JosephKK
Tom Bruhns [email protected] posted to sci.electronics.design:
From the few handfuls of times that i have made the calculation, it
seems to be about 370 ohms. That can't be a coincidence can it?
If you assume a two-wire line made from highly conductive round
wires two inches in diameter and spaced 200 inches apart, well away
from any ground and essentially air-insulated, the differential mode
impedance
will be pretty nearly 636 ohms resistive. To get to 1000 ohms,
they'd need to be spaced 4160 inches apart, and kept much further
than that
from ground. It's tough to make a really high impedance RF
transmission line.
If you're operating a line at a frequency where the series
resistance of the conductors is an appreciable fraction of the
series inductive reactance, or the shunt conductance is an
appreciable fraction of the parallel capacitive reactance (in other
words, at low frequencies),
the line characteristic impedance may be quite reactive. The calc I
just did for this hypothetical line at 60Hz and assuming room
temperature copper conductivity suggests about 636-j10 ohms;
assuming I didn't mess it up, you can probably forget about the
reactive part for most calcs.
Cheers,
Tom