Roger said:
Magic. Thank-you both for your help.
Roger
do you know about rupture current ratings? that is the maximum fault
current the fuse can interrupt (without arcing over and then blowing
itself to smithereens). For glass fuses, its bugger all. HRC = High
Rupture Current (80kA typ.). A new NZ house has a fault current of about
6kA, which explains how come techs find glass fuses all blown to shit.
And why microwaves have ceramic fuses, which absorb the fault current by
melting sand.
I had to use HRC fuses in a 48Vdc LED video screen I worked on. Each
module drew 55W at 48Vdc, but there were 2,000 of them fed from the one
telco PSU (100kW), which could happily drive 2kA into a dead short,
continuously. So I needed a fuse with a 10kA *DC* interrupt rating (a
lot harder than AC). I used a Bussman/Cooper ABC series 2A (10kA dc
rupture) fast-acting fuse in each psu, and a MDA series 30A (10kA dc
rupture) slow-acting fuse in each data/power distribution module (drives
12 psu's). why slow acting? couldnt get a fast 30A fuse with 10kA dc
interrupt rating. And the pcb silk-screen has "2A/10kA" written
underneath the fuse, in big letters.
Cheers
Terry