PIC based Pt100 RTD temp sensor circuit
Discussion in 'Electronic Basics' started by MarkMc, Jul 5, 2005.
  1. MarkMc
    MarkMc Guest
    Can anybody give me any hints ideas or circuits to allow me to read the
    temperature from a Pt100 RTD probe in to a PIC microcontroller?
    Regards,
    Mark
  2. Dan Hollands
    Dan Hollands Guest
    There are 3 issues
    1. convert the change in resistance into an analog signal
    2. digitize the analog signal and get the digital value into the
    microcontroller
    3. convert the digitized value into real units
    Which are you concerned about?
    Dan
    Dan Hollands
    1120 S Creek Dr
    Webster NY 14580
    585-872-2606
    www.QuickScoreRace.com
  3. The signal from an RTD is very small, so you need a low offset, low
    drift amplifier to bring the signal up to a range that is appropriate
    for the PIC A/D converter.
    If you are determined to roll your own amplifier, I suggest you visit
    the various op amp manufacturers' sites and look for application noted
    for platinum RTDs.
    For example:
    http://pdfserv.maxim-ic.com/en/an/AN3450.pdf
    http://www.national.com/nationaledge/dec04/article.html
  4. MarkMc
    MarkMc Guest
    I had a read of the MAXIM application notes, which use the MAX197 IC
    and a couple of op amps for amplification. This seems to be perfect,
    but the only problem is that it costs £20 for a single 28-pin DIN
    MAX197, which makes it a bit unviable for me. It is a one-off personal
    project, but others on my brewing forum may well want to build units
    themselves.
    I think I understand what's required at a high level, but my
    electronics isn't up to it at the low-level. I need a range of 0C to
    100C and 0.5C accuracy/resolution for my application.
    High level things I think I need (high-level block diagram)
    4-wire PT100 RTD
    "Something" to generate the excitation current - I think this needs to
    be extremely accurate and invariable.
    Something to amplify the small voltage across the RTD in to the range
    of an ADC. Looks like NS ML4140A-2.500 is used for this in the links
    above?
    An ADC to convert the analogue signal in to a format for my PIC to use.
    Are there not PIC's which have on-board ADC's that I can use for this
    purpose or is this not a good idea?
    I think I know how to convert from the digital voltage in to a
    temperature - divide the known voltage range up in to chunks based on
    the bit resolution of the ADC. Say - 0-5v ADC and 10-bit, I would then
    5/((2^10)-1) to get the voltage increment per bit. Then map the
    'voltage' reading back to resistance (known excitation current), and
    use a look-up table to 'linearise' and then interpolate to give a
    reasonable approximation of temperature.
    One thing I'm not sure about is how to calibrate this process.
    Another is that IIRC 0C is 100R and 100C is 138.5R (for Platinum PT100)
    which @ 1mA gives a voltage reading range of 100mV-138.5mV. I'm sure I
    can scale this up so that the 100C resistance maps somewhere near 5
    volts, but the 0C will not be near 0v. so some of the 10-bit signal is
    wasted. Could I not get better accuracy (perhaps it's not needed with
    10-bits) by translating the 0C voltage/resistance somewhere near 0v and
    then scale/amplify so that 100C is near 5v so I'm using a larger
    portion of the bit range?
    Regards,
    Mark
  5. MarkMc
    MarkMc Guest
    I'll have to digest some of this to understand it fully, but one thing
    which I'm not too sure how to do is the two point calibration.
    IIRC the MAX197 app notes suggest calibrating with a highly accurate
    100R and 300R resistors. Say I do this and note the voltage or binary
    value from the ADC, what do I then do with these two values? I see how
    I can apply a correction factor, but this doesn't take both calibration
    points in to consideration.
    Cheers,
    Mark
  6. MarkMc wrote:
    (snip)
    Except for the transposition of LM, yes. It is a precision 2.5 volt
    reference regulator. In combination with the opamp, it forces the
    voltage drop across the grounded 2.5K resistor to be a constant 2.5
    volts, so the RTD current is forced to be a constant 1 mA.
