Repair UPS Santak

Discussion in 'Troubleshooting and Repair' started by troiuuuu, Mar 27, 2016.

  1. troiuuuu

    troiuuuu

    4
    0
    Mar 27, 2016
    I use UPS Santak 1kva/700w for 4 years, But when UPS off, UPS do not run and Fault with same image below.
    How can I solve UPS?
    [​IMG]
    THanks and best regard
     
  2. dorke

    dorke

    2,342
    664
    Jun 20, 2015
    Maybe this can help.
    What is the model number?
     
  3. 73's de Edd

    73's de Edd

    2,743
    1,131
    Aug 21, 2015
    .


    Sir troiuuuu. . . . . . .

    ( But not Troi oi ? )

    The very MOST common fault of that and UPS's in general is the degradation and capability of the unit to still provide full voltage and current drain capabilities from its battery after years of use.
    Pull the covers and take a voltage reading of the battery with no loading and then activate the unit to see how much that voltage then draws down.
    Give us the battery voltage and current rating . . .from the units battery.

    73's de Edd


    .
     