DSC 4020 CF

Discussion in 'Security Alarms' started by Buggs, Aug 6, 2007.

Scroll to continue with content
  1. Buggs

    Buggs Guest

    I have a new 4020CF commercial fire panel V 3.54 that won't answer a
    download call. Verified connections, polarity, voltages, and programming
    with no luck. DSC tech support is clueless. Anyone had a similar problem?
     
  2. did your try totally powering down panel and repower back up this works
    with other systems when they jam.
     
  3. Buggs

    Buggs Guest


    Yup.
    js
     
  4. Buggs

    Buggs Guest

    Yeah, no problem. It connects via PC Link too, it just won't answer the
    phone.
    js
     
  5. Frank Olson

    Frank Olson Guest

    Check the main chip. If it says "Made in Sarasota", that explains why
    it won't answer the phone.
     
  6. A.J.

    A.J. Guest

    The line that it is hooked up to actually rang ?

    I came across a bulding where the communicator was using the manager's phone
    and during the day time she had the phone line call forwarded to her cell
    phone.
     
  7. Norm Mugford

    Norm Mugford Guest

    Verify the phone number on the line to make sure it's the
    line you're calling, then try reversing tip & ring.

    Norm Mugford



    I choose Polesoft Lockspam to fight spam, and you?
    http://www.polesoft.com/refer.html
     
  8. Buggs

    Buggs Guest

    Yup.
    js
     
  9. Buggs

    Buggs Guest

    The line rings, and tip and polarity checks ok.
    js
     
  10. Buggs

    Buggs Guest

    S.B. Polarity checks OK.
    js
     
  11. We had the same thing happen with a 4020, DSC told us we had too many devices on the system and the board was not getting the proper amount of power to work correctly.

    Went to Tri-ed bought a new board, CHANGED ONLY THE BOARD, and now we could upload from the office.

    I think you may just have to change out that Defective Security Cpu. PC-4020.
     
  12. Buggs

    Buggs Guest

    We had the same thing happen with a 4020, DSC told us we had too many devices on the system and the board was not getting the proper amount of power to work correctly.

    Went to Tri-ed bought a new board, CHANGED ONLY THE BOARD, and now we could upload from the office.

    I think you may just have to change out that Defective Security Cpu. PC-4020.


    Yeah, I ordered a replacement, which should be here today.
    The only devices connected to this board is one keypad, and a 4701 dual phone line module. DSC tech support may as well not exist. I have called them only a few times over the years, and have been disappointed every time. This is the last time I ever use a DSC fire panel.
    js
     
  13. Buggs

    Buggs Guest

    Yea, this one is a combo. I don't ever do a full ul/dl on a maxsys panel,
    but I still like to be able to connect to it. This is the last time I'll use
    one for fire though.
    js
     