due to the harmonics is
dissipated as heat, some of it in the TS transformers. The harmonics in the
system at the load can also induce circulating currents in other equipment
at the load. In other words, the PS in your PC will generate harmonic
currents which will show up in your refrigerator!!
An occasional fault can occur in a power system when the power factor
capacitors resonate with inductive reactance's in another part of the system
to which they are connected. However, this does not happen at the power
frequency, but rather at one of the harmonics mentioned above. There are
documented cases of failures where the system was excited into oscillation
by harmonics of the load at say the 13th or 17th of the power frequency.
If the harmonics were not there, the failure would not be triggered.
There are industry standards such as IEEE-519 & IEC-555 which define
limits of harmonic generation in products to be used in power systems.
Also, definitions of derating systems for transformers.
I wonder how long it will be before the utilities start fitting homes with
such meters. With all the electronics that people have these days,
and all of it using conventional rectified supplies with no power
factor correction, people will be in shock when they get their
electric bills after such a meter is installed
A good reference for those working in the field & which doesn't get into
higher mathematics is Mark Waller's book on Harmonics. It's available
new or used from Alibris. I got mine at a power systems conference.
Try
www.alibris.com or
http://www.alibris.com/search/search.cfm?qwork=4191854&matches=4&qsort=r
Cheers, John Stewart