Getting 240 volts from 208 volts
Discussion in 'Electrical Engineering' started by [email protected], Nov 29, 2006.
  1. Guest
    The need to get 240 volts instead of using 208 volts for 240 volt
    loads is not what I will be discussing here. If you want to discuss
    that, please start a new thread. What I want to ask about here is
    the viability of using buck/boost transformers to get that 240 volts,
    either for delta connected three phase loads, or for single phase
    loads.
    What my calculations came up with is a wiring arrangement using the
    common 240/120 to 24/12 single phase buck boost transformer to get
    nearly the correct voltage. Actually, it would involve 3 of them.
    To understand what I am going to describe, you should already know
    how a buck/boost transformer is used in an autotransformer setup to
    make voltage adjustments.
    Given a 208Y/120 power source, the ideal buck-boost transformer would
    have 120 volts input and 18.56406460551 volts out. With the output
    wired to boost the supply voltage, you get 138.56406460551 volts L-N
    and thus 240 volts L-L. Such transformers are not actually made that
    I can find.
    My suggestion is to use a 240/120 to 24/12 transformer wired for 240
    volts input and 24 volts output. The primary would be connected L-L
    to the source, thus powered by 208 (207.846096908265) volts. The
    output would then be 20.8 (20.7846096908265) volts. This output
    would then be wired in series with a particular L-N connections so
    that it's phase angle is 30 degrees. Assuming a supply labeled as:
    A
    N---C
    B
    One B/B transformer fed from an A-B connection would have its output
    at the polarity that corresponds to the A input connected to line B.
    Showing this accurately is beyond ASCII graphics so I'll skip that
    to avoid introducing new confusion. If this is wired as intended the
    result is 120 volts at 0 degrees plus 20.7846096908265 volts at 30
    degrees. This results in 138.390751136 volts at 4.306619096 degrees.
    Do the same on all 3 phases with 3 such transformers. The resultant
    L-L voltage is then 239.7 (239.699812265) volts, very close to the
    desired 240 volts. Normal voltage variations are greater than this.
    Assuming a perfectly resistive load on the 239.7Y/138.39 side of this,
    the supply would see a current angle displaced 4.3 degrees for a power
    factor of about 0.997.
    I have seen many buck/boost wiring diagrams. But of all those seen,
    none has ever done any cross-phase connection, not even of this small
    amount. So I have these questions:
    1. Is this an unknown method?
    2. Is this prohibited by code?
    3. Is there anything unsafe about this?
    4. Would a power factor of 0.997 be a problem where loads often have
    their own power factors much worse than this?
    There is another method that is a little more complex which involves
    phase B being boosted by have as much as above from a reduced A-B as
    well as from a reduced C-B. The same transformers can be used, but
    would have to be wired with 12 volt secondaries not connected together
    at all (or double the number of transformers at half the capacity).
    This would result in a final L-N voltage of 138.000, and a L-L voltage
    of 239.023, which is still very close to the target. But it would have
    a 0 degree voltage phase shift. If the phase shift is more of an issue
    then this approach is an alternative.
    Or the inherint phase shift of the first setup could be used opposite
    to the shift of a reactive load and presumably reduce its effect.
    My real interest is not so much in supplying three phase loads at 240
    volts, but rather, supplying single phase loads at 240 volts. Three
    phase loads are more likely to be designed with the expectation of
    the supply voltage being 208Y/120. But single phase loads may not.
    Given a three phase source, getting nearly 240 volts is not hard. But
    a common problem is that residences in large buildings are often given
    2 legs of a three phase system as "fake" single phase (where the legs
    are really 2 phases at 120 degrees). Getting 240 volts out of this is
    my real goal. One could get three phase back from this like:
    A A *
    N ... N C
    B B
    although that would have some substantially reactive current angles
    on both of the supplied phases for any load on the output C-N. The
    first or second examples I gave above might be applied on top of this
    three phase hack, but only to get one phase of 240 volts at about the
    A-B phase angle. Still, this is a lot of transformers and wiring at
    this point.
    By skipping the three phase step, 1 or 2 B/B transformers could be
    used on a 2 phase 120/208 volt system two different ways. Probably
    the simplest is one transformer with 240 volts in and a pair of
    16 volts secondaries out. Wire the input to the 208 volt A-B and
    use each of the secondaries to separately boost out A and B. This
    will get only 235.5589 volts total. One side effect of this is that
    the phase angle of A and B with respect to the neutral will increase
    somewhat from 120 degrees to 126 (126.008983198) degrees.
