How does the amount of power a transmission line can handle vary with its
voltage and the distance? In other words, how much power could a 10 mile
long 69kV line carry during normal usage (excluding unusual conditions
that may produce temporary overloads)? Or, put another way, if I had to
transmit 100 megawatts 20 miles, what voltage would be necessary?

How does the answer vary if there are two circuits used rather than one?
Is it just double?

I know the size of the conductors affects the answer, I'm curious about
the largest commonly used size for a given voltage.
 
J

JohnR66

Jan 1, 1970
0
Michael Moroney said:
How does the amount of power a transmission line can handle vary with its
voltage and the distance? In other words, how much power could a 10 mile
long 69kV line carry during normal usage (excluding unusual conditions
that may produce temporary overloads)? Or, put another way, if I had to
transmit 100 megawatts 20 miles, what voltage would be necessary?

I'm not a power transmission engineer, but to send that kind of juice that
far, would require six figure voltages or you have to use expensive, heavy
cables. At 69KV you're around 1000 amps on each leg.
How does the answer vary if there are two circuits used rather than one?
Is it just double?

Half the current, so it is possible to use lower transmission voltages.
I know the size of the conductors affects the answer, I'm curious about
the largest commonly used size for a given voltage.

Yes, it would be interesting if a power transmission engineer would jump in
here.
John
 
B

Beachcomber

Jan 1, 1970
0
I'm not a power transmission engineer, but to send that kind of juice that
far, would require six figure voltages or you have to use expensive, heavy
cables. At 69KV you're around 1000 amps on each leg.


Half the current, so it is possible to use lower transmission voltages.


Yes, it would be interesting if a power transmission engineer would jump in
here.
John
I'm not a power transmission engineer, but I did stay at a Holiday Inn
last night... :>

My old college reference book gives these capacity examples for a
single-circuit, 3 phase transmission line.

138 kV ---> 80,000 kW
345 kV ---> 500,000 kW
765 kV ---> 2,500,000 kW

There are other specific values for factors such as sag, conductor
size, overhead vs. underground, etc. The above figures are ballpark.

The important relationship is that the theoretical power capacity
increases as the 'square' of increased voltage, thus the higher
voltages are much more efficient at transmitting large quantities of
power, with all else being equal. The practical upper limit for
voltage, however, is determined by the point at which corona breakdown
takes place, and, of course, the size-expense of the insulators,
bushings, conductors that require spacers, extra surface area, etc.

Double circuit towers essentially give you redundancy and double the
capacity of one three-phase line, but with the limitations of limited
work clearances for maintenance and the potential dangers and
undesirable effects of inductive coupling when a de-energized line is
situated next to an energized line.

Also, theoretically, high voltage DC is more efficient than AC for
long distance and large loads since there is only resistance and no
reactance, opposing the current flow. In practice, DC transmission is
more complex and expensive since AC-DC conversion must be done at
either end of the line.


Beachcomber
 
B

Beachcomber

Jan 1, 1970
0
138 kV ---> 80,000 kW
345 kV ---> 500,000 kW
765 kV ---> 2,500,000 kW

There are other specific values for factors such as sag, conductor
size, overhead vs. underground, etc. The above figures are ballpark.
Also, during the early years of the 20th Century, it was determined
that efficient AC power transmission could be done in the range of
about 1000 volts/mile, as a minimum.

Beachcomber
 
D

Don Kelly

Jan 1, 1970
0
--------------
P =[(Vs*Vr)sin(theta)]/Zo =(SIL)sin(theta)
where Vs and Vr are sending end and receiving end voltages in KV (line to
line )
P is the power transmitted in MW (total)
Zo is nearly root (L/C) where L and C are the inductance and capacitance
per mile (Resistance can be neglected in most cases) and theta is the angle
between the sending and receiving end voltages(line to neutral) .
Outside limit on theta is 30 degrees (approx 0.12 degrees/mile) to maintain
a stability margin and 15-20 degrees is better.
A rough estimate for Vs =Vr is that Vs^2=Mw*miles for a 30 degree phase
shift which puts the levels above at about 230-240 miles at the 30 degree
limit and 150-200 miles as a practical limit. Certainly longer and shorter
lines exist and power capacity increases or decreases accordingly.

Lots of factors involved but resistance is usually (except for short lines)
the least of these. For HV lines, bundled conductors are used to reduce
surface fields as well as inductance and generally the mechanical
requirements mean that the conductor current capacity is not a problem. This
also means that Zo for high voltage lines is about 250-275 ohms vs 350-400
ohms for single conductor, lower voltage lines. (so for a 20 degree phase
shift at 765KV and a loading of 2350MW the distance would be about 170
miles. Whether this load could be transmitted a longer distance would depend
on a host of other factors.
 
