F
Floyd L. Davidson
Bill Bowden said:If the limit were 25 feet, you would have a problem connecting your
phone to the telco which may be several miles away.
They usually use 48 volts to supply 20mA of current in series with your
phone. The phone is about 600 ohms and drops 12 volts at 20mA which
leaves 36 volts that can be lost in the line. If you use 22 gauge
copper wire, the resistance is about .016 ohms per foot, and 36 volts
at 20mA is about 1800 ohms, so the maximum length would be 1800/.016 =
112500 feet or 21 miles. A larger gauge will increase the distance.
600 Ohms is the nominal *impedance* of a telephone set. The DC
resistance is necessarily less than 350 Ohms. Common values are
roughly about 200 Ohms.
Loop current is supplied through a resistance though, which is
typically 400 Ohms. (For extended length loops the voltage may
be higher than 48 VDC and/or the resistance may be less than 400
Ohms.)
And it is also true that the line has to work when the
battery voltage is low! So while it is a "48 Volt Battery",
the typical voltage is 52 VDC and the range that may be seen
is 42 to 56 VDC. So maximum loop length would need to be
calculated using 42 VDC, not 48 VDC.
Also the common wire sizes are 26 gauge and (on rare occasions)
24 gauge.
While 20 mA is the current at which the line is considered
"offhook", the actual steady state loop current must be 23 mA or
higher. Typically it is 27 mA or higher (and is current
limited).
Hence you have the right idea for determining maximum loop
length, it is actually slightly more complex and requires
different numbers.