    Note that the above would have 132 (132.181693135) volts L-N and would
    not be suitable for any L-N loads expecting 120 volts, and hence cannot
    be used for any 3-wire 120/240 volt loads. Such loads would probably
    have to use a 120 in 120/240 out autotransformer (half capacity) or a
    208 in 120/240 out isolation transformer (full capacity) to get all the
    right voltages. And these more expensive transformers due to the higher
    capacities involved.
  2. Guest
    |>loads.
    | 208->230 or 208->240 is one of the most common uses of such
    | transformers.
    I've never seen a buck boost wiring diagram (and there are a LOT of
    them in many manufacturer catalogs and spec sheets) that shows how
    to do this for 208->240.
    |>I can find.
    | Well, I think you should have googled before you did all that
    | calculation.
    Why do you think I didn't? You found calculations for all this
    somewhere that I couldn't?
    | A 120/240 - 12/24 would be used to go from 208 -> 230.
    Not what I'm interested in.
    | For 240, then 120/240 - 16/32 will be what you want, or close enough
    | to it for most all purposes.
    | If you really need 11 decimal places of accuracy, then simple
    | transformers aren't going to do it for you under any circumstances.
    The accuracy is just point figuring for math purposes. I do expect to
    get to 240 volts within a couple volts. If they made a buck/boost
    transformer with 18/36 output, that would hit it without having to use
    the crossed phase angles. But 16/32 doesn't accomplish it. There are
    no 18/36 volt out transformers from Google searches, nor any diagrams
    showing how to get the correct voltage from 12/24 or 24/48 volt ones.
    With 208, a pair of 16 volt boosts could get within 5 volts. Since they
    don't make these as 18/36 volt transformers, I presume such a voltage
    has other uses and getting 240 from 208 is not really considered in the
    design.
  3. Guest
    The biggest variable will be what the PoCo sends you.
    I consistantly see 247-248 on my single phase service but I have seen
    it as low as 225 in my travels around town.
  4. Guest
    On Wed, 29 Nov 2006 20:42:17 -0500 wrote:
    | On 29 Nov 2006 23:19:58 GMT, wrote:
    |>I do expect to
    How many of those 225's are really 208's a bit hot?
  5. Don Kelly
    Don Kelly Guest
    Get rid of all the extra decimal places that your calculator is giving you-
    they are actually meaningless as 120V (implied +/- 0.5V is not the same as
    120.0000000V (implied +/-0.0000005 V)
    If your calculator cannot be set to give a specific number of significant
    figures, then I can sell you a simple fix consisting of a piece of masking
    tape.
    Noting that your 120V is likely to be in the range 114-126V normally- then
    what is the point?
    However, if the secondary windings of your buck boost transformer are
    completely isolated from ground or the primary (and each other) then you can
    do this. It's not a big deal.
    As for phase shift- then consider phase shift with respect to what? Your
    load sees a 3 phase voltage and acts accordingly. The primary voltage may be
    shifted in phase but so is the primary current so that with a 1.0 pf load,
    the primary sees a 1.0 pf load (ignoring reactive losses of the transformer-
    where do you get a reactive input with no reactive output?). --
    Don Kelly
    remove the X to answer
  6. Guest
    I use the extra digits for a purpose. First, it ensures that accumulated
    errors do not happen. Secondly, it helps determine if numbers are "matches"
    that suggest simplified formulas. I've seen cases where NOT having them
    can lead to suggested matches that really aren't just because certain paths
    of arithmetic come close but don't hit the mark. For example I ran into
    these numbers:
    138.390751136
    138.564064606
    They look close. But they have different meaning. They just happen to be
    close. But there is no mathematical equivalency to how they were calculated.
    But if some calculation had come up with:
    138.564064605
    then the chance that it would be equivalent to the 2nd of the first 2 is
    very high. The use of irrational numbers and a variety of different formulas
    can result in "number crossings" that may or may not have significance.
    | tape.
    I wouldn't use it.
    When I see a reference to "208v" I figure it is probably the voltage involved
    line to line when the line to neutral voltage is "120v". The confidence is
    high, but it is not a certainty. But if I see "207.846v" then the confidence
    is way up. Even more so with "207.84609690826527522329356v".
    Yes I understand that voltage can vary. And I understand my arithmetic is
    more accurate than the voltage.
    | what is the point?