D

Don Kelly

Jan 1, 1970
0
----------------------------
Michael Moroney said:
Thanks for the replies.

Another question: How do they normally transfer power from point A to
point B when there are multiple lines of different voltages? I'm thinking
as an example of a specific case where A and B are substations, there's a
large power source adjacent to A (so power normally would flow from A to
B), and A and B are connected with multiple lines: 2 345kV, 2 138kV, and
2 69kV. (The 69kV lines go a different route and feed 3 smaller
substations along the way, and in normal use may be broken into 2 parts so
no power goes from A to B along them, I don't know. The other lines have
no taps between A and B)

Would they normally try to run most of the loads at substation B off the
lower voltages while passing the 345kV through, would they load B so
power is drawn proportional to each line's capacity, or can they somehow
"parallel" the 138kV lines with the 345kV with 345-138 transformers at
each end and something (what?) to balance the power according to capacity?
345kV and 138kV lines continue past B, also off from A.

Just curious.

There are many different schemes in the substations The lower voltage lines
would be the oldest and would come from nominal 69KV busses to 69KV busses
at B .The same thing would be the case for the 138 and 345KV lines. As the
system grew, there would be a need for more transmission capacity but that
doesn't mean throwing out existing infrastructure- it gets demoted to a
"lower" level. The 345KV line is now the backbone of the system while the
69KV mainly serves secondary loads. Depending on needs the three systems
may be independent or can be interconnected at each end by transformers in
the substations. There would be little or no need for control of individual
lines as the power handling capacity of each is related to the square of the
voltage level and, generally there is a natural balance that takes place.
The lower voltage lines would be feeding the smaller loads at the in between
substations while the 345KV line would bypass these (uneconomic to feed
these loads from the 345KV lines) and only feed the major substation at B
from which there may be a feed back to intermediate points at the lower
voltage. Think of a net made with strong ropes, interliked with lighter
ropes and cords.
 
D

Don Kelly

Jan 1, 1970
0
----------------------------
Michael Moroney said:
Thanks for the info.


That certainly appears to be the case. The 69kV are on wooden poles, and
while one of the 345kV lines is older than the 138kV towers, it's because
they replaced two single circuit set of pylons with 2 circuit tower, to
make room for the other 345kV line.


Are you saying that if I have a 345kV line, a parallel 138kV line
connected to the 345 line with 345-138 transformers at each end, and a
parallel 69kV line connected with appropiate transformers at each end,
the power will naturally balance itself over the lines in a reasonable
fashion without additional controls?
------
Basically yes. To analyse a particular situatio would require sufficient
line data and load data to allow a load flow study which is a common
procedure even for situations involving hundreds to thousands of lines where
thousands of simultaneous non-linear equations have to be solved- quickly.
What happens when the routes are different? Consider an equilateral
triangle A B C where the legs are long enough that phase shift is
significant, and you wish to move power from A to B using both A-B and
A-C-B paths (all paths same voltage), and a smaller load at C.
----
The flow would depend on all the loads but note that the voltages at A and B
are the same for both lines. Is there a chance of overloading one line or
the other- yes- but to actually determine the flow on both lines requires
analysis based on sufficient knowledge of the line parameters and operating
conditions.
--------
 
D

Don Kelly

Jan 1, 1970
0
----------------------------
John Gilmer said:
It will "balance out" but the balance point may not be where you like it.

One would want to send the most current over the link with the least
losses.
One would model it as there independent voltage sources feeding three
resistors connected to ground at the receiving end. The total current is
what the load demands. The resistances are scaled with the square of the
voltage. (A 1 ohm resistance on a 50 K line scales as 4 ohms on the 100
K
line.) The currents are scales with the inverse of the voltage. You
throw in some linear restraints (the maximum current on each line) and
you
have a problem that a bright high school student could solve but that your
typical EE profession would not attempt untill you came up with his fee or
a
charge number for his time sheet.
-----------
Unfortunately that would lead to the wrong answer. A resistance model is not
applicable as the current distribution is mainly controlled by reactance
which is typically far greater than the resistance. Power flow on a given
line depends on the voltage , reactance and phase angle with resistance
having relatively little effect - The easy approximation simply ignores line
losses. There is no way to avoid the use of complex numbers unless you want
to go back to differential equations. Scaling is easy- it's called the per
unit system-done all the time by utility engineers.

Some idea of what exists is important in trying to set up a model.

In this case, you have 3 busses, a known voltage magnitude at one of them
and known power and reactive loads at the others- Only 5 non-linear
simultaneous equations are needed to get a correct answer (or an
approximation if line/source resistance is ignored). This is not a difficult
problem but somewhat beyond high school in general.
Oh, yes, the negligable (with respect to that in the lines) phase shift in
the transformers can be included.
--

Don Kelly [email protected]
remove the X to answer

------------snip------
 