LED or CFL flickering with motion sensor in circuit

Nehmo

Oct 15, 2011
7
Joined
Oct 15, 2011
Messages
7
I use a motion sensor wall switch to control the bathroom light. It works fine with an incandescent bulb, and it works with some CFL bulbs and even some LED bulbs. Most bulbs of either CFL or LED cause annoying flicker. There is a difference in behavior of bulbs from the same manufacturer. That is, some bulbs don't flicker.
I realize the motion control is working like a dimmer, and I've bought dimmer-compatible bulbs. But they still flicker.
I know I could put a relay in the circuit to end the flickering. And I know I could go back to incandescents. I don't like either of those solutions.
Is there some simple way to avoid flickering of an LED when using a motion sensor control?
And what's the explanation anyway?
60037_fbd8c450b5e68ecd03fe8363b0ad010916ea31fa_original.jpg
 

hevans1944

Hop - AC8NS
Jun 21, 2012
4,886
Joined
Jun 21, 2012
Messages
4,886
This is just a guess... most solid-state switches (SCRs and TRIACs) require a minimum holding current that must be in phase with the zero-crossing of the AC line voltage before the semiconductor will latch on. Most CFL and LED line-operated lamps do not draw enough current, or the current is phase-shifted with respect to the supply voltage by the internal switch-mode electronic power conversion circuits, and therefore do not remain conducting after triggering. One solution, as you mentioned, is to go back to using incandescent lamps. Perhaps just a small "night light" type of lamp connected unobtrusively in parallel with the rest of the lights will solve the problem. You might even be able to fit a 7-1/2 watt lamp inside the handy-box the motion sensor is mounted in without experiencing excessive heat rise.,, if that's enough of a resistive load to solve the problem.
 

Sunnysky

Jul 15, 2016
541
Joined
Jul 15, 2016
Messages
541
This sensor triac needs more load current to sustain a holding current in all Quadrants.
i.e. a less efficient light.

Not all lights have PFC and this would help the triac work , maybe. (dimmable)


try that nitelite suggestion if you have a GFCI outlet or a dummy load of 10W
 

Nehmo

Oct 15, 2011
7
Joined
Oct 15, 2011
Messages
7
The GFCI receptacle is on a separate circuit.
Anyway, I added a 7.5 watt incandescent in parallel with the LED, and the motion detection switch works properly now.
But I've seen available motion detector units that originally come with LED lamps. They must have a different design, or maybe they have a load built in.
 

Sunnysky

Jul 15, 2016
541
Joined
Jul 15, 2016
Messages
541
LEDs with constant current SMPS will work while PWM types are more common in low power lamps would flicker.
 

ORBear

Feb 28, 2017
1
Joined
Feb 28, 2017
Messages
1
Thanks for the insight. I am converting a number of older florescent light fixtures to LED. They are all on occupancy sensors. When I installed the LEDs they flickered when they were supposed to be off. I added a 5W night light in parallel and it solved the problem. What I don't understand is that these older occupancy sensors have a relay on the load output so I don't see why they would need any holding current!?
 

Greg01

Apr 5, 2017
1
Joined
Apr 5, 2017
Messages
1
Hi,
I have a similar problem but different!! My motion sensor switches an incandescent spot lamp. However when the spot lamp comes on, my led lights in my lounge flicker. They cease flickering when the motion switched spot lamp goes off. Replacing the led lamps with incandescent lamps fixes the problem but doesn't help with the idea of led lamps being cost savers. Can anyone help?
 

Sunnysky

Jul 15, 2016
541
Joined
Jul 15, 2016
Messages
541
Add a 30W tungsten lamp to LED supply load to satisfy triac switch for LEDs if possible. ??
 

(*steve*)

¡sǝpodᴉʇuɐ ǝɥʇ ɹɐǝɥd
Moderator
Jan 21, 2010
25,510
Joined
Jan 21, 2010
Messages
25,510
What I don't understand is that these older occupancy sensors have a relay on the load output so I don't see why they would need any holding current!?

They may have a capacitor across the relay contacts. This passes enough AC current to allow the very efficient lights to turn very slightly on.
 

Sunnysky

Jul 15, 2016
541
Joined
Jul 15, 2016
Messages
541
Thanks for the insight. I am converting a number of older florescent light fixtures to LED. They are all on occupancy sensors. When I installed the LEDs they flickered when they were supposed to be off. I added a 5W night light in parallel and it solved the problem. What I don't understand is that these older occupancy sensors have a relay on the load output so I don't see why they would need any holding current!?
If it uses a triac to create some transformerless DC voltage with a small Relay and small LED load the triac may be false triggered by dV/dT noise which must be filtered externally or internally to the triac by some means of attenuation.

Often an Incandescent load is enough to prevent this external leakage and dV/dT noise false trigger in triacs..