    Most PICs have an internal 10 bit (1024 level) ADC. You just need to
    amplify and shift the signal into the ADC measurement range. You may
    also want to reference the ADC full scale voltage to a precision
    reference, instead of using the 5 volt supply as the full scale value,
    or else the accuracy of the PIC supply gets involved in the measurement.
    You might use a distilled water ice bath and boiling point as a two
    point calibration. Otherwise, you buy a high accuracy liquid
    thermometer and use it in a stirred water or oil bath as a temperature
    reference.
    You can add an arbitrary offset to the resistance measurement by
    connecting R1 in figure 1 to an adjustable voltage, instead of to
    ground. This voltage should be a low impedance source (not just a pot
    hooked up between two voltages) like an opamp follower, in order to
    not upset the subtracter's ability to measure the voltage across the
    RTD. The subtracter circuit is A4 and the resistors around it.
    You can use a pot between the 2.5 volt reference and ground to feed
    the follower.
    When you have zero degrees just above ground and 100 degrees just
    below the ADC positive reference voltage (full scale voltage) you are
    ready to calibrate and linearize the circuit with stored constants in
    the program.
  7. Dan Hollands
    Dan Hollands Guest
    A design to do what you want is a big challange to one of your experience.
    You will probably spend considerable money and a great deal of time and
    still not achieve your goal
    There are a multitude of RTD digital panel meters that do what you want
    available in the UK
    Just buy one - it will work and probably be cheaper than you can do it
    yourself
    Search internet for RTD temperature panel meter UK
    Dan
    Dan Hollands
    1120 S Creek Dr
    Webster NY 14580
    585-872-2606
    themselves.
    4-wire PT100 RTD
    above?
    Regards,
    Mark
  8. The two point calibration I was referring to is just interpolating 0
    to 100 degrees, linearly between the two A/D values you get with an
    ice bath and a boiling bath, using your RTD and amplifier. The
    linearity errors over that small temperature range are not very big.
    If you want to correct them, you need a table or polynomial fit to the
    RTD curve, and fit that to your zero and 100 degree points.
  9. MarkMc
    MarkMc Guest
    Had a look, and they seem to be about £200. Not what I'd call cheap
    for hobby use.
    What would be so expensive to make?
    I have the PIC microcontrollers and programming hardware + software
    etc. The way I see it I just need to find a good OpAmp and ADC?
    Half the fun is the journey with this hobby I think. Yep, right now, I
    don't know too much, but I think I'm getting somewhere - doesn't seem
    too scarey.
    Regards
    Mark
  10. MarkMc
    MarkMc Guest
    Ah, I see. The calibration I had in mind was to pull things in to line
    with the look-up tables.
    Cheers,
    Mark
  11. Guest
    A couple suggestions. Excite the RTD with a current proportional to
    the PIC supply, scaled down to about 1 mA. That would involve
    replacing the precision 2.5 volt reference with a 2 to 1 voltage
    divider from the 5 volt supply. Now, since the excitation will be
    proportional to the supply, if you use the supply as the positive
    reference voltage for the A/D, the signal will also be proportional to
    the A/D reference. This cancels any scaling errors for changes in the
    supply and eliminates the need for a precision component.
    Use the two point calibration method (which eliminates the need for .1%
    or better standard resistors and compensates for tolerances in your
    RTD) and apply this formula to the result.
    temperature in degrees C = (counts-Czero)*100/C100
    where Czero is the A/D result for ice bath, and C100 is A/D result with
    boiling bath. If you do this at sea level, this linear approximation
    for the RTD averages about .235 degree error over the range of 0 to 100
    degrees C. If done at higher elevations, you can change the constant
    100 factor to something lower that represents the local boiling
    temperature. If you have precision resistors available, they can be
    substituted for the RTD during calibration. Store the calibration
    constants in EEPROM.
  12. Guest
    I found an error in my math. The average error in the linear
    approximation over this range with a best fit is .097 degrees. If you
    force the errors to zero at the end points (a sub optimal fit, overall)
    the worst error occurs at about the mid point temperature and is about
    -.4 degrees. If you fudge the endpoints to read .25 degree high, the
    midpoint error is reduced to about -.15 degree.
  13. MarkMc
    MarkMc Guest
    Thanks, these look like really good reading.
    Regards,
    Mark