Transmitting electricity at high voltage reduces the fraction of energy lost to
resistance, which varies depending on the specific conductors, the current flowing, and the length of the transmission line. For example, a 100 mi (160 km) span at 765 kV carrying 1000 MW of power can have losses of 1.1% to 0.5%. A 345 kV line carrying the same load across the same distance has losses of 4.2%.
[20] For a given amount of power, a higher voltage reduces the current and thus the
resistive losses in the conductor. For example, raising the voltage by a factor of 10 reduces the current by a corresponding factor of 10 and therefore the I 2 R {\displaystyle I^{2}R}
losses by a factor of 100, provided the same sized conductors are used in both cases. Even if the conductor size (cross-sectional area) is reduced ten-fold to match the lower current, the I 2 R {\displaystyle I^{2}R}
losses are still reduced ten-fold. Long-distance transmission is typically done with overhead lines at voltages of 115 to 1,200 kV. At extremely high voltages, more than 2,000 kV exists between conductor and ground,
corona discharge losses are so large that they can offset the lower resistive losses in the line conductors. Measures to reduce corona losses include conductors having larger diameters; often hollow to save weight,
[21] or bundles of two or more conductors.