I have a 4-20ma source input and I want to display this on 22 meters . Could I use all the metes in series as they accept 4-20ma inputs or is this configuation all wrong.
Any advise please
 

shrtrnd

Jan 15, 2010
3,876
Joined
Jan 15, 2010
Messages
3,876
It depends completely on your displays. (The manufacturer)
Contact the display (meter) manufacturer, and ask them.
You may very well need an amplifier to drive that many displays, and especially if
there is distance between meters involved.
 

Lindsay

Jan 31, 2013
5
Joined
Jan 31, 2013
Messages
5
My digital displays have input impedance of 10Mohms.
Can anyone advise best way to have either voltage or current inputs of 22 dispalys.
They are all 1 metre apart. The input is either 0-10 V dc or 4-20ma
 

shrtrnd

Jan 15, 2010
3,876
Joined
Jan 15, 2010
Messages
3,876
We just don't have enough information.
What's your application, what's the model number of your displays?
Typically in industrial applications, inputs are 4-20mA, 1-5VDC, here in the States anyway.
There are plenty of people on this site that will help you if you can give a little.
 

Lindsay

Jan 31, 2013
5
Joined
Jan 31, 2013
Messages
5
I am trying to display a depth reading on multiple displays. I have a pressure transducer with an output of 4-20ma or 0-10V DC,. I have 22 digital programmable panel meters that operate from 12 or 24 V dc. They can have an input of either 4-20ma or 1-10V dc.
I will calibrate each meter to show equivalent depth of 0 to 25 mts. The panel meter has input impedance of 10 Mohms. The meter type is a MB3800
 

duke37

Jan 9, 2011
5,364
Joined
Jan 9, 2011
Messages
5,364
I am not an expert on these, however this will not stop me!

If you use more than one meter on the current source, the meters will need to be connected in series. they may not like not being able to find their own ground. The input impedance will be determind by a resistor to generate a voltage, this will be much lower than 10M. Where does the current come from? If from the meter, then you will have 22 times the voltage required.
The advantage of the current source is that wiring resistance is of little importance.

The obvious way out of this is to go for the voltage source when any number of displays can be connected in parallel.
 

(*steve*)

¡sǝpodᴉʇuɐ ǝɥʇ ɹɐǝɥd
Moderator
Jan 21, 2010
25,510
Joined
Jan 21, 2010
Messages
25,510
I am not an expert on these, however this will not stop me!

A current loop works by encoding the signal on the current in the wire rather than the voltage across a pair of wires.

The idea is that the current remains constant in the wire regardless of the resistance and voltage drop in the wire.

All devices are connected in series (so they see the same current.

Not having a common earth for the signal is a feature and one that current loop devices will be able to handle.

The limitation is the maximum voltage the signal source is able to use. This determines the total resistance (and/or voltage drop) in the loop.
 

gorgon

Jun 6, 2011
603
Joined
Jun 6, 2011
Messages
603
I have a 4-20ma source input and I want to display this on 22 meters . Could I use all the metes in series as they accept 4-20ma inputs or is this configuation all wrong.
Any advise please

The main problem you will have is the output voltage of the 4-20mA source. To use 4-20mA on 22 meters you need to place all in series. Each display will drop a number of volts over the internal sensor resistance, and will 'eat' up the available overhead voltage available from the output. The sensor resistance is normally in the range of 100-200 ohm, and 20mA over 200 ohm will drop 4V off the overhead. For 22 displays this could be as much as 88V drop plus the normal 10V needed in the bottom. I've never heard of a 4-20mA output with 100v overhead, so I think I can safely say that this is not the way to go.

To solve your problem, you could put in a current to voltage converter, or 4-20mA to 2-10V driver amplifier to source all meters in parallel, with 2-10V inputs. You may find that the displays is not isolated and may interfere with each other. Some meters has an isolated input and this is no problem then.
 

KrisBlueNZ

Sadly passed away in 2015
Nov 28, 2011
8,393
Joined
Nov 28, 2011
Messages
8,393
Gorgon's first paragraph hits the nail on the head regarding using a current loop and connecting the meters in series.

If the meters have a 10 megohm input resistance in voltage mode, connecting 22 of them in parallel will give a combined input resistance of 450 kilohms, which is still pretty high. That's the way to go, in my opinion. Set everything to voltage mode and connect the meter inputs in parallel.
 

gorgon

Jun 6, 2011
603
Joined
Jun 6, 2011
Messages
603
You could wire all the displays in series if you kept the maximum voltage low enough. A ten ohm resistor would produce 40 to 200 mV and 22 in series would add up to 4.4V something the transmitter could be expected to handle.

You could if you made the displays yourself, and used very good quality sensor resistors, but the OP never say he wants to make the displays himself, and most standard shelf displays use a much higher sensor resistance, as mentioned before.

That said, most 4-20mA drivers use 24V as drive voltage. This will result in a headroom of 14V above the normal 10V offset. In cases where the output driver is supplied from a separate voltage supply, you may even have all, or most of the 24V range as headroom.

I've had a look at several displays and found that 50-100ohm is a normal input sensor values, and the lowest I found was 33ohm, but most outputs limit the total resistance to 500 - 700 ohm. and this parameter is the limiting factor.
 
Last edited:

duke37

Jan 9, 2011
5,364
Joined
Jan 9, 2011
Messages
5,364
Looking at Wikipedia I found this.

"Several passive indicator devices may be connected in series, but a loop must have only one transmitter device and only one power source (active device)."
 

gorgon

Jun 6, 2011
603
Joined
Jun 6, 2011
Messages
603
It's no problem to connect devices in serial, it's the number (22) that's the problem.
 

KrisBlueNZ

Sadly passed away in 2015
Nov 28, 2011
8,393
Joined
Nov 28, 2011
Messages
8,393
Wiring a lot of current inputs in series and using a high voltage source will cause a problem if the meter inputs are simple current shunts.

Assume each meter has an input current shunt of 250 ohms, a typical value. At 20 mA the total series voltage drop will be 110V, so a 120V power source leaves 10V across the transmitter, which sounds good.

But at 4 mA loop current, the total voltage across the meters will only be 22V and the transmitter will have 98V across it, which is likely to damage it.
 

Lindsay

Jan 31, 2013
5
Joined
Jan 31, 2013
Messages
5
Hi everybody and thanks for comments. I have not bought any meters yet, but was checking if it was feasible to do this.
There has to be a better way to have so many meters or dispalying showing this information ?
 

KrisBlueNZ

Sadly passed away in 2015
Nov 28, 2011
8,393
Joined
Nov 28, 2011
Messages
8,393
It's probably a reasonable way to go.

The alternative would be to convert the current into a digital representation and transmit that to the indicators, but I've never heard of an off-the-shelf panel meter that accepts data in digital form. You would have to design one, as well as the method of transferring the data to them all.

Panel meters with simple voltage input are produced in bulk, so they are cheap to buy. They're also easy to connect. Factoring in these practical advantages, I can't think of any better way to do what you want.
 

Lindsay

Jan 31, 2013
5
Joined
Jan 31, 2013
Messages
5
Yes , I also think thats probably the best way to go. I know the meters I have in mind do accept a 0-10V input so i could have all the meters in //el.
 