Hi everyone.

First, I have to say I am not very good at this!!

I use a din rail switch to control a water pump. this was very easy to
install 2 cable go directly to the pump the third is connected in both
sides of the switch and this controls if the pump is on or off. The
switch only has one entrance in each side.

Now, I bought a din rail timer to automatically control the pump. This
timer has 2 entrances in each side. One side has the symbol 1
------------~-------------2 and the other 3------------/-----------4.

Manual says "Ensure that the 230Vac supply is connected to terminals 1
and 2. Load should be connected across terminals 3 and 4."

Anyone can help me?

Thanks in advance
Paulo
 
N

Nobody

Jan 1, 1970
0
First, I have to say I am not very good at this!!

I use a din rail switch to control a water pump. this was very easy to
install 2 cable go directly to the pump the third is connected in both
sides of the switch and this controls if the pump is on or off. The
switch only has one entrance in each side.

Like this?

L o-----[ Switch ]-----+
|
[ Pump ]
| |
N o--------------------+ |
|
E o-----------------------+
Now, I bought a din rail timer to automatically control the pump. This
timer has 2 entrances in each side. One side has the symbol 1
------------~-------------2 and the other 3------------/-----------4.

Manual says "Ensure that the 230Vac supply is connected to terminals 1
and 2. Load should be connected across terminals 3 and 4."

Anyone can help me?

Probably:

L o--[1 3]---[ Switch ]-----+
[ ] |
[ Timer ] [ Pump ]
[ ] | |
N o--[2 4]------------------+ |
|
E o--------------------------------+

Either way, ensure that you have live (L), neutral (N) and earth (E) the
right way round. If you don't know which is which, get someone who does
know to wire this up for you.
 
P

PA

Jan 1, 1970
0
Thanks for you quick reply!!!

I just found the manual here http://www.greenbrook.co.uk/pdf/T80-C.pdf

This version of the manual says
"Ensure that the 230Vac supply is connected to terminals 1
and 2. Terminals 3 and 4 are volt free. Live in goes to terminal 3 and
live out to terminal 4 goes to load. There is no neutral switching
with the T 80"

with this timer I should not need the switch.

can you please confirm your diagram with this info?

Thanks again.

PA
 
N

Nobody

Jan 1, 1970
0
Thanks for you quick reply!!!

I just found the manual here http://www.greenbrook.co.uk/pdf/T80-C.pdf

This version of the manual says
"Ensure that the 230Vac supply is connected to terminals 1
and 2. Terminals 3 and 4 are volt free. Live in goes to terminal 3 and
live out to terminal 4 goes to load. There is no neutral switching
with the T 80"

with this timer I should not need the switch.

can you please confirm your diagram with this info?

In that case:

+-------------------+
| |
L o-------+----[1 3]----+
[ Timer ]
N o-------+----[2 4]--------+
| |
| [ Pump ]
| | |
+-----------------------+ |
|
E o----------------------------------+

I.e.:

Live -> Timer 1 and Timer 3
Timer 4 -> Pump (Live)
Neutral -> Timer 2 and Pump (Neutral)
Earth -> Pump (Earth)
 