transformer phasing question
Discussion in 'Electronic Basics' started by [email protected], Jan 22, 2004.
  1. Guest
    A very common power distribution transformer uses a DELTA wired primary
    and a WYE wired secondary (thus including a neutral connection). In the
    WYE secondary, you then can get a lower voltage from the hot-to-neutral
    connections, or a higher voltage from the hot-to-hot connections. Some
    common voltages:
    120 volts hot-to-neutral and 208 volts hot-to-hot in US, Canada
    230 volts hot-to-neutral and 400 volts hot-to-hot in Europe
    277 volts hot-to-neutral and 480 volts hot-to-hot in US
    346 volts hot-to-neutral and 600 volts hot-to-hot in Canada
    The interesting thing about this is that while the hot-to-neutral lines
    provide power in the same 3 phases that the primary windings have, the
    hot-to-hot lines are off by 30 degrees. Normally that is no big deal
    since 3 phase machines only care about the phases on what is hooked up.
    Now here is my question. Suppose I have a 1 phase device hooked up to
    just one pair of hot-to-hot lines. Further suppose this is a resistive
    load (power factor 1). At the load the phase relationship between the
    voltage and current will be 0 degrees. But what about the relationship
    between the voltage and current in the two windings that are feeding
    this power? Wouldn't they be off by +30 degrees and -30 degrees? So
    wouldn't this appear to them to be a partially reactive load? And what
    about the current on the primary side. Wouldn't that reflect the phase
    difference there, too?
    If the above is true, and it would seem to me to be the case (but I am
    asking to have that confirmed since there might be some physics that are
    involved that I am not aware of), then if one were expecting to have
    loads that are routinely out of balance on a 3 phase line, that the best
    choice would be to configure the secondary so that the exact voltage one
    needs is provided on exactly one winding (whether the secondary is wired
    WYE or DELTA)?
    In many commercial buildings, power is provided in three phase due to
    the higher capacity, at the 120/208 volt level in the US. This is the
    right voltage for the lights and most appliances at the hot-to-neutral
    lines. Then the hot-to-hot 208 volts is expected to serve the higher
    voltage needs like larger 1 phase air conditioners, electric stoves,
    and whatever else needs voltage in that range. But doesn't this kind
    of setup potentially put an unbalance demand on the 3 phase connection?
  2. Actually, you have that backwards, the line to neutral phases
    correspond to the line to line primary phases. This is because each
    branch of the Y shares a core with one of the sides of the delta.
    (snip)
    So the current in that load involves current in two branches of the Y
    and so, current in two sides of the delta.
    The different phase voltages in the Y branches add up vectorially to a
    new voltage, and that voltage produces a resistive current that is in
    phase with that voltage. That current passes through two branches of
    the Y and it is, as you say, 30 degrees out of phase with each of
    those branch voltages.
    However, since each Y branch is driven by one side of the primary
    delta, those currents must also be 30 degrees out of phase with two of
    the delta sides. but this primary current is carried by the voltage
    between two primary line phases, with that voltage and current exactly
    in phase. So the resistive load across two branches of the Y appears
    to the primary lines as a resistive load between two of the line
    phases with no phase shift.
    If the loads of all phases are balanced, the 30 degree phase shifts
    all cancel out. If the load is completely unbalanced, as you
    specified, then there is a reduction in the total power the
    transformer can carry do to the power factor.
    Pictorially:
    The instantaneous secondary load voltage and current is represented by
    a horizontal vector (say, to the right).
    --RRR-->
    A \ /B
    Y n
    |C
    So the winding currents are A down to n and n up to B.
    The primary current that carries the load passes through c down to b
    (the current A to n) and c up to a (the current n to B), since those
    windings share magnetic flux with branches A (to n) and (n to) B,
    above. If branches A and B are at rated current, so must be windings
    c to a and c to b.
    a
    c< |
    b
    So all the load current passes through c, but splits and exits equally
    out of a and b. There is no current in a to b winding, since there is
    no vertical component in the load current. So the 30 degree power
    factor is also reflected in 2 of the primary windings. These windings
    are carrying only 87% of their power capability at rated current,
    because of the power factor.
