I have a some European (i.e. 230V) kit that is frequency independant. In my
house (120V) I have the usual split-phase arrangement (i.e . +/- 120V off
the pole, some circuits fed with -120V and neutral, some with +120V and
neutral, net effect is 120V where it's needed). I don't have any 240V
outlets (i.e. -120V and +120V). If I wanted to run this kit is there any
theoretical reason why I shouldn't wire it to each of two hots on separate
120V circuits (obviously making sure one is +120V and one is -120V). What
about practical reasons?

Thx

D
 
M

Mitch Thompson

Jan 1, 1970
0
No theoretical reason, other than 240V is not 230V. Also, you could get
inductive heating and choke on the circuits you use, due to the unbalanced
load situation you will cause in each of the two circuits.

For safety's sake, have a 2 pole breaker and 240 volt receptacle installed.

Mitch Thompson
http://autopanelboard.home.insightbb.com/home.html
Electrical Panel Schedule software for use with AutoCAD

For safety's sake, get a two pole breaker and a 240 volt receptacle
installed
 
D

Den

Jan 1, 1970
0
Mitch

I *wasn't* going to do it!

Can you explain why there would be inductive heating (I guess I'm unclear as
to what induction and choke are). I don't see why the circuits would be
unbalanced. I sorta checked out of physics somewhere between DC electricity
and AC and thermionic valves and electronics!!

Cheers

Den
 
D

Den

Jan 1, 1970
0
Hmm

I hadn't thought of that angle ... it's obvious when you state it clearly as
you have done.

I'm going to be using a step up transformer ... it's just I wondered if it
could be done this way ... I wasn't going to actually do it as it would
clearly be (at best) bad practice ... and as you have demonstrated
dangerous.

Thx

D

| I have a some European (i.e. 230V) kit that is frequency independant. In my
| house (120V) I have the usual split-phase arrangement (i.e . +/- 120V off
| the pole, some circuits fed with -120V and neutral, some with +120V and
| neutral, net effect is 120V where it's needed). I don't have any 240V
| outlets (i.e. -120V and +120V). If I wanted to run this kit is there any
| theoretical reason why I shouldn't wire it to each of two hots on separate
| 120V circuits (obviously making sure one is +120V and one is -120V). What
| about practical reasons?

If you attach a 240 volt device between the two opposite 120 volt hot lines
which are wired on separately protected circuits, you have a hazard if one
of those circuits is opened due to some fault. It can happen just because
you might switch off one of the circuits. The problem is that your device
is now a crossover between the opposite 120 volt lines. That puts the device
in series with everything on the opened circuit operating in parallel. This
combination now gets 120 volts divided up some way depending on the effective
resistance of each device. Some devices can be damaged with low voltage.
And the open circuit will still have voltage on it, creating a hazard if you
or someone else tries to work on that circuit.

240 volt devices must be either connected as the only device on the circuit
if there is a possibility of a single pole being opened (such as with fuses
as the protection), or must be connected to a 2-pole circuit breaker which
will open both poles should either is overloaded or faults.

Alternatively, you could use a 120 volt to 240 volt (or 230 volt) step up
transformer. If one of the wires on the 230 volt device is connected to
the chassis (often done with older equipment), you must ensure it connects
to the wire that is grounded. American 240 volt circuits cannot provide
that, but you could do it that way with the transformer to match what is
found in Europe.
http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
N

ns

Jan 1, 1970
0
Doable, if you use the 2 hot circuits from a split-plug circuit (i.e.,
protected by 2 ganged circuit breakers).

I've been using this approach for the last 17 years for a counter top
mixer/blender (Kenwood Chef) that is rated as 240 V.
It worked just fine using the voltage range of 208 (from an apartment
split-plug feed) to 240 V (from an detached house split-plug feed). 230
rated is really 230 +10/-6% (or is it +6/-10%?), so if you use the above
approach, you should be OK.
 
B

bushbadee

Jan 1, 1970
0
Very often laundry rooms have 240 volts to run driers and they use both
legs.
 
K

KR Williams

Jan 1, 1970
0
phil-news- said:
| Very often laundry rooms have 240 volts to run driers and they use both
| legs.

And they use the neutral, too.

Sometimes. Sometimes not. I believe my laundry room is a three
wire connection (I know my last house was, and I didn't buy a new
cord). All would be well if the appliance manufacturers didn't
cheat with 110V components. Even as is, it's not a big deal (but
not pure either).
 
[email protected] wrote:

Back when all these things were decided, though, they didn't know how to
make things as safe (e.g. separate ground wire), nor how to make sure no
one used the ground wire as a current conductor (GFCI),

A GFCI is not intended to prevent the use of a ground wire as
a current conductor. It is intended to protect you, by
interrupting the circuit if there is an imbalance (of about
5 mA or more) in current flow on the hot vs the neutral wires.
The idea is that a short in something you are holding runs
current through your body to ground, which could kill you.

It is specifically allowed by the NEC to be used where no
ground wire exists - thus can't be intended to be used to
make sure no one uses the ground wire as a current conductor.
See 406.3 (D) (3) in the 2002 code.

 
K

KR Williams

Jan 1, 1970
0
phil-news- said:
| In article <[email protected]>, phil-news-
| [email protected] says...
|>
|> | Very often laundry rooms have 240 volts to run driers and they use both
|> | legs.
|>
|> And they use the neutral, too.
|
| Sometimes. Sometimes not. I believe my laundry room is a three
| wire connection (I know my last house was, and I didn't buy a new
| cord). All would be well if the appliance manufacturers didn't
| cheat with 110V components. Even as is, it's not a big deal (but
| not pure either).

I have not seen a dryer that does not use the neutral. What I am told is
that the heating elements are connected between the 2 hot wires, but the
motor, which is not that big, is connected between 1 hot wire and neutral.
I guess that is the "cheat". Maybe motors for 120 volts are cheaper due
to mass market in them (technologically, there wouldn't be any difference).

No, the "cheat is that there is a ground (no neutral) and the
120V motor uses the return through the *ground* (it's wired to
the case). AIUI, the later codes require the fourth wire
(neutral), like they do with kitchen ranges.
Now it would make more sense to me to just go ahead and hook the motor to
240 volts, too. I'd rather have that. The question is, how much would I
be willing to pay extra for that, to have a possibly non-stock motor used,
and also to have the control circuits on 240 volts, to eliminate the neutral
wire entirely. Not much point in it.

Given the volume of widgets sold, I can't see it costing a dime
extra. There is no way anyone is going to use a drier on 120V
(well my MIL tried for a while, but that's another scary story).
But I'd still rather have an electrical system that didn't use neutral, and
no appliances depended on it. It would still have ground, and the secondary
transformer winding would still be grounded at the most central point to
have the least voltage to ground. For single phase that would be the center
tap as is common in North America, and for three phase it would be the center
wire of a WYE (or star) secondary.

I don't see the point. Very few appliances need the higher
voltage and the ones that do should have a separate circuit
designed for the higher load. I don't see the need for a 240V
circuit to power my bed lamp, alarm clock, cell-phone charger
(the only things normally on my bedroom circuit). Ok, there is a
1/2 ton AC on there for a couple of weeks in the summer too (were
I wiring the house it would have its own circuit - wire's cheap).
Big deal.
Then to make things more universally
compatible, both single phase and three phase would have the same voltage
between hot wires. If it were me picking that voltage, I'd go a bit higher
with 300. That would mean 150 volts to ground on single phase and 173.2
volts to ground on three phase. But the only voltage used would be 300.
Back when all these things were decided, though, they didn't know how to
make things as safe (e.g. separate ground wire), nor how to make sure no
one used the ground wire as a current conductor (GFCI), had all these bulb
sockets with metal base as one of the conductors, and didn't want to use
2 pole switches. And we can't change today because of so much installed
base of distribution and usage. Well, we still could stop using the neutral
on 240 volts and maybe adopt 240Y/139.

Too complicated. Why bother. I rather like things the way they
are. It's simple, cheap, and easily expandable (for values of
easy approximating the ease of opening a wall ;).
 
K

KR Williams

Jan 1, 1970
0
phil-news- said:
| In article <[email protected]>, phil-news-
| [email protected] says...
|> | In article <[email protected]>, phil-news-
|> | [email protected] says...
|> |>
|> |> | Very often laundry rooms have 240 volts to run driers and they use both
|> |> | legs.
|> |>
|> |> And they use the neutral, too.
|> |
|> | Sometimes. Sometimes not. I believe my laundry room is a three
|> | wire connection (I know my last house was, and I didn't buy a new
|> | cord). All would be well if the appliance manufacturers didn't
|> | cheat with 110V components. Even as is, it's not a big deal (but
|> | not pure either).
|>
|> I have not seen a dryer that does not use the neutral. What I am told is
|> that the heating elements are connected between the 2 hot wires, but the
|> motor, which is not that big, is connected between 1 hot wire and neutral.
|> I guess that is the "cheat". Maybe motors for 120 volts are cheaper due
|> to mass market in them (technologically, there wouldn't be any difference).
|
| No, the "cheat is that there is a ground (no neutral) and the
| 120V motor uses the return through the *ground* (it's wired to
| the case). AIUI, the later codes require the fourth wire
| (neutral), like they do with kitchen ranges.

Are you sure of that? I've seen these wired up, and they put the
white wire on the neutral bus, not the ground bus.

Could be. They are the same lug in the entrance panel. I guess
you can call it a neutral, since it is carrying current. ;-) It's
bonded to the case though. ...as my MIL found out.
Are you talking about a NEMA 6-30R or a NEMA 10-30R? I'm talking about
the 10-30R.

Not sure. I've only seen the thing twice (when I bought it and
when I moved).
|> Now it would make more sense to me to just go ahead and hook the motor to
|> 240 volts, too. I'd rather have that. The question is, how much would I
|> be willing to pay extra for that, to have a possibly non-stock motor used,
|> and also to have the control circuits on 240 volts, to eliminate the neutral
|> wire entirely. Not much point in it.
|
| Given the volume of widgets sold, I can't see it costing a dime
| extra. There is no way anyone is going to use a drier on 120V
| (well my MIL tried for a while, but that's another scary story).

I never suggested going with pure 120 volts. That would require 60
amps that way. Instead, what I am suggesting is to use only 240 volts,
instead of a mix of 240 volts for heating elements and 120 volts for
motor and control sorcuits.

I didn't say you did. My point was that a 240V motor, given the
volume of driers sold, shouldn't be any more expensive than a
120V motor. I have no clue why they use a 120V motor. Seems
pretty stupid to me, but there must be a reason.
|>
|> But I'd still rather have an electrical system that didn't use neutral, and
|> no appliances depended on it. It would still have ground, and the secondary
|> transformer winding would still be grounded at the most central point to
|> have the least voltage to ground. For single phase that would be the center
|> tap as is common in North America, and for three phase it would be the center
|> wire of a WYE (or star) secondary.
|
| I don't see the point. Very few appliances need the higher
| voltage and the ones that do should have a separate circuit
| designed for the higher load. I don't see the need for a 240V
| circuit to power my bed lamp, alarm clock, cell-phone charger
| (the only things normally on my bedroom circuit). Ok, there is a
| 1/2 ton AC on there for a couple of weeks in the summer too (were
| I wiring the house it would have its own circuit - wire's cheap).
| Big deal.

Almost nothing needs a particular voltage. The need is for some
amount of power (real or reactive as the case may be). For things
as small as a bed lamp, alarm clock, or cell-phone charger, 240
volts offers virtually no advantage.

Sure, my point is that most rooms have nothing in them that takes
any significant power, so 120V is good enough. Kitchens,
perhaps.
My suggestion for no neutral as a power configuration is more about
getting things on a singular standard voltage, and doing so in a
well balanced way, with a minimal ground potential. It's not that
things like bed lamp, alarm clock, or cell-phone charger need 240
volts, but rather, if they an everything else used 240 volts, then
the wiring would be simpler, and the ground potential would still
only be 120 volts (139 volts for three phase). In Europe, the 230
volt standard is between line and neutral/ground. So the ground
potential is the full amount.

I don't see many appliances in the home that need higher power
than can be delivered now at 120V. AC units, sure, but they
usually have dedicated circuits. I have a small window unit, but
it works fine off 120V too.
Eliminating the neutral leaves only one voltage, the line to line
voltage. Making the voltage higher means less current and even less
I^2*R losses in the wiring.

Sure, but I don't see this as a significant issue in a
residential dwelling.
|> Then to make things more universally
|> compatible, both single phase and three phase would have the same voltage
|> between hot wires. If it were me picking that voltage, I'd go a bit higher
|> with 300. That would mean 150 volts to ground on single phase and 173.2
|> volts to ground on three phase. But the only voltage used would be 300.
|> Back when all these things were decided, though, they didn't know how to
|> make things as safe (e.g. separate ground wire), nor how to make sure no
|> one used the ground wire as a current conductor (GFCI), had all these bulb
|> sockets with metal base as one of the conductors, and didn't want to use
|> 2 pole switches. And we can't change today because of so much installed
|> base of distribution and usage. Well, we still could stop using the neutral
|> on 240 volts and maybe adopt 240Y/139.
|
| Too complicated. Why bother. I rather like things the way they
| are. It's simple, cheap, and easily expandable (for values of
| easy approximating the ease of opening a wall ;).

Perhaps only because you are already accustomed to it? Obviously we are
not changing things. But if you had only know of a system like I suggest,
would you think making a change to add a neutral wire and allow things to
be run at half the normal system voltage be allowed, and have a different
value for three phase circuits?

The advantage of the system as it stands is that I can use 120V
for small things and glue two together for the biggies. That's
about as simple as it gets.
 
K

KR Williams

Jan 1, 1970
0
phil-news- said:
| Could be. They are the same lug in the entrance panel. I guess
| you can call it a neutral, since it is carrying current. ;-) It's
| bonded to the case though. ...as my MIL found out.

An entrance panel might do that.

Entrance panels *DO* do that. The ground and neutral are bonded
in the entrance panel. In this particular case the *RED* wire
was connected to the ground-strap and the white was hooked to the
hot. exciting when you touched the drier case! I found out jut
how exciting when I hooked a ground strap to the cold water pipe,
an zapped a 60A fuse.
But there should be separate neutral and
ground bus bars, just connected together in the entrance panel and kept
separate in subpanels.

Not necessary. In the entrance panel they can all be wired
together. Certainly in a sub-panel they're separated (I just had
to separate them in her house so we could sell it).
|> Are you talking about a NEMA 6-30R or a NEMA 10-30R? I'm talking about
|> the 10-30R.
|
| Not sure. I've only seen the thing twice (when I bought it and
| when I moved).

Grab this file and view the dimensions:

http://www.nema.org/DocUploads/569F336F-E550-4BD8-935019C2E658D5A0/WD6w.pdf

I can do that, but I'm not about to pull our laundry room apart
to measure. ;-)
| I didn't say you did. My point was that a 240V motor, given the
| volume of driers sold, shouldn't be any more expensive than a
| 120V motor. I have no clue why they use a 120V motor. Seems
| pretty stupid to me, but there must be a reason.

A motor can be made cheaper if it's windings are at a fixed voltage and
there is no option to rewire to a higher voltage, as would be the case if
the windings were paired with 4 leads each.

IIRC 600V wiring is required for all residential circuits. I
thought this was true for appliances too, but I could be wrong.
I'm not a power expert, as you've noted.
Since instead of a versatile
motor, you have to make separate ones for each voltage. Given the massive
market scale for 120 volt versions (for whatever reason, but perhaps due
to it being used for other appliances, too), the 240 volt version will
cost more because of the higher cost to inventory compared to sales
volume. Even if a single voltage motor over a dual voltage one saves
only $0.25, manufacturers will do such things.