Unless a relay is latching type, they all have a holding current about 20% of activation current with normal hysteresis. That also defined by the Must latch voltage and much lower Must release voltage, but this is not relevant to your issue.
 

Babbo

Jul 5, 2017
3
Joined
Jul 5, 2017
Messages
3
I have the LED-flashing-with-occupancy-sensor switch problem too. Can I install a low wattage incandescent bulb alongside two LEDs in the same fixture to solve the problem? Everyone says not to combine LEDs and incandescent bulbs.
 

Babbo

Jul 5, 2017
3
Joined
Jul 5, 2017
Messages
3
I wasn't sure if adding the incandescent to the load was exactly the same as adding it to the fixture. Thanks to all.
 

AnalogKid

Jun 10, 2015
2,893
Joined
Jun 10, 2015
Messages
2,893
You might even be able to fit a 7-1/2 watt lamp inside the handy-box the motion sensor is mounted in without experiencing excessive heat rise.
I strongly disagree with this suggestion. A wall box does not have many open holes because its primary job is to contain fires. I doubt there is enough room inside to add a bulb behind the sensor/switch, but if there were the bulb would fry the sensor electronics in under an hour.

Demo: Plug a 7 W night light into a wall socket, remove any shade or cover, turn it on, and cup you hand around and over the top of the bulb so it is 1/2" away from your skin. Wait.

ak
 

hevans1944

Hop - AC8NS
Jun 21, 2012
4,886
Joined
Jun 21, 2012
Messages
4,886
I strongly disagree with this suggestion. A wall box does not have many open holes because its primary job is to contain fires. I doubt there is enough room inside to add a bulb behind the sensor/switch, but if there were the bulb would fry the sensor electronics in under an hour.

Demo: Plug a 7 W night light into a wall socket, remove any shade or cover, turn it on, and cup you hand around and over the top of the bulb so it is 1/2" away from your skin. Wait.

ak
Well, I did say might... but you are right. It was a dumb suggestion to try to fit the lamp inside the handy-box. Shouldn't put anything in a handy-box that is going to intentionally generate heat. It might even be illegal to do so, in which case it was a really dumb suggestion, although I have seen (and used) a commercial light-switch dimmer that got pretty warm working with eight 60 W incandescent lamps. It was rated to handle 600 W, but it did get rather warm. So, just put the 7.5 W incandescent load somewhere conveniently in parallel with the LED load and safely in open air. Post #4 indicated this actually worked for the OP, but for some sensor/controllers it may not be enough of a load. See post #8 above.
 

AnalogKid

Jun 10, 2015
2,893
Joined
Jun 10, 2015
Messages
2,893
Dimmer heating made my wife nervous until I pointed out that the front plate is the heatsink and is working to eject the heat, the components inside are rated for way higher temperatures, and the wall box is completely fireproof by law.

ak
 

hevans1944

Hop - AC8NS
Jun 21, 2012
4,886
Joined
Jun 21, 2012
Messages
4,886
Dimmer heating made my wife nervous...
It made me nervous too, but I left it installed. This was for dimming eight (four on each side of the medicine cabinet mirror, Hollywood dressing room style), large-globe, frosted, 60 W incandescent lights. Worked pretty good for that, and at full brightness the lamps kept the bathroom nice and warrm. Expensive heat though, so I eventually replaced them with LED equivalents. Dimmer didn't work quite as well with the dimmable LEDs, but it was satisfactory, so that's the way I left it. Then we moved to Florida, where everything is electric, and lights are either curly-bulbs or LEDs. I hate curly-bulbs, so have slowly been replacing them with LEDs as soon as I can afford new ones.
 

butchdon

Jul 20, 2017
1
Joined
Jul 20, 2017
Messages
1
I had a LED ceiling light I just purchased that flickered when connected to a motion sensor. I returned it and got another. Same thing. So I swapped out the MS switch for a standard single pole. works fine.

Installed the MS switch in my kitchen. Unfortunately, the two ceiling floods are LED's, so now they flicker. There's nowhere to place a "load" incandescent bulb to cure this issue. Is there another solution? This must be happening all over the country as people convert to LED's. We love the occupancy switches.

Someone needs to invent a 7 1/2 W wafer resistor you can place in the bulb socket.
 

Tha fios agaibh

Aug 11, 2014
2,252
Joined
Aug 11, 2014
Messages
2,252
Someone needs to invent a 7 1/2 W wafer resistor you can place in the bulb socket.
Negating the efficiency of the led isn't the best solution.
The problem with leds is they respond so quickly, the light dims to the slightest ripple of its supply. This makes a strobe effect.

Your motion detector circuitry was likely designed for slower incandescent lamps, long before modern led lamps were available.

They have some md devices that use a relay output. That would work. Also, I'm sure manufactures are working on a cleaner output as we speak. Perhaps a Schmidt trigger added before the triac?
 