We have been using Reliance Flexpak 3000 DC drives to supply the
conveyance drives on our machines for about 7 years now and have
experienced frequent motor bearing failures due to voltages being
induced into the rotor and discharging through the tail bearing. I
realize this is a common problem in the drive industry but we also use
many other types of drives AC PWM, AC Sensorless Vector Drives, And
Minpak DC drives from many other manufacturers including Allen Bradley,
Lancer, Toshiba and we have not seen the bearing failures with these
other drive systems.
Does anyone have any suggestions to prevent these effects and
limit the voltages induced. We have run tests by isolating motors and
found 70 VAC on the motor casing to ground. In talking with Reliance
support they suggested building a filter on the output of the drive to
smooth out the waveform but they couldn't spec out capacitor and
inductor values because each filter application would be speed, load
dependant.
Thanks in advance for any help
conveyance drives on our machines for about 7 years now and have
experienced frequent motor bearing failures due to voltages being
induced into the rotor and discharging through the tail bearing. I
realize this is a common problem in the drive industry but we also use
many other types of drives AC PWM, AC Sensorless Vector Drives, And
Minpak DC drives from many other manufacturers including Allen Bradley,
Lancer, Toshiba and we have not seen the bearing failures with these
other drive systems.
Does anyone have any suggestions to prevent these effects and
limit the voltages induced. We have run tests by isolating motors and
found 70 VAC on the motor casing to ground. In talking with Reliance
support they suggested building a filter on the output of the drive to
smooth out the waveform but they couldn't spec out capacitor and
inductor values because each filter application would be speed, load
dependant.
Thanks in advance for any help