    The point is correct numeric identification. If the line to neutral voltage
    can vary from 114 volts to 126 volts, then the line to line voltage can vary
    from 197.45379206285201146 volts to 218.23840175367853898 volts :)
    If I see "197v" somewhere, I don't know if it comes from just dropping "200v"
    down by 3 volts or what. But if I see "197.45379v" then I have a very high
    confidence that it was derived from 114 times ths square root of three.
    I know how it's done.
    You're saying that a transformer can store energy and have current flowing
    in a secondary winding when the primary is at a zero crossing?
  7. Bud--
    Bud-- Guest
    Use a 16/32V buck/boost. Connect the 32V boost from B to B'. Connect the
    primary from A to B' - 208+32=240 applied to primary. The primary is
    supplied from the boost side so the secondary supplies the primary
    current in addition to the load.
    The 16V secondaries could be wired to boost A to A' and B to B' but I
    don't see any advantage.
    A 24V boost from 208V to 232V is probably close enough.
    Autotransformer conversion between 208 and 240 is specifically permitted
    by the US-NEC 210.9-ex1 and 215.11-ex1
  8. Ben Miller
    Ben Miller Guest
    I was going to point him to exhibit 210.19 in the 2005 handbook, which shows
    autotransformer connections both buck and boost between 208 & 240.
    Ben Miller
  9. 3 phase phase shifting transformers shift the phase of the voltatge and
    current equally.
    In your second proposed connection, the voltage was boosted out of phase.
    The current in the primary consists of a current phasor in the shunt winding
    added to the current phasor going through the series winding and the load.
    If you apply a 1 PF load, the primary current will be zero when the primary
    voltage is zero, negleticing transformer magnitizing current. The load
    voltage won't be zero and the load current won't be zero at the same point
    in time, but the current in the load and series winding will be canceled by
    the current in the shunt winding (remember it's boosting another phase).
  10. Guest
    |> |>loads.
    |> | transformers.
    Sounds good. I haven't seen this one, but I should have thought of it.
    My calculation tells me that if you start from 120 volts L-N dead on (for
    reference purposes) and boost the 120 volt leg that is at 120 degrees
    (also dead on phase angle) the boosted phase ends up at 148.555171749
    volts at 113.821609305 degrees. The other phase(s) remain the same.
    The L-L` ends up at 239.822419510 volts. That's close enough. But it
    can only be used on appliances that are listed as accepting L-N voltage
    at least at 148.555171749 nominal (more likely having to be around 160).
    This ends up more balanced, though not perfectly so (because the angle
    is not 180 degrees). Now you have L`-N at 134.084668120 for both phases
    with angles of 116.582018908 and 243.417981092 (based on original phase
    angles of 120 and 240). And you get the same exact 239.822419510 volts
    as above, but at a slightly lower L`-N voltage.
    I would rather wire it this way over the above way.
    Note the precision calculations are based on 120.000000000 exact L-N
    voltage.
    It would be at least semi-balanced that way. Not well enough for powering
    audio equipment, but probably OK for other things that don't need neutral.
    The audio equipment could then be powered from a 1:1 isolation transformer
    that would line up the phases at 180 degrees, or drop back down to running
    the audio equipment at 120 volts with a 60-0-60 split.
    Except during brownouts. Consider the range of voltage you might get
    and the range of voltage the appliance can work with. They should fit
    if they are aligned right on center. But if you shift the supplied
    voltage range down, the supply range may fall outside the utilization
    range.
    In any configuration? What about three phase conversions? All diagrams
    I have ever seen involve extending a L-N at the same exact angle it starts
    at. And what if the source supply is closed delta (that probably violates
    that rule I didn't look up, yet, because the only way to do that on a
    corner grounded delta would end up with a tap-grounded delta with an odd
    tap position for the grounding).
  11. Guest
    | writes:
    | The errors are already there. 120V +/- 0.5V means the voltage could be
    | 120.0, 120.2, 119.5, 119.7, or an infinite number of other values between
    | 119.5 and 120.5 volts. See below.
    Of course. The reality is the supply is a statistical range. But it does
    have a center. A given service drop may have a long term center that is
    offset from 120 maybe even by quite a few volts. But the _basis_ voltage
    is still 120 volts. I could run all my calculations on various voltages
    in the range, and the extremes of the range, and get range results with
    precision.
    | They teach the opposite in introduction to engineering courses. They
    | teach the concept of "sig figs", significant figures. Simply put, you
    | never use more digits after the decimal point than the accuracy you know,
    | and when performing mathematical operations, you use the accuracy of the
    | least known source and you must avoid adding more decimal places just
    | because the calculator shows more digits. The extra decimal places in
    | something like "207.84609690826527522329356 V" gives a false sense of
    | accuracy.