    If you picture the line wave as three symmetrical vectors with respect
    to a floating common point in the middle of the delta (that is
    rotating, and just happened to be frozen, momentarily), with the ends
    of those vectors pointing to the corners of the delta, you find that
    the line current in the c phase is in phase with the voltage, but the
    line currents in phases a and b are 30 degrees shifted with respect to
    their voltage. So a three phase transformer connected this way is
    inefficient (2/3 * .87 of its rated capacity because only 2/3s of the
    windings are being used, and those operate at .87 of power capacity)
    driving a single phase load. Is this a surprise, when you could have
    just used a single phase transformer? But the three phase transformer
    still has the capacity to drive three loads that add up to 173% more
    than this single load that hit the winding current limit, if those
    loads are balanced.
    So the transformer is only 58% utilized for this single phase load.
    Of course, if you had hooked a single phase load from neutral to one
    branch of the Y, it would have been only 33.3% utilized (since that
    load would have used exactly 1/3 of the windings running at a power
    factor of 1). Phew!
  3. Guest
    | (snip)
    | (snip)
    That's actually what I said, but in different terms (hot instead of line)
    and probably not clear enough. I should have added "compared to the
    hot-to-hot lines of the primary" on the last sentence of that paragraph.
    That would seem to be the case. I can't think of a reason why it wouldn't.
    |> So wouldn't this appear to them to be a partially reactive load?
    |> And what about the current on the primary side. Wouldn't that reflect the phase
    I don't see how that happens. But the picturing below might be a better
    reference.
    |> WYE or DELTA)?
    Yes, one would want to have balance if possible (usually is). But I want
    to explore how it all works out when not in balance (worst case scenario).
    Later I want to work it out for Delta to 6-Star configuration, as well
    as a 2 core T-T configuration.
    | Pictorially:
    | --RRR-->
    | A \ /B
    | Y n
    | |C
    | c to a and c to b.
    | a
    | c< |
    | b
    But isn't the current in winding c-a and in winding c-b, as well line c,
    at a horizontal phase angle here? But there's no voltage at that angle.
    | loads are balanced.
    I'm not surprised at all regarding the reduced capacity, and that a
    single phase transformer would be better.
    Of course if the power is fed in one phase only, that's drawing off
    some 3 phase distribution point ... but it's likely to only be a tiny
    portion of the total load at that point.
    But I could get 3x the power at 100% utilization if the load were in
    proper balance.
    | factor of 1). Phew!
    If the secondary was 208Y/120 and all the load were on a single 120 volt
    line, that would be as you describe. But if the load needed to be 208
    volts, and the secondary is WYE, then we have the 30 degree reactive case.
    A delta secondary might be a better choice if the load is going to be
    frequency or regularly out of balance, but all three phases are still
    needed at times ... or maybe even paralleling 3 phase and 1 phase.
  4.
  5. Guest
    | OH Dear !!
    | I hope you are not employed as an engineer somewhere.
    Not an electrical engineer. My area of expertise is computer network and
    systems administration and programming. Electronics is a hobby, and hence
    the questions to acquire the knowledge. So do you have any further answers
    to contribute?
  6. I hope I didn't imply by my answers to your post that this was a
    trivial problem that I could understand at a glance. I think it took
    me three tries before I could get to the end of my review without
    contradicting myself. I think this is one of those contradictions
    that I forgot to go back and fix. Your question was a good
    opportunity for me to have to think about 3 phase power and I should
    have started of a little more humble.
    (snip)
    Whoops. Another point I later contradicted and did not go back and
    correct. My first (non graphic) analysis somehow converted a
    horizontal (vectorially speaking) load into a vertical one (I reversed
    the sign of one of the delta currents). Glad to see you actually read
    what I wrote. Sorry I didn't catch this correction, myself.
    (snip)
    My head hurts, already. Phasor diagrams will help.
    (snip)
    There is no voltage at precisely that phase but there is a voltage
    between c and a (and between c and b) that can be resolved into two
    components, 1 of which is in that direction.
    I was analyzing the case where the single phase load reached the
    current capacity of the transformer, as the most extreme example.
    Not quite. This single load uses all of the current capacity of two
    of the 3 sets of windings. Balancing the loads will eliminate the
    power factor current on those two sets, and also make use of the third
    set, but this first load has to be lowered before two other equal
    loads can be added and still keep the winding currents at the same
    peak they had, originally.
    Yes, that was what I was describing.
    There is no real advantage to one over the other, as far as I know.
