I should have mentioned--be carefull if you unlink the the N and E
buses on the switchboard with the power on; check immediately for
voltage drop between the busses when you remove the link. Anything
more than 15 volts or so is cause for concern. A faulty customer earth
and an earth leakage fault on one appliance could raise exposed
metalwork throughout the installation to mains voltage resulting in
nasty and possibly dangerous shocks when N & E are unlinked. shocks
due to an interchanged nuetral and earth connection anywhere in the
system could be fatal under these circumstances. Best to remove the
link with power off and only power up when you want to make
measurements. Electricians use a special high current pulse tester to
measure N/E resistance but a quick and dirty measurement is to connect
a 200 Watt light bulb between phase and earth anywhere in the system
with the N and E busses unlinked. The bulb should light at full
brilliance and voltage between the E & N at the switchboard should
still be under 15 volts or so. If not, then you need an electrician.
If AU regs are the same as NZ then work on the switchboard and on the
installation earth has to be done by a registered electrician,
especially if you want to keep your insurance cover.