    Have a panel with a trouble because log is full but cant figure out how to clear log.Any help would be appreciated.

    Panel is safetech series 1000
     
    Last edited: Dec 29, 2010
  2. pauljschulte

    pauljschulte

    2
    0
    Dec 29, 2010
    found my answer

    1.hold select and press enter
    2.use select to scroll to log
    3.press enter and it will flash between view log and clear log
    4.press select when it shows clear clog
    5.press enter and it shows....sure?then press enter and it says done.
    6.reset and your good to go

    THANKS ALL!!
     