    One case puts all the load current on two primary lines with a 30
    degree phase shift (remember that the primary phase voltages do not
    match any of the voltages across any delta winding. The delta winding
    voltages are the vectorial difference of two line voltages. So a pure
    resistive current in one delta winding puts a 30 degree power factor
    load on two of the lines. The Y loaded case puts zero phase shift on
    one line and a lower current 30 degree shifted load on the other two.
    The only way to have a single phase load not produce power factor
    current on a 3 phase line is if it is a 4 wire setup, and the load is
    connected one line to neutral. Any single phase line to line load
    with or without a transformer will produce power factor current
    somewhere.
    (I think.)
  7. Guest
    |> | (snip)
    |> | (snip)
    I'm still working on even getting the terms right on all this.
    | (snip)
    |> reference.
    | (snip)
    Yes, they do help. I should drag out shome graphics plotting tools. I can
    visualize them in my head, but I find it hard to draw them in ASCII.
    | (snip)
    |> | Pictorially:
    |> | --RRR-->
    |> | A \ /B
    |> | Y n
    |> | |C
    |> | c to a and c to b.
    |> | a
    |> | c< |
    |> | b
    Which means the current will have to be seen as 30 degrees reactive?
    |> | loads are balanced.
    I can see where that would be pushing things. That 1 phase would be
    more than its contribution in a fully loaded 3 phase scenario.
    I do know if I had a 208Y/120 secondary and put 100 amps load on each
    of the 3 ways to get 208 volts, I'm really looking at 173.2 amps on
    each of the hot lines (some of the current crosses between the phases
    but most of it combines in the lines back to the transformer secondary).
    With a WYE secondary, that 173.2 amps is the current through each of
    the windings. But with a DELTA secondary, the windings end up with
    just 100 amps current, same as the loads. But this is right because
    the 173.2 amps in the windings of a WYE secondary are really over the
    120 volt potential, while the 100 amps in the windings of a DELTA
    secondary are really over the 208 volt potential. So the KVAs work
    out to be the same.
    Europeans can work this out with 400 and 230 volts.
    |> proper balance.
    The scenario I am thinking of is where 3 phase is the power source, and
    the available loads, equally divided over all three phases on the secondary
    of the transformer, will add up to the total transformer capacity. Then
    the loads are selectively turned on so that all of the loads on ONE of
    the phases are on, and none of the loads on the other 2 phases on.
    Then a later scenario I will explore is 2 of the 3 load sets are on.
    I want to understand what capacity every part of the system might need to
    have for the worst case scenarios. And I haven't even gotten into the
    harmonic and pulsed loads that can really throw three phase out of whack.
    For example I read that it might be necessary to double the current capacity
    of the neutral, but it looks to me like the very worst case would require a
    triple capacity, or a DELTA secondary with 15.5% extra current capacity
    (each leg carrying the full 200 amps, instead of 173.2 amps, from the above
    scenario, if the current pulse times are so narrow that there is no way to
    "share current" between phases).
    With 1 load set on, I can see where the transformer is at 58% of capacity
    ( 100% / sqrt(3) = 57.735% ). That's not overloading the total capacity,
    but I want to be certain there are not spot overloads anywhere.
    | somewhere.
    | (I think.)
    I believe I have a full understanding of adding vectors to get the voltages.
    What I'm working on right now is understanding the currents. But what I
    see is that when there is only current drawn in 1 phase angle, it stays in
    that angle all the way back to the power source. If voltage were supplied
    to the 3 phase system in only 1 phase (1 leg opens in a delta primary for
    example), then all the voltage presented everywhere will be only in that 1
    phase angle, although in different voltages in various parts because with a
    delta primary, losing the B leg means windings A-B and B-C are now in series
    with the remaining voltage source between lines A and C, resulting in the
    two corresponding secondary windings to become "flattened" at half voltage.
    The scenario with 1 load set appears to me to be simple in transposing the
    current back to the power source. But with 2 load sets on, you have to add
    those current vectors and ultimately it will be their sum; what I want to
    understand are the intermediate steps to get there.
    The T-T transformer will be interesting to study this on, too:
    | <=> | -OR- | <=> *-------*
    If you do this with 240/120 center tapped on the phase with the tap in the
    middle, you get 240 volts delta-like from it, or 208 volts in one phase
    along the untapped winding. The interesting thing about T-T is it uses
    only 2 cores.
    The 6-star would be nothing more than a special case of WYE, I believe: