Shunt??
Discussion in 'Home Power and Microgeneration' started by Jack Russell, Aug 11, 2005.
  1. Jack Russell
    Jack Russell Guest
    I have been looking at meters for my solar system. It is very simple and
    small at this point but it will expand.
    QUESTION: What is a shunt and why do I need or not need one in a meter.
    Thanks, Paul...
  2. A meter shunt is a precise, low resistance resistor that is placed in
    the wiring to the item that you want to monitor. A low resistance
    shunt has minimal effect on system operation because the voltage
    drop is very small.
    Shunts are rated at xx millivolts at yy amps (50mv 50A for instance).
    They are used with millivolt meters that are calibrated to read amps
    with a specific shunt.
    The wiring from the shunt to the meter can be small gauge as there
    is very little current in the meter leads. Simple switches can be used to
    connect several shunts to one meter.
    Bill Kaszeta
    Photovoltaic Resources Int'l
    Tempe Arizona USA
  3. A shunt is a resistor having a very low but precise resistance.
    A meter - analog or digital - doesn't generally measure current in any
    direct sense. Rather, it measures the voltage across a resistance that
    is placed in series with the current of interest.
    You want that resistance to be very small so as not to interfere with
    the circuit and draw any significant power from it.
    When currents are large - e.g. when you're making toast with a 12V
    system and drawing 150A from the batteries - the resistor you're
    measuring current with has to be a very low value or it would
    dissipate a LOT of power.
    In this example the system would most likely have a "500A/50mV" shunt.
    This means that only 50mV would be dropped across the shunt at 500A.
    From this we can calculate that the shunt has a resistance of:
    R = E/I = 50mV/500A = 0.05V/500A = 0.0001 Ohm = 100microOhms
    ....a very small value indeed.
    The voltage across the shunt at 150A would be
    E = IR = 150A * 0.0001Ohm = 0.015V = 15mV
    And the power dissipated by the shunt...
    P = EI = 15mV * 150A = 2.25W
    A resistor dissipating even a few Watts isn't something you want to
    touch.
    With the exception of magnetically-coupled ones, any
    current-measurement meter needs a shunt. It's just that if you're not
    measuring a lot of current, the shunt may be small enough to fit
    inside the meter.
    -=s
  4. Jack Russell
    Jack Russell Guest
    The meters that I have been looking at have the shunt integrated into the
    meter (I assume). So what you are saying is that I would be better with a
    "Shunted" meter...
  5. daestrom
    daestrom Guest
    Some intermediate sized ammeters have the shunt 'built-in'. This sounds
    like what you're seeing. These are called 'internal-shunt ammeters'. The
    'good' is that you don't have to worry about matching the correct mV meter
    with the correct shunt. The bad news is you have to wire the meter into the
    main current path. So you have to put the meter somewhere not too far out
    of the way of the circuit path.
    External-shunt meters, have the others have said require two parts, the
    shunt and a precious mV meter. Depending on the type of mV meter, the total
    resistance of the leads to and from the mV meter can be important. Most
    such meters also include a factor of 'total lead resistance'. Too much or
    too little resistance and the accuracy is affected. But the nice thing
    about these is the shunt is the only part that needs to be in the power
    circuit. So a shunt between your batteries and charger (perhaps in the
    garage), can have small-gauge meter leads (properly fused) run to some
    central monitoring panel. Meter leads running over 100 ft are not uncommon.
    For really high current applications, 'internally shunted' meters are rare.
    Almost always see external shunts when you get up into the hundreds of amps
    range.
    daestrom
  6. Ecnerwal
    Ecnerwal Guest
    A shunt is a very small resistance, which is used to generate a small
    voltage from a large current, so that a small voltmeter (marked in Amps)
    can indicate the amperage passing through the shunt.
    In practice, with today's electronic voltmeters, you can do without one
    by using one of the cables you'll have in there anyway as a shunt, but
    not adding any _extra_ resistance in the form of a shunt and its
    associated connections. You will need to convert a voltage measurement
    (from each end of the cable) into a current measurement (using the
    resistance of the cable), and this may not be _quite_ as precise across
    wide temperature ranges as a "real" shunt, but with a modern digital
    voltmeter (more or less infinite input resistance) it's Pretty Darn
    Good; especially if the operating temperature is reasonably close to the
    temperature at which you measured the cable resistance (or take
    resistance measurements at various temperatures if you want to be picky,
    and use the closest one).
  7. Jack Russell
    Jack Russell Guest
    THANKS FOLKS!! for all your help