    Only to people that misunderstand the difference between precision and
    accuracy. But then, I've found a lot of people that misunderstand that.
    But such statistics won't change my way of doing things. If someone
    misunderstands that I'm giving precision rather than accuracy, then I
    say that is their problem, not mine.
    Of course people don't care if it's 208.000000000 volts or 207.846096908
    volts if they get shocked by it. Even a damned good meter isn't going
    to give you all that many digits (a damned good one might do 207.846 and
    a half-way decent one could do 207.8).
    | As an example, how should an engineer write the line-line voltage of a 3
    | phase system is the line-neutral voltage is given as 120. volts? The
    | decimal states the "120" is known to 3 significant figures (voltage is
    | within +/- 0.5 volts of 120 volts), and the square root of 3 is
    | essentially known to a near infinite number of digits, the smaller of the
    | two is 3 digits, so the correct answer is 208. volts. Same question, but
    | if the voltage is given as 120.0 volts, the correct answer is 207.8 volts.
    | If the line-neutral voltage is known only within +/- 5 volts, it should be
    | written as "120" (no decimal point), as it's known to only 2 figures, and
    | the line-line voltage should *not* be written as 208 volts (3 figures),
    | but 210 volts (2 figures, rounded). Since the nominal "120 volts" is not
    | supplied by the power company within 3 significant figures, all the "208
    | volts" figures used everywhere is, from an engineering viewpoint, wrong!
    First of all, saying "120" does NOT say that it is 3 significant figures.
    It could be a reference label to the connection that is defined nominally
    as 120 volts can could be found to be anywhere from 114 to 126 volts in
    places where the voltage is within 5%, or even further at 108 to 132 volts
    when 10% is the margin. And you can find different ranges based on long
    pr short term statistics.
    Nevertheless, I run my calculations at precision (not accuracy) based on
    the "definition voltage". This lets me double check things, and assures
    that where multiple steps should end up back at a whole number they very
    likly will, or will be so damned close it's obvious to anyone. If you
    do some calculations and the end result is 119.999999997 you can just
    tell it was "meant to be" 120. But if the result is 119, that's not so
    obvious.
    My vector calculator uses long double precision, and rounds the results
    to 9 fractional digits. I could recode it for more if I ever need to.
    I also know the programming techniques to maximally preserve precision
    in floating point calculations on a computer.
    | This becomes ambiguous when the number of sig figs is less than the number
    | of digits left of the decimal point (what does 69,000 volts mean?),
    | but that's one of the reasons for scientific notation as well as metric
    | prefixes. 69 kV has 2 figures accuracy, 69.0 kV 3 figures, 69.00 kV four
    | figures etc.
    I really don't know their basis voltage. If that is the L-N voltage on
    a system with a L-L basis voltage of 120 kV, then the L-N _basis_ voltage
    would be 69282.032302755 ... rounded to 9 fractional digits :) That
    would be the center point in a range.
    | And when designing something, you must be sure the added digits don't come
    | back and bite you.
    Don't worry. I know how to handle high precision arithmetic.
    | When designing something, you should never have to guess the origin of a
    | calculation as well as not being misled by the accuracy. A figure
    | like "197.45379 +/- 0.5 volts" is absurd.
    | And this concludes today's Engineering 101 class :)
    When I was in school in the 1970's, courses in sciences and engineering
    never explained anything about precision vs. accuracy. I found a lot of
    people, including professors, didn't understand the distinction. More
    recently I was reading a (rather heavy) college freshman chemistry book
    (a chemistry prof my dad knew gave to him) and it actually did address
    the precision vs. accuracy issue.
    So would you change "197.45379 +/- 0.5" to be "197 +/- 0.5" or would you
    change it to be "197.5 +/- 0.5"? Is 196.9530 within the range? What about
    197.9536?
    What you are doing when you change it to either 197 or 197.5 is called
    quantization. It really is possible to have more precision than accuracy.
