fuse capacity higher -why?

Discussion in 'Electronic Design' started by dew, Mar 15, 2006.

Scroll to continue with content
  1. dew

    dew Guest

    A fuse has a interrupting capacity, which is the maximum current the
    fuse can safely interrupt. Generally this should be higher than the
    prospective short circuit current-why is this so?in other words,why
    should the fuse wire capacity be higher than the line wire capacity
    say for example-the maximum short circuit current is 50 A.if the fuse
    capacity is 51 A, it wil allow 50 A current also.This shouldn happen
    right?plz clarify asap
    thanks
     
  2. The interrupting current is not the fusing current.

    Fusing current is the current that melts the fuse element. The melted
    element will then attempt to interrupt the current by producing a
    break in the continuous metal path through the fuse.

    Interrupting current is the highest current, who's arc between the
    melted blobs of metal the fuse can extinguish within a reasonable
    period of time (a 1 or 2 half cycles, perhaps). If the supply to the
    fuse can produce a short circuit current higher than this, the fuse
    housing will either melt, turn into a plasma ball, explode, or some
    sequence of these effects. None of those reactions is considered a
    safe and successful current interruption.
     
  3. Phil Allison

    Phil Allison Guest

    "dew"

    ** The maximum " interrupting capacity " of a fuse is at least 10 times &
    can be well over 1000 times its rated (maximum holding) capacity.


    ** Simply so the fuse will *open* when a short happens - rather than turn
    into a fire ball.


    ** The continuous current capacity of an *equipment fuse* should not be
    greater than the AC line cables that feed it - however AC line cables are
    always protected by fuses or breakers of their own.


    ** You have your definitions all screwy.



    .......... Phil
     
  4. Joseph2k

    Joseph2k Guest

    Yes, fault currents can be many times to thousands of times that normal
    currents. Interrupting capacity is as described. Also, interrupting
    current capacity requirements are always based on available fault current
    calculations. Having done this several times in the course of my work in
    the past few years has been a real education in protection systems.
     
  5. Terry Given

    Terry Given Guest

    in NZ, an old house will typically have around 1kA fault current; newer
    houses are more like 6kA.

    Where I used to work designing motor controllers, the fault current was
    250,000A - lots of grid-connected SCIMs with inertial loads, and 2m from
    a 2MVA xfmr.

    Cheers
    Terry
     
  6. Phil Allison

    Phil Allison Guest

    "Terry Given"

    ** An absolute LIE.

    ** An even BIGGER LIE.


    ** Yawn.....

    Crap on, crap on, crap on ....




    ......... Phil
     
  7. Terry Given

    Terry Given Guest

    not according to the EWRB (Electrical Workers Registration Board), who
    probably know what they are doing.
     
  8. Phil Allison

    Phil Allison Guest

    "The Pinball Wizard of Nelson "



    ** Blah blah blah ......

    No info - just asinine Kiwi fuckwittery.





    ......... Phil
     
  9. Terry Given

    Terry Given Guest

    your geography is a bit screwy.... nor have I done much work with
    pinballs, and nothing since 1990. perhaps one day you'll learn to
    harness the power of the internet - a quick google search found this:

    http://study.massey.ac.nz/major.asp?major_code=2356&prog_code=93353
    the data came from an electrical inspector, when I did my ESTB a couple
    of years ago (yes, I'm a fully qualified appliance serviceman, although
    the pay is piss poor, who would want to do that shit)

    old houses have a lower fault current than new houses, cos the wires are
    smaller. the 60A pillarbox HRC fuses will actually limit fault current
    slightly (as do all fuses) to somewhat less than the fault current of
    the transformer feeding that house (just as well really), but the dangly
    wires to the house do the bulk of the work - 1kA needs about 0.23 ohm,
    which is ~ 20m of 4mm^2 (incl. return). 6kA needs about 0.04Ohms.

    I recently had the supply to my house re-wired, and as it was 80 metres
    my sparky used 70mm^2 Al, around 80mOhm for the round trip, so at the
    switchboard I will only see ~ 3kA.

    If your house is a lot closer to the pillarbox (modern in-fill housing
    is often only a few metres away), impedances go down and fault currents
    go up. its pretty clear that 1-6kA is quite feasible. Besides, I've
    repaired many PSUs, appliances etc with 20mm fuses (125A rupture
    current) that have been utterly destroyed - in some cases not even end
    caps remained - so clearly the fault current is well above 125A
    (although some of those may well have come from commercial buildings,
    where the fault current is even higher).

    Cheers
    Terry
     
  10. Phil Allison

    Phil Allison Guest

    "The Pinball Wizard of Nelson "

    ** Then you are free to say exactly which Kiwi shithole you ARE the
    "Pinball Wizard" of - Terry.

    We all need to know.

    Urgently.


    ** The cap fits ......

    Even if that pointy head of yours is swollen like a toad fish.

    ( snip puerile tripe about some worthless Kiwi IT degree - peeeeukkeeee )




    ** Yawn .............

    Anyone with a DVM and an 2400 watt electric jug can demonstrate it is
    totally false in regards to a domestic, 240 volt, power outlet.

    **** off - IDIOT !!!!




    ........ Phil
     