Hi, my customer asked us to develop a three phase AC deepfryer, the input voltage is 230/380V Main voltage, Power 7000W. My colleague created a drawing in Wye connection as shown.

I try to create the same but in Delta connection, but I am unable to figure out the phase voltage (i.e. the voltage across each heating element). Can anyone help or give me some clues ?

Thanks a lot !
deepfryer - Wye.jpg deepfryer - Delta.jpg
 

Martaine2005

May 12, 2015
4,951
Joined
May 12, 2015
Messages
4,951
This site also has all the calculations.. Here.
It's way over my head but the information is there.

Martin
 

Bluejets

Oct 5, 2014
6,925
Joined
Oct 5, 2014
Messages
6,925
If your elements are the original star connected, you'll blow the guts out of them on delta.
Reason being the original star has 2 elements per phase with any imbalance on the neutral.
Delta has one element across across the two phases.
Why you would need to change to delta is beyond me.o_O
 

jacklam2048

Feb 22, 2021
33
Joined
Feb 22, 2021
Messages
33
If your elements are the original star connected, you'll blow the guts out of them on delta.
Reason being the original star has 2 elements per phase with any imbalance on the neutral.
Delta has one element across across the two phases.
Why you would need to change to delta is beyond me.o_O

Hi Bluejets, Thanks your reply.
I think in Delta connection, the current across each heating element is much smaller comparing to the phase current in Star, thus the heating element connections are not so easy to burn out. Sometimes the burn out of the terminals at the heating elements is a headache and cause a lot of maintenance cost.
 

Harald Kapp

Moderator
Moderator
Nov 17, 2011
13,722
Joined
Nov 17, 2011
Messages
13,722
I think in Delta connection, the current across each heating element is much smaller comparing to the phase current in Star
Only if the impedance of the heating element is increased accordingly.
As the voltage increases by sqrt(3), impedance needs to be tripled to maintain the same power:

Star: Pstar = Vstar² / Rstar

Delta: PDelta= VDelta² / RDelta = (Vstar × sqrt(3))² / RDelta = 3 × Vstar² / Rdelta

With the requirement Pstar = Pdelta you get

PDelta= 3 × Vstar² / Rdelta = Vstar²/ Rstar

Cancelling Vstar out of the equation gives:

3 / Rdelta = 1 / Rstar or equivalently: Rdelta = 3 × Rstar
 

Tha fios agaibh

Aug 11, 2014
2,252
Joined
Aug 11, 2014
Messages
2,252
I think the confusion is between supply and load.

The phase current inside the windings of a Delta connected transformer will draw less current than a Wye.

But, you are showing your deepfryer load wired with a Delta configuration.

If you apply 230v 3p to the Delta load, you are changing the impedance with the extra windings.

Rough math shows your amperage increasing from 10 to 15 amps per leg and wattage increasing from 2.34kw to 3.45kw per element.

I agree with Bluejets that you'd blow it up if hooked up this way.
 

jacklam2048

Feb 22, 2021
33
Joined
Feb 22, 2021
Messages
33
I think the confusion is between supply and load.

The phase current inside the windings of a Delta connected transformer will draw less current than a Wye.

But, you are showing your deepfryer load wired with a Delta configuration.

If you apply 230v 3p to the Delta load, you are changing the impedance with the extra windings.

Rough math shows your amperage increasing from 10 to 15 amps per leg and wattage increasing from 2.34kw to 3.45kw per element.

I agree with Bluejets that you'd blow it up if hooked up this way.
 

jacklam2048

Feb 22, 2021
33
Joined
Feb 22, 2021
Messages
33
Yes, I have calculated:
In Wye connection, the resistance of each heating element is 22.6 Ohm.
If I convert it to Delta connection, the resistance of each heating element has to be 68.48 Ohm.
Thanks all people's reply !
You are helpful !
 

jacklam2048

Feb 22, 2021
33
Joined
Feb 22, 2021
Messages
33
Only if the impedance of the heating element is increased accordingly.
As the voltage increases by sqrt(3), impedance needs to be tripled to maintain the same power:

Star: Pstar = Vstar² / Rstar

Delta: PDelta= VDelta² / RDelta = (Vstar × sqrt(3))² / RDelta = 3 × Vstar² / Rdelta

With the requirement Pstar = Pdelta you get

PDelta= 3 × Vstar² / Rdelta = Vstar²/ Rstar

Cancelling Vstar out of the equation gives:

3 / Rdelta = 1 / Rstar or equivalently: Rdelta = 3 × Rstar
Thanks Harald, Your calculation is a great help !
 