    You could have a 6 digits voltmeter that reads 207.846 volts. Then you
    can watch it waver up and down between 206.846 and 208.846. The accuracy
    of the supply is +/- 1 volt while the precision of the meter _may_ be
    +/- less than 0.001 volt. If the meter is calibrated to 0.0005 volts
    accuracy, then its precision is easy to deal with. However, if it is
    out of calibration, it can still give you precision. If you have a
    reference voltage you can check the error. But even if it is out of
    calibration by an unknown voltage, you might still read a figure around
    120 volts on a circuit that should have around 120 volts and know that
    it is at least not too far off. Then with the precision and lack of
    accuracy, you can still measure the _other_ phase and see _about_ how
    many volts different they are. You cannot do that if you misunderstand
    precision and assume it is always bound to accuracy (sometimes it is,
    but not in this case).
    BTW, the square root of three is approximately:
    1.7320508075688772935274463415058723669428052538103806280558069794519330169088
    but most electrical engineers will use 1.732 or even 1.73 because it is quite
    adequate where precision isn't needed.
    1.73 squared is 2.9929
    1.732 squared is 2.999824
    1.732050807568877 squared is 2.999999999999998983191099041129
    The later is how far I have memorized the square root of three. But I can
    calculate it with a program I wrote to many million digits if you'd want it.
    When I want to know things like "does this calculation involving the square
    root of 3 produce a result that is supposed to be at a whole number", then
    I intentionally use more precision to be sure of it.
    And I can also give you some whole number fractions that get very close to
    the square root of 3. Here are some examples:
    2011930833870518011412817828051050497 / 1161588808526051807570761628582646656
    3484766425578155422712284885747939968 / 2011930833870518011412817828051050497
    5496697259448673434125102713798990465 / 3173519642396569818983579456633697153
    You can verify these by squaring the numerator, squaring the denominator,
    and multiplying the denominator squared by 3 and getting the numerator
    squared within a digit or two.
    Of course someone will just say why not use:
    1732050807568877293527446341505872367 / 1000000000000000000000000000000000000
    Try it and you will see that the three I gave above have double the precision
    as this one (about equal to the total number of digits expressed). I can also
    do this for PI:
    8904500941523253328862487239770856471 / 2834390681219723641210580762604275775
    which is double the precision of:
    3141592653589793238462643383279502884 / 1000000000000000000000000000000000000
    I guess you can call me the master of trivial precision.
  12. Guest
    |> may be
    |> load,
    |> transformer-
    | current equally.
    So if you have a non-reactive pf 1 load on L-N and another on L-L the
    current on the primary side will be exactly the same?
  13. Don Kelly
    Don Kelly Guest
    the two (exact) integers 2 and 2 are identical but this doesn't mean that
    the calculations involved to reach them are the same. The above argument
    doesn't apply. If you want to eliminate round off errors in calculations
    then store the numbers between calculations -surely you are not entering
    numbers with so many digits- My calculator can display the number of sig
    figs that I want but the arithmetic done is to whatever floating point
    precision that is involve. That doesn't mean that the results are more
    accurate.
    Your confidence is misplaced in that it has no relationship to reality.
    when you say 120V, you are saying that it is a voltage between 119.5V and
    120.5 V That is 3 significant figures. It is not the same as 120.0000 V.
    Similarly, even though your calculator multiplies this by root(3) and gives
    207.8460969...., the result is accurate only to 3 significant figures or
    208V +/_ 0.5V. The rest is a tribute only to the capability of your
    calculator. This is something that engineering schools try to drum into
    their students. Solutions to problems that show answers like 207.8460 ....
    lose marks if the original data doesn't justify this accuracy.
    In addition, how often does a nominal 120V actually appear at the outlet?
    You are working with nominal values
    In rare cases, such as ill conditioned matrices, there is a need for double
    So what is the confidence in the 114?
    No. Suppose that you have your Zig-zag secondary with a resistive load so
    that both voltage and current are shifted 30 degrees (in the same direction)
    from the reference (say phase a primary -consider a star primary for
    simplicity). Now, if the secondary current is reflected into the primary as
    you indicate then there would be a problem - you have secondary windings
    from each pair of phases tied in series. That correctly implies a common
    current in these two windings. However there is another phase a winding in
    series with a c phase winding and the current in this is actually lagging
    by 30 degrees (accounting for winding polarity) Now, on the basis of
    secondary currents reflecting back to the primary, this implies that the
    primary current of phase a is both leading and lagging. It also implies
    that all 3 phase currents are in phase - double contradiction.
    An easier argument is that the transformer doesn't produce or absorb
    (ideally) any power or reactive (conservation of energy)so that for a given
    secondary P and Q out, there must be the same P and Q input. If the loads
    are balanced then that would also mean that the pf of the input is the same
    as the output.
