RS Logic AB PLC Timer Problem

Discussion in 'General Electronics Discussion' started by Yiven, Jan 30, 2018.

  1. Yiven

    Yiven

    1
    0
    Jan 30, 2018
    I have a RS Logic AB PLC used for over ten years, it work well before, but not sure why the output logical is wrong right now, it seems the PLC timer not work correct, the timer's setting time seems be set to 0, and the outputs without delay in betweens (was work well with setting delay), can somebody share the experience about this situation?
     
  2. Minder

    Minder

    2,834
    586
    Apr 24, 2015
    Not sure what the problem is as you describe it?
    Try programming a separate rung with another timer, or just test a rung with the timer in it.
    Post a sketch of the rung in question.
    M.
     
  3. JWHassler

    JWHassler

    77
    16
    Dec 22, 2014
    Is there a backup battery in this device?
    "ten years" and "timer setting =0" make one suspect that.
     