I don't buy that argument. The gas/electric argument seems to be
better, but even that falls short. Motors wound for both are
ubiquitous. It's not rocket-surgery to have motors strapped for
whatever voltage.
|> Almost nothing needs a particular voltage. The need is for some
|> amount of power (real or reactive as the case may be). For things
|> as small as a bed lamp, alarm clock, or cell-phone charger, 240
|> volts offers virtually no advantage.
|
| Sure, my point is that most rooms have nothing in them that takes
| any significant power, so 120V is good enough. Kitchens,
| perhaps.

I'll still be putting a 6-20R or two in most rooms of my future house.

Maybe that's a good idea. Overkill, and you'll never get your
money back, but if that makes you happy... My father did the
equivalent sorts of things, though no one else cared.
The major room that won't have them is the bathroom (even though hair
driers pull a power level that really should use 240 volts).

I don't agree at all. Who needs more than a kW for a hair-
drier?! I'd rather *not* have 240V anywhere close to water. I
had 240V to my pool pump for the obvious reasons, but poolside
appliances ran off 120V. The 240V GFCI breakers were nutso too.

I have
seen countertop microwave ovens that use 240 volts, but never a hair
dryer. Usually they are wired on a dedicated circuit, and for the
planned one, it will get one. All the 6-20R's in the kitchen will be
GFCI protected at the subpanel adjacent to the kitchen, as will the
5-20R's. Both will have 120 volts to ground, which is the biggest risk
in a kitchen or other wet area.

....and you want 240V to the bathroom? My built-in
microwave/convection/range-hood is 120V. I know because I
replaced the thing a couple of years ago. No big issue there.
|> My suggestion for no neutral as a power configuration is more about
|> getting things on a singular standard voltage, and doing so in a
|> well balanced way, with a minimal ground potential. It's not that
|> things like bed lamp, alarm clock, or cell-phone charger need 240
|> volts, but rather, if they an everything else used 240 volts, then
|> the wiring would be simpler, and the ground potential would still
|> only be 120 volts (139 volts for three phase). In Europe, the 230
|> volt standard is between line and neutral/ground. So the ground
|> potential is the full amount.
|
| I don't see many appliances in the home that need higher power
| than can be delivered now at 120V. AC units, sure, but they
| usually have dedicated circuits. I have a small window unit, but
| it works fine off 120V too.

Sure, many things available that use 240 volts can also use 120 volts.
But I prefer to use them at 240 volts regardless. The only things that
I would be using at 120 volts are those that do not have any 240 volt
versions (which is most things).

I don't (prefer). I'd rather leave things at the lowest voltage
possible. 120V is just peachy for 90% of my uses. Dedicated
outlets (240V) work for the rest.
|> Eliminating the neutral leaves only one voltage, the line to line
|> voltage. Making the voltage higher means less current and even less
|> I^2*R losses in the wiring.
|
| Sure, but I don't see this as a significant issue in a
| residential dwelling.

We see things differently.

Obviously. The IR drop on most residential circuits is trivial,
IMO. My cell-phone charger isn't causing too much in the way of
global warming, the wires in the wall feeding it far less so.
| The advantage of the system as it stands is that I can use 120V
| for small things and glue two together for the biggies. That's
| about as simple as it gets.

But if the system had always been just 240 volt, would you really have
thought "Gee, if only I could have a current carrying conductor back to
the grounded center tap, I could run things on 120 volts, even though
I would now have double the current and no less risk of ground shock".

No, I wouldn't have had any such thought. I don't want 240V to
supply a tenth of an amp. There are so few places in my house I
need such huge power (and those have dedicated outlets) that I
see wiring 240V everywhere as a complication.
BTW, shared neutral wiring effectively gets you the same benefit of less
current for a given total (and balanced) load. Two 60 watt lights with
one on each pole of a shared neutral 3-wire circuit will draw a total of
0.5 amps, the same as a 120 watt 240 volt light would.

Obviously, but now I need both 120V and 240V lamps. No thanks.
Leave the trivial loads at 120V.
But to get that
advantage you also have to have the risk of a shared neutral circuit.