    The answer to this quandary is that one must look at ampere turns, not
    amperes.
    Check it out in the simpler case of a single phase transformer 1200/240 V
    with a center tapped secondary. If you have a load of 5A, unity pf at 120V
    on one side and a load of 10A at 0.8 pf lag on the other leg. what is the
    primary current? It cannot be 0.5A ,1.0 pf and 1.0A at 0.8 pf.
    Considering each secondary separately you would have a=Np/Ns =10
    Np*Ip =Ns* (Is1 +Is2)= Ns* (14.3 @ -24.8 degrees) or 1.43 A at 0.91 pf lag
    Check from power
    Ps1 =120*5 =600 watts Ps2 =120*8 =960 watts Qs1 =0 Qs2=120*6 =720 Vars
    total 1560 watts, 720VAR or 1720VA at 0.91 pf lag and a current of 1.43A
    For the 3 phase scheme this is also true. The primary amp turns must
    balance the amp-turns of the two secondary windings in each phase. The
    currents in these windings are 60 degrees apart and the number of turns is
    the same in each.
    Then considering that one of the phase a secondaries has a current leading
    by 30 degrees, the other phase a secondary has a current effectively lagging
    by 30 degrees so the sum of the ampere turns seen by the primary is NI1
    +NI2 =N(root(3)I at angle 0 so for a balanced secondary load at unity pf,
    the primary current which must balance the total secondary ampere turns- not
    the amperes in the secondary windings) is at unity pf.
  14. Don Kelly
    Don Kelly Guest
    But doesn't the fact that the "precision" is an artifact of the calculator
    and is actually meaningless mean anything?
    To rely on such "precision" which occurs because the calculator is a stupid
    beast and does all its work to whatever level of precision it is designed to
    use and will treat an entry of 120 as 120.000000....
    The extra zeros exist because it is can't do otherwise as it doesn't have
    intelligence to do so. The user should have this intelligence. There is no
    problem with this as it does reduce computational round off to an
    insignificant level but when returning to the real world, the user should
    have the intelligence to correlate the numerical values to the real world.
    This reliance is a product of misunderstanding, not a cure for it.
    By the way, Michael is quite right - I was giving 120, with no decimal
    point, a sig fig level of 3 by interpreting it as 120.
  15. Guest
    |>precision.
    | Such precision isn't necessary in that case, unless you're pulling a stunt
    | like wiring two big substation transformers to have a zero voltage
    | difference between two terminals, and using your two hands to "measure"
    | the difference. In that case the accuracy doesn't matter (you don't care
    | if the transformers are putting out 69 kv or 68 kv) but you do want the
    | difference to be very precisely 0.
    You're using "precision" and "accuracy" interchangeably here.
    |>accuracy.
    | I know the difference perfectly well.
    | Right. To an engineer it's ambiguous, but it implies accuracy to two
    | figures. "120.", to an engineer, states 3 figures accuracy.
    | There are different usages to an engineer and, say an electrician or a
    | lineman working on something. Even today, electricians often speak of
    | "two twenty" although the nominal voltage has been 240V (or at least
    | larger than 220V for decades)
    Indeed. "two twenty" is a label, not a measure. So is "220V" and "240V"
    and even "207.84609690826527522329356". As labels they imply certain
    meanings which have nothing to do with precisions or even measures. The
    label "207.84609690826527522329356" means "120 times the square root of 3
    with an extremely high degree of confidence" as opposed to "some number
    that just happens to come out really close" (as often does happen when
    many formulas with irrational numbers are involved).
    |>obvious.
    | Unnecessary, and misleading.
    Tell that to the calculator or computer giving the results.
    |>| figures etc.
    | Specifying "69282.032302755" as a center point in a range that can be a
    | few hundred volts is absurd.
    That depends on the context. If I want to specifically make a reference
    to a baseline value related by a specific irrational number, more precision
    increases the confidence of correctly matching the numbers. If I just want
    to refer to a "69kv" circuit to by common label, to distinguish it from a
    "12kv" circuit, those terms are enough. But if I do some arithmetic and what
    I end up with is 68971.54879012, even though all steps used many digits of
    precision, then I know one of two things: either an error was made somewhere
    in the arithmetic, or the result happens to be close to, but is not the same
    as, "69282.032302755". If I express either one to 2 digits, each would be
    "69k". Precision in the arithmetic is more than just getting all the digits
    (even though so many are not actually needed for use), but it is about
    understanding what the number is. ONE of those numbers relates to exactly
    120000 as a definition point by a ratio of the square root of three, whereas
    the other does not. When doing arithmetic, this is important to perceive,
    especially if you may be dealing with formulas that come full circle back
    to numbers you already work with.
    |>| back and bite you.
    | YOU know, but does anyone using your design documents, should you be
    | designing something?
