Only in a perfect world, and as we all know, our world isn't perfect.
For two or more AC machines to share the load well, the governors on the
machines (either electronic or mechanical) *must* have a characteristic
called 'droop'. This is the phenomenon where the governor output (fuel
control/throttle) only rises if the speed is below a setpoint. And in order
to get more fuel, the speed further below setpoint. Speed droop is often
measured as a percentage. If the unit is run isolated from all other
generaters and has its load varied from no-load to full-load, the amount of
speed reduction needed to have the governor go from cut-off to full throttle
is measured. This speed reduction (in RPM) is divided by the no-load speed
(also in RPM) and expressed as a percentage. Speed droops of small to
medium sized machines often runs 3 to 7 % (i.e. @5%, the speed of an 1800
RPM, unloaded generator will drop to 1710 when fully loaded)
If you take two AC machines with the same droop characteristic (let us
assume 5%), they will share the load quite nicely, even if one is much
larger than the other and running at a different speed (with different
number of poles in their respective generators). For example, say you have
a 10kW, 1800 RPM machine carrying 2kW operating in parallel with a 100kW,
3600 RPM machine carrying 20kW. Now suddenly switch on a 55kW load. Both
machines will begin to slow down and their governors will increase their
fuel flow. But look closely at what happens. The small machine slows down
about 2.5% to about 1755 RPM. The governor of that machine will increase
fuel flow by 50% of rating and the generator is now carrying 7kW.
Similarly, the large machine slows down about 2.5% to about 3510 RPM. The
governor of *that* machine will increase fuel flow by 50% of rating and the
generator is now carrying 70kW.
So, with the same droop characteristic, these two machines were originally
loaded to 20% of their capacity, and after switching on a large load they
are both loaded to 70% of their capacity. And it all came about because the
two governors have similar characteristics. These machines do *not* need
any cross-connections for this to work. Similarly, a sudden reduction in
load will come off the two machines nicely and neither will reverse power
the other unit.
The only problem is that frequency went from 60hz original, to 58.5hz. This
can be corrected by adjusting *both* governor setpoints upward at the same
time. If you adjust just one of the governor setpoints upward, it will
sense that engine speed is further away from the setpoint and increase fuel
flow to the engine. This will increase the load on the generator. As the
load is 'picked up' by this machine, the opposite machine will see a
reduction in load and start to speed up slightly. So the second machine's
governor will sense speed closer to the setpoint and decrease the fuel to
its engine and its generator load will decrease.
I've paralleled hundreds of generators over the years using both
synchroscope and lights (three phase lights can be fun as they can be wired
to 'rotate'
. Almost universally, the 'incoming' machine is run slightly
faster than the system it is being connected to. This helps to ensure that
the moment it connects, its governor will see a slight drop in speed and
increase fuel flow. This is important as most generators intended for
parallel operation have reverse-power protection and in order to avoid false
tripping of the unit, it is best to pick up some load immediately. Even
extremely *large* units (1200MVA), when first connecting in are run slightly
fast (after all, if the speed is exactly matched, the synrchoscope doesn't
rotate at all).
Now, that all said, there is yet a different situation with some of the
small portable units available. Some of the small portable units are
actually DC generators with electronic inverters. Since the machine is
actually DC, all this previous talk about governors and droop is not
applicable. What is important when connecting inverters together is how the
inverter electronics are designed. Some manufacturers (Honda I believe is
one) have a special cable to connect between the units. This cable actually
connects between the *inverters* so the two *inverters* that are inside the
units can communicate and share load between them.
daestrom
P.S. DC generators can be made to share their loads in a similar manner by
designing the voltage regulators to have a 'droop'. Or just the machine's
inherent voltage regulation, if properly designed, will do it as well.