Huh? That's the whole point. We don't have any "shared-
neutral" loads. THe ones that are shared are designed to do so.
But that is a viable option with a 2-pole circuit breaker that ensures
both poles are cut off if either overloads. But I don't plan to do any
shared neutrals.

Of course. Why are you bringing in this strawman??

THe system works remarkably well, and has for many years. Many
smart people have done much to make it safe. I'm not about to
throw out all that's been learned over the last century and do
something different because I *THINK* I know better. I'll trust
the NEC, thanks.
 
K

KR Williams

Jan 1, 1970
0
phil-news- said:
| IIRC 600V wiring is required for all residential circuits. I
| thought this was true for appliances too, but I could be wrong.
| I'm not a power expert, as you've noted.

I've seen wiring rated only 300 volts at the local big box store.

Really? I thought all wiring hat to be rated for 600V. If
you're right, this isn't goodness. Again, if I'm wrong, I
appreciate you pointing out my errors!
|> Since instead of a versatile
|> motor, you have to make separate ones for each voltage. Given the massive
|> market scale for 120 volt versions (for whatever reason, but perhaps due
|> to it being used for other appliances, too), the 240 volt version will
|> cost more because of the higher cost to inventory compared to sales
|> volume. Even if a single voltage motor over a dual voltage one saves
|> only $0.25, manufacturers will do such things.
|
| I don't buy that argument. The gas/electric argument seems to be
| better, but even that falls short. Motors wound for both are
| ubiquitous. It's not rocket-surgery to have motors strapped for
| whatever voltage.

A general purpose motor would be. One specifically designed for
appliances where availability of 120 volts is always assumed (and in
the gas dryer case, where 240 volts might not be), i cheaper made with
only a single voltages, rather than reconfigurable.

I see others who have raised that argument here. It makes sense,
sorta, but multiple windings (series or parallel) aren't a biggie
either. All the stationary power-tools in the same cost region
have such taps, including those with the cheap universal motors.
This is the only "reason" I've seen, but it's hard to buy this
one too.
|> The major room that won't have them is the bathroom (even though hair
|> driers pull a power level that really should use 240 volts).
|
| I don't agree at all. Who needs more than a kW for a hair-
| drier?! I'd rather *not* have 240V anywhere close to water. I
| had 240V to my pool pump for the obvious reasons, but poolside
| appliances ran off 120V. The 240V GFCI breakers were nutso too.

It's only 120 volts to ground, same as a 120 volt circuit.

Of course. Tell me something I don't know. That is indeed the
beauty of the system. One can split off the low-power circuits
from the high-power circuits and they all play nice.
It won't
make any difference near water. What do you think is wrong with 240
volt (2-pole) GFCI breakers?

Nothing, except the expense. 2-pole GFCI breakers are
*expensive*. 120V GFCI outlets are dirt cheap. ...and work just
as well for small loads.
|> I have
|> seen countertop microwave ovens that use 240 volts, but never a hair
|> dryer. Usually they are wired on a dedicated circuit, and for the
|> planned one, it will get one. All the 6-20R's in the kitchen will be
|> GFCI protected at the subpanel adjacent to the kitchen, as will the
|> 5-20R's. Both will have 120 volts to ground, which is the biggest risk
|> in a kitchen or other wet area.
|
| ...and you want 240V to the bathroom? My built-in
| microwave/convection/range-hood is 120V. I know because I
| replaced the thing a couple of years ago. No big issue there.

If hair driers were available in 240 volt, then yes, I'd get that ...

Are you talking about US 240V or the Europen 240V? I wouldn't in
either case, but for different reasons.
if I still had hair.

;-)) I have more hair than my wife, which pisses her off
constantly. I cannot stand hair dryers, but she insists on using
them. Go figure.
Microwave ovens can be had for 240 volt, and that
is my plan to get.

I think mine could be wired for 240V, but that wasn't of interest
since the house is already standing. I wasn't about to re-wire
the place.
And no, I don't want 240 volt in the bathroom, but
the reason is because I don't think there ever will be any bathroom
appliances for 240 volt (at least not in the USA). But otherwise I
would have no objection to 240 volts there, as long as it is center
tap grounded so the ground potential is only 120 volts.

