UPS on Super-Caps

Discussion in 'General Electronics Discussion' started by shiekh, May 4, 2011.

Scroll to continue with content
  1. shiekh

    shiekh

    77
    1
    Oct 11, 2010
    I am wondering about running a UPS on a super-cap array (I'm tired of replacing the battery)

    http://www.goldmine-elec-products.com/prodinfo.asp?number=G18113

    should be able to hold up 100W for about 3 mins (some of this will be powering the UPS itself)

    I was wondering what algorithm a UPS uses in general to test its batteries, and if a super-cap array like this will trigger the battery alarm or not. Hopefully the charger will also be happy.

    At first I was worried about the need to balance the array (with zener diodes), but since they sell it as an array, I suppose this is not a real concern.

    These 2600F capacitors can now be got used for about $10 each

    http://www.goldmine-elec-products.com/prodinfo.asp?number=G18107
     
    Last edited: May 9, 2011
  2. Resqueline

    Resqueline

    2,848
    2
    Jul 31, 2009
    Ok, so the bank is 433 Farads & 15 Volts = 48750 Joules.

    100W is 7.25A at 13.8V and this gives a rate of change of 17mV/second (at that voltage). At 10V you might get a rate of change of 23mV/second.
    The UPS might cut off at 10V so you have 3.8V to work with giving 3.8/0.02 = 190 seconds = 3 minutes & 10 seconds. All this is assuming a 100% UPS efficiency.

    If you can modify the charging voltage up to 15V, and perhaps lower the cutoff voltage you'll get a longer run-time, potentially giving you at least 3 minutes in practice.

    The capacitors needs to be charged to at least 11V before connecting the UPS. I don't know anything about the battery test method. I'd certainly balance the array!
     
  3. shiekh

    shiekh

    77
    1
    Oct 11, 2010
    Progress report, for those that might be interested in trying the same:

    * The UPS I picked actually runs between 13.6 and 10.6V (I had estimated 13.8 and 10.0V) which makes it equivalent to a 1AH 12V battery.

    * The UPS had no problem filling the capacitors from 0V

    * The array does not need any balancing (some 4.7V Zeners could be used to balance pair-wise if one really wanted such protection)

    * Fortunately the UPS does not trickle charge, which might just slowly overfill the capacitors (balancing Zeners would help if there was a trickle charge)

    * 'Bad battery' alarm has not appeared, so it seems to be recognizing the capacitor array as a good battery

    * Have build a wooden carrier for the capacitor array after figuring out a design that is easy to make (see attachment)

    Of course the run-time is short (a few minutes), but this is easily enough to carry one through a glitch, and in such a low duty application the capacitors should last indefinitely.
     

    Attached Files:

    Last edited: May 24, 2011
  4. AprilSteel

    AprilSteel

    111
    9
    Feb 2, 2017
    This is 6 years old now but I would be interested to know more about using a supercap bank as a battery for a power grid. Anybody got one of these running or a UPS running the personal grid from solar panels?
     
  5. shiekh

    shiekh

    77
    1
    Oct 11, 2010
    AprilSteel likes this.
  6. AprilSteel

    AprilSteel

    111
    9
    Feb 2, 2017
Ask a Question
Want to reply to this thread or ask your own question?
You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.
Electronics Point Logo
Continue to site
Quote of the day

-