    Can anyone advise on the following wiring configuration for a British wiring
    installation.

    An air conditioner unit has been previously installed, but instead of being
    connected to a dedicated 32 amp supply, a socket outlet has been removed
    from the ring circuit and a 25 amp RCBO installed to feed it. Is this
    acceptable?
     
  2. No.
    It would be acceptable if the aircon could run off a 13A fused spur.
     