    Lots of people certainly don't know how to deal with precision. Lots of
    people say "accuracy" when precision is what is meant ... or visa-versa.
    And who says I would put that on a design document. I would where I feel
    it is important to identify that meaning of a number. But where meaning
    is unimportant and construction value is all that is needed, I would supply
    the value and its tolerance.
    BTW, everything would all be different if we used base 8 or base 12 instead
    of base 10. We "quantize" to base 10 when we round things to make values
    fit available accuracy. Then we force precision to that level. It would
    end up at different points in a different arithmetic base. Thus we can
    actually have differences in engineering or construction that relate to
    what base we use.
    | If you needed to specify the rating of a capacitor to connect line-line
    | in a 120 volt line-neutral 3 phase circuit, would you specify a capacitor
    | with a breakdown voltage of 293.9387692 volts (120V * sqrt(3) * sqrt(2)
    | sine wave peak voltage, plus a hundred picovolts safety margin) ?
    293.93876913398137178367408896470696703591369767880041541192310807 :)
    Seriously, it depends on the context. If I'm trying to match numbers,
    I'd use more digits just to be sure the matching confidence is high.
    Normally, for a capacitor, I'd want a lot more margin to account for
    variation in voltage, environment, manufacturing, and aging. So I am
    likely to say "at least 600 volts" and may even go higher.
    100 years ago you could be a "1000 pound rope" and never see it break
    even with 2000 pounds of load on it. Today, you buy a "1000 pound rope"
    and you can't sue the manufacturer for it breaking under your 1005 pound
    load. That's a misuse of the numbers. And it certainly is not precision.
    It's just being cheap.
    | This is an accuracy issue, but it fails on precision grounds as well.
    | Are the three transformers in a 3 phase circuit _precisely_ identical
    | to that many degrees precision? Is the phase angle _precisely_ 120.000000
    | degrees? Is the resistance/capacitance/indeuctance of the 3 supplying
    | conductors _precisely_ the same? Etc.
    This is called "tolerance".
    Of course not.
    But when one is discussing the bounds of theoretical and comparing results
    to confirm formulas, the numbers have a different set of semantics.
    |>197.9536?
    | What is this "197.45379" figure? A one time measurement? A calculation?
    | If a calculation, what is the accuracy of the figures used in the
    | calculation? What is the "+/- 0.5" figure? A specification? An observed
    | range? An error figure carried through the calculation (say double a
    | figure of 98.726895 +/- 0.25) ? What is the accuracy of the "0.5" figure?
    | Where did all those decimal points come from, was it multiplication or
    | division of something with few significant figures by an irrational number
    | such as sqrt(3)? Depending on the answer to these, it may be appropiate
    | to write it as 197. or 197.5.
    It also depends on whether you are talking about real physical things
    that can be measured to a certain accuracy, or discussing theory and
    the mathematics behind it.
    | There are instances where you have to bring both a figure and the error
    | specification through the calculation.
    | Again, in many cases, you have to bring both the figure and the error
    | range through the calculations. But unless the accuracy error somehow
    | cancels (such as subtracting two figures known to have total inaccuracy
    | from the same source) that extra precision is useless.
    And where I need to bring the error range through, I sure will. And it
    sometimes influences things in unexpected ways (especially with things
    like non-linear effects). But that wasn't needed in my recent posts.
    | Irrelevant to every engineering application I can think of.
    However, keep in mind that is an irrational number. It is always in some
    amount of error. Depending on what kind of math is involved, you might
    need more precision for _this_ number and the calculations using it. For
    example, if a calculation has to be repeatedly multiplied and divided by
    this number as new factors keep being introduced, this error builds up.
    More precision to match the scale of the arithmetic (e.g. how many times
    a program loop doing this has to run).
    Chaos theory describes how this affects calculations. It is also termed
    the "butterfly effect". Was that storm that came through caused by a
    butterfly somewhere? No. Could it have been influenced in some minute
    way? Yes. Not in ways you could measure, but in ways much larger than
    it's small size and mass would suggest.
    | Exactly.
