Rate of Rise detectors

A quick question on how to hook up the Rate of Rise sensor. I am
assuming it gets hooked up to the proper zone and the zone set as it
would be for a smoke alarm.
 
R

Robert L. Bass

Jan 1, 1970
0
A quick question on how to hook up the
Rate of Rise sensor. I am assuming it
gets hooked up to the proper zone and
the zone set as it would be for a smoke
alarm.

That is correct. Program it as a fire alarm zone. Wire it across any zone
which can be programmed for fire. Since it's a non-powered device you
needn't worry about power rest like a smoke detector.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
2291 Pine View Circle
Sarasota · Florida · 34231
877-722-8900 Sales & Tech Support
http://www.bassburglaralarms.com
=============================>
 
S

Stanley Barthfarkle

Jan 1, 1970
0
That is correct. One thing to keep in mind when wiring a heat detector, or
any fire zone for that matter, is that all devices on the same zone loop
should be wired in parallel, since fire devices use "N/O" (normally open)
contacts, as opposed to Intrusion zones such as door sensors, motion
sensors, etc, which are "N/C" (normally closed) and would be wired in
series.

An explanation of series and parallel wiring can be found with a Google
search on the subject.
 