Hello, need a little help with this?

Discussion in 'Power Electronics' started by Darius_silve, Feb 21, 2021.

Scroll to continue with content
  1. Darius_silve

    Darius_silve

    2
    0
    Feb 21, 2021
    So, I have a very powerful server with 2 power supplies labeled as (each)


    • FREQUENCY:50/60Hz
    • INPUT:176V-264V~ 15A MAX (what does this mean)
    • OUTPUT:1800W(MAX) +12.0V—150A

    I’ll be getting an electrician to install a 220v plug in for my home which is located in Canada Calgary with the normal being 120v at 15 amps

    My question is that if I switch up to the 220v being installed in my house would it be enough for the 2 (1800 walts) labeled above? I also think I’ll be installing a 20 amp or 30 so it’s able to handle it?
     
  2. Darius_silve

    Darius_silve

    2
    0
    Feb 21, 2021
    This sever will be running 24/7 365
     
  3. davenn

    davenn Moderator

    13,883
    1,966
    Sep 5, 2009

    It means it can handle any mains input voltage between those two values and still produce a stable output

    You need to show the electrician those spec's BEFORE he starts work so that he can do the appropriate cabling
    and 220V outlet requirements for the required current ( up to 15A) ... that isnt a standard 10A 220V cable and socket requirement
     
  4. Bluejets

    Bluejets

    5,043
    1,053
    Oct 5, 2014
    1800w on a standard 10A outlet @220v It's only 8A afterall.should be no problem or cause for anything out of the ordinary with regard to cabling.

    It's only 8A after all.
    Your toaster, jug and clothes dryer pulls way more than that.

    Not only that but that rating is the maximum it can deliver.
    More important info would be the draw of the server.
     
  5. Nanren888

    Nanren888

    507
    150
    Nov 8, 2015
    Sorry, for the aside, but confused.
    Isn't he on 120v & has 240volt appliances
    " switch up to the 220v being installed in my house" - Is it standrard in Canada to be able to specify either?
     
    davenn likes this.
  6. Audioguru

    Audioguru

    3,395
    733
    Sep 24, 2016
    In Canada each house has 240VAC center-tapped. Then there are two bands of 120V live and neutral or both lives producing 240VAC for high power like electric stoves, clothes dryers and air conditioners.

    Since he will have two times 1800W running all the time, the electricity bill will be VERY high.
     