    .... where precision isn't needed ... but engineers need to know where it is
    not needed, and where it _is_ needed. I think too few can do this well.
    | Good engineering can justify calculations without that, plus anything
    | beyond the simplest it really can't be done anyway.
    | Useless except to a math geek.
    | I can tell you for a fact that in introduction to engineering course,
    | writing the line-line voltage of a 120.V line-neutral circuit as
    | 207.8460969V will be marked wrong.
    Most likely what is being asked for is a label, not mathematical matching.
    What would you write for the line to line voltage for a circuit with 230V
    as the line to neutral voltage? 398V? 400V?
    Did you see my proposal for an electrical system (if I could go back in
    time ... a hypothetical exercise that could not really happen today) where
    I proposed a standard voltage of 288 volts line to line, and mentioned that
    it would be based on 144 volts line to neutral from single phase sources
    and 166 volts line to neutral from three phase sources. Then I went on to
    indicate that a higher voltage system could use that same 288 volts in a
    line to neutral way and have 499 volts line to line. I mentioned that I
    thought the voltages were "catchy" because they all ended in two like
    digits. But I wonder if such a system have been used, how many people
    would still end uo just calling the latter "500V".
    Humans LOVE round numbers. I think this is excessively so. So did you
    pick 398V or 400V above? I bet it was 400V. Nice round number.
  16. Guest
    If the precision is so meaningless, what would you do if each time you
    did use a calculator, those "extra meaningless digits" were randomly
    different?
    Wo what would you do if each time you used a calculator that always gave
    you 16 digits of precision was also giving you random variations in the
    lowest 4 digits when you didn't need even anywhere near 12? If you press
    "3" then "SQRT" and keep getting:
    1.732050807566414
    1.732050807569301
    1.732050807569073
    1.732050807568584
    1.732050807568319
    1.732050807565962
    1.732050807569763
    1.732050807567522
    etc
    Would you just ignore the last 4 digits as meaningless, or wonder what the
    calculator was doing? All of these values are plenty precise for work in
    three phase power systems, so why should anyone care?
    It depends on how the numbers are being used. If they are being used to
    show what formula was being used to derive these numbers, precision can be,
    and is, very useful. In most cases just a few more digits does the job.
    I've seen cases where a precision of more than 20 digits was needed to
    verify a correct formula.
  17. Guest
    |> you-
    |> as
    |> "matches"
    |> paths
    |> these numbers:
    |> 138.390751136
    |> 138.564064606
    |> calculated.
    |> 138.564064605
    |> formulas
    | accurate.
    The calculations _may_ be equivalent. Or they may not be. But I know from
    experience that when irrational numbers are involved (like most square roots)
    the chance of a false positive prefect match is very low.
    |> involved
    |> is
    |> confidence
    When you say that "120V" means a voltage between "119.5V" and "120.5V"
    (which I don't necessarily agree with), what are you saying when you say
    "119.5V"? Are you saying "a voltage between 119.45V and 119.55V" ??
    Range has to be defined. It is so often _defaulted_ to be defined as
    have a precision step above or below. But that is not always reality.
    A range might be 3/4 of a precision step above or below.
    "120V" might be a range from "114V and 126V".
    |> then
    |> | what is the point?
    |> voltage
    |> vary
    |> "200v"
    |> high
    That depends on what I'm relating the confidence to. There would be a
    high level of confidence if I am relating 114 to 197.45379 divided by
    the square root of three. But it certainly is possible for the 114 to
    come about for other reasons.
    | as the output.
    | amperes.
    | Check from power
    | the same in each.
    I see now we weren't taking about the same thing. I was only looking at
    each single phase load. You're showing the current lead/lag cancel out
    when the same thing is down in a balanced three phase system.
    Consider the typical "2 legs of 208Y/120" service where an autotransformer
    derives the missing leg:
    A Y A Y
    N Z Y ==> N Z
    B N B
    This is certainly not very well balanced.
    Now you get a voltage between X and Z at a phase angle of the phase that
    is missing. Put a load between X and Z. What phase angle do you get on
    the incoming A-N and B-N? What pf? 0.5? Leading or lagging?
    I could also do:
    A Y A Y
    N Z Y A ==> W N Z
    B N W
    Hey, now I have the 240 volts I wanted, and with a neutral right in between.
    Of course I could have gotten it from either 120 volt leg with a 1:2 step up.
    But at least I am putting half the current on A and half on B. It just has
    a lousy power factor.