Absolutely. I see no reason for 240V anywhere that massive loads
aren't. AC units, sure. Hair driers, please.
I'd almost consider having no outlets at all in the bathroom. But there
are still people around with hair.

I have a beard too. Gotta plug that Wahl-wart in somewhere! ;-)
|> Sure, many things available that use 240 volts can also use 120 volts.
|> But I prefer to use them at 240 volts regardless. The only things that
|> I would be using at 120 volts are those that do not have any 240 volt
|> versions (which is most things).
|
| I don't (prefer). I'd rather leave things at the lowest voltage
| possible. 120V is just peachy for 90% of my uses. Dedicated
| outlets (240V) work for the rest.

Then why not run everything on 12 volts?

Absurd. The occasional vacuum cleaner would object.
The shock hazard to ground is only 120 volts on a center tapped 240.
In Europe, that is different, as it is 230 volts to ground there, plus
or minus 10 volts depending on which country.

....which is exactly what I've been arguing! I much prefer the
"Edison-connection" to what the right-pondians use. Pehaps we're
yelling past each other?
Instead of having a 240 volt transformer center tapped to give you
two sides of 120, why not go with 120 volts center tapped at 60?
Wouldn't that be even less of a shock hazard?

Because perhaps it would make a mess of 240, when it's needed?
| No, I wouldn't have had any such thought. I don't want 240V to
| supply a tenth of an amp. There are so few places in my house I
| need such huge power (and those have dedicated outlets) that I
| see wiring 240V everywhere as a complication.

One tenth of an amp at 240 volts is only 24 watts. That's not huge power.
And the voltage is not so huge, either.

I'll bet half my line cords don't use too much more than this.
Certainly if you go to 100W there are only a *few* widgets over.
If I could get everything in 240 volt versions, I'd do that.

....and I think you're nuts. ;-)
|> BTW, shared neutral wiring effectively gets you the same benefit of less
|> current for a given total (and balanced) load. Two 60 watt lights with
|> one on each pole of a shared neutral 3-wire circuit will draw a total of
|> 0.5 amps, the same as a 120 watt 240 volt light would.
|
| Obviously, but now I need both 120V and 240V lamps. No thanks.
| Leave the trivial loads at 120V.

That isn't a 240 volt lamp. That could be 2 120 volt lamps on each side
of a shared neutral circuit.

Now you're demanding that I need four-wire 240V to every outlet
in my house? I don't think so!

I think you're wandering around this whole issue, so perhaps
you'd better define what exactly your "perfect" house would look
like.

|> But to get that
|> advantage you also have to have the risk of a shared neutral circuit.
|
| Huh? That's the whole point. We don't have any "shared-
| neutral" loads. THe ones that are shared are designed to do so.

A 240 volt circuit is equivalent to a shared neutral circuit; both have
a 120 volt shock hazard.

Good grief!
|> But that is a viable option with a 2-pole circuit breaker that ensures
|> both poles are cut off if either overloads. But I don't plan to do any
|> shared neutrals.
|
| Of course. Why are you bringing in this strawman??

Just to show how 240 volts really works. But you just don't need the neutral.

You just said you did above. You are wandering again.
| THe system works remarkably well, and has for many years. Many
| smart people have done much to make it safe. I'm not about to
| throw out all that's been learned over the last century and do
| something different because I *THINK* I know better. I'll trust
| the NEC, thanks.

Much of what we have is, however, limited to the course of history. Why
we have a neutral wire at all is a legacy from days when they though it
was an adequate form of grounding. Later the smarter people realized it
was not, and thus we now have a true grounding wire. But getting rid of
the neutral wire isn't something that can be done just because one is or
is not smart; it's an economic issue because things depend on it.

The neutral wire is a wonderful thing. It allows us to have both
120V and 240V, where it's needed. ...and both at the same time,
where needed. ...another great invention of "Edison".
 
