    I'm going to have a pole building type barn built. Can I place non-metallic
    conduit under the concrete slab before it's poured such that it can be
    utilized as an electrical raceway? All I want to do is distribute some
    power to an electrical floor lift that will be in the middle of one of the
    12 foot wide bays. thanx

    Don
     
  2. Rich.

    Rich. Guest

    Yes, PVC conduit is designed for just such a purpose.
     
  3. Dean Hoffman

    Dean Hoffman Guest

    Another question. Does he have to use expansion fittings for pvc
    that will be in concrete?
     
  4. Rich.

    Rich. Guest

    Encased IN concrete or run under a concrete slab?
    How long of a run?
    Does the conduit cross any building expansion joints?
     
  5. Dean Hoffman

    Dean Hoffman Guest

    I don't know the particulars. It was just a hypothetical question.
     
  6. Rich.

    Rich. Guest

    I'm not try to bust your hump, but knowing the particulars can mean the
    difference between a correct or an incorrect answer.
     
  7. Don S.

    Don S. Guest

    I figure I should put the nonmetallic conduit in a trench below the concrete
    before it is poured. The run probably won't be more than 30 ft. There are
    no building expansion joints. Also, is this something the inspector needs
    to see before I pour the slab?

    Don
     
  8. Rich.

    Rich. Guest

    Yes the inspector needs to see it before the slab is poured.
     