D

Den

Jan 1, 1970
0
Hmm, it certainly wouldn't require a dedicated circuit in the UK! 2400W at
240V is only 10A. Standard British sockets are rated to 13Amps (each plug
has a replacable fuse - so the fuse rating may be 1A for a lamp, but 13A for
a microwave). Circuits are often rated at 30A. I used to run a 3kW (i.e.
12.5A) electric kettle quite happily off the standard wall socket and
another 3kW heater off another on the same circuit.

I was gobsmacked at the limitations of the standard outlets when I moved to
the US - 15A at 110V - 1.6kW.

Heigh-ho!

D

| Out of curiosity, do kitchen (and other) non-built-in appliances in Europe
| and other 230V countries frequently have power ratings of more than 1500
| watts? In the US, anything that uses NEMA 5-15P plugs (that is, nearly
| everything) is limited to about 1500 watts.

I've seen a microwave oven rated for as much as 2400 watts. But that is
here in the US and it had a 6-15P on it. I'm sure they could use them in
Europe, too. In both cases it would require a dedicated circuit.


| A history question: My 60 year old house has some original outlets that
| have slots that can accept either vertical and horizontal prongs on the
| plug, but no ground pin. (imagine something that can accept any of
| NEMA 5-15P, 5-20P, 6-15P, 6-20P, if you hacksaw off the ground pin!)
| Why? DC?

I remember seeing those, too. I never did figure out the reason for it.
http://ka9wgn.ham.org/ |
--------------------------------------------------------------------------
---
 
D

DarkMatter

Jan 1, 1970
0
Hmm

I hadn't thought of that angle ... it's obvious when you state it clearly as
you have done.

I'm going to be using a step up transformer ... it's just I wondered if it
could be done this way ... I wasn't going to actually do it as it would
clearly be (at best) bad practice ... and as you have demonstrated
dangerous.

The 120 to 230 volt step up transformer IS the way to go for safety,
AND for proper operation. The only difference will be what frequency
your 230 volt device was intended to be operated at.

Learn why top posting is such a bad thing in Usenet. Then refrain.
 
D

DarkMatter

Jan 1, 1970
0
| Very often laundry rooms have 240 volts to run driers and they use both
| legs.

And they use the neutral, too.

A dryer element is purely resistive, and it wouldn't make a shit.

That element could easily be driven in such a way. The motor and
timer are driven off one 120 volt side, and use the neutral.

The heating element would not need it were it a single element, but
they are rarely anything other than split pairs with the center on
neutral.

You seem drier than you were a few minutes ago. Perhaps you should
go check your clothes dryer to see if it has finished its cycle. :]

BushLAMEEE's use of that "b" in front of his posts has to be one of
the most lame behaviors in any professional group I have yet seen.

Topic header appropriately trimmed. Assholes appropriately ignored.
 
D

DarkMatter

Jan 1, 1970
0
| In article <[email protected]>, phil-news-
| [email protected] says...
|>
|> | IIRC 600V wiring is required for all residential circuits. I
|> | thought this was true for appliances too, but I could be wrong.
|> | I'm not a power expert, as you've noted.
|>
|> I've seen wiring rated only 300 volts at the local big box store.
|
| Really? I thought all wiring hat to be rated for 600V. If
| you're right, this isn't goodness. Again, if I'm wrong, I
| appreciate you pointing out my errors!

All I know is I have seen the wire with that rating available for sale.
Whether it is allowed or not, I cannot say. I'd expect to have problems
using it for 480 volts.

If you would be comfortable with wire rated for 600 volts when using it
on 480 volts, why not be comfortable with wire rated for 300 volts when
using it on 240 volts?

There are UL ratings for PVC, THHN, and various other wire
sheathings. The military rates teflon wire of a particular type at
1000V, whereas UL only gives it a 600V rating.

I see 300Volt PVC wiring in device chassis all the time.

Even the national laboratories buy COTS now, and all that mil
scrutiny is gone, or much of it, anyway. The EIA standards used in
most commercial electronic labs allows for 300 volt PVC. I think that
baseline NEMA is 600V, and perhaps that of THHN or better. Baseline
NEC is for PVC, but I don't know the ratings scheduled. As far as I
know, the UL boys are the folks that do the insulation ratings though.