continuous online dual conversion UPS
Discussion in 'Electrical Engineering' started by [email protected], Mar 3, 2009.
  1. Guest
    While reading some technical descriptions of specific UPS models, including
    user manuals, I have found that many describe a low voltage level at which
    they "switch" or "transfer" from utility power to battery power.
    For this kind of UPS, where even the utility power is always converted to DC
    and then back again to AC (inverter), why can't they do a combined capability
    in a low voltage situation in order to extend the battery as long as possible?
    One type of low voltage scenario I have seen happen a few times is when the
    voltage is dropped to HALF the nominal voltage. The primary (pardon the pun)
    cause I understand for this is when a delta-wye transformer loses one phase
    on the primary side. Suppose phase B is lost. Phases A and C are still live.
    The delta primary A-C winding still has full voltage. However, the A-B and
    the B-C windings are in series fed from phases A and C. Given an equal load
    on the secondaries for A-B and B-C, this should divide the voltage in half
    for each. So 120/240 becomes 60/120, and 208Y/120 becomes 104Y/60.
    At half the voltage, a UPS would want to draw twice the current to sustain the
    connected loads (maybe more if the circuitry operates at less efficiency in
    this condition). And that may be too much current. At some low voltage the
    current will exceed what the input should operate at.
    So, when this low voltage condition exists, why not just go ahead and operate
    the AC to DC conversion at a level right at the current limit, and obtain the
    remaining power from the battery? By drawing less from the battery, and the
    most that is still safe from what can be gotten from the low utility voltage,
    the battery can last longer than it otherwise would. Is it too complex or
    costly to make an AC to DC conversion (basically a power supply) section that
    would operate on these lower voltages? Or is it too complex or costly to make
    one that can limit its operation to a specific current level?
  2. Guest
    | Another idiot idea from Phil. Why would you want the added
    | complexity for a half assed idea that would make the unit more likely to
    | fail? Why do you think CVTs are used on some systems? On second
    | thought, do you ever think things through before starting one of your
    | weird assed threads?
    You can't read. But then, you seem to have had this trouble for the past few
    years. I would speculate it has been a lifelong condition for you. I simply
    do not know if this was something that happened early in your life or just a
    few years ago, since I have not seen your writings prior to a few years ago.
    The unit is more likely to fail if you let the battery carry the full load,
    instead of letting the battery share the load with what power it can get from
    the available mains voltage.
    And I did not specify a particular design. If you want to discuss the failure
    modes of a particular design, then go ahead and spell out what that design is
    and we can discuss how and why it might fail (break down). If you do that, do
    keep in mind that it was your design, not mine.
    If you want to assert a belief that no design is possible to do this, then by
    all means assert that. That will, of course, open you to the criticism that
    you are unable to come up with all possible designs, and MAY have missed one
    that would work well. You could defend against that by spelling out all the
    possible designs in advance.
  3. Guest
    | I have no problem reading and identifying moronic concepts.
    You have no skill in reading electrical enginering or technology. All the
    rest is fiction in your mind.
    | Then the battery is too small, or too old. An overly complex design
    | isn't the answer to crappy maintenance.
    It doesn't matter what the battery size is, small, medium, or large. If you
    power the loads entirely from the battery, it will last a shorter time than
    if you power the loads half from the battery and have from the mains.
    | You didn't specify a design because you can't. It is another of your
    | ignorant 'Gee Whiz!!!' ideas that won't work.
    Whether I can or not is irrelevant. I didn't try. So it doesn't matter.
    What I did was ask about the concept. You suggested it would fail, so you
    are the one that has a specific design in mind. YOUR DESIGN is a failure.
    You said so.
    | Its your stupid idea so its up to you to show us a design that will
    | work while meeting all safety requirements, including isolation form the
    | faulty power line, while continuing to draw power from it. How are you
    | going to match the distorted waveform in real time, and adjust the
    | voltage to what you need? Like I said in my first reply, "Why do you
    | think CVTs are used on some systems?" but you didn't answer, because you
    | don't know, or because it would prove this stupid scheme is worthless.
    I came up with the basic concept. I didn't say I have a design that would
    work. I didn't say there has to be a design that worked. I ASKED ABOUT THE
    CONCEPT. YOU are convinced it cannot work, but YOU are completely unable to
    say why it would not work. Sounds to me like you are unwilling to disclose
    your design failure or whatever logic you came up with that suggests all the
    possible designs would fail. So what's left is your baseless assertion.
  4. Guest
    | Yawn. Another lame attempt to slur my name. The 'fiction' is that
    | you believe the crap you dream up will work. What have you ever done in
    | the real world? My design ideas are in space, aboard the ISS, used to
    | track everything launched by NASA, the ESA, and by NOAA to track and
    | control their LEO Weather Satellites. I also came up with the idea of
    | uplinking a subcarrier channel to a C-band satellite from a different
    | site than the main carrier. This was for United Video's microwave
    | division for their EPG service on the WGN feed. It eliminated two
    | leased phone lines from Salt Lake City where the mainframe computers
    | were, to the WGN uplink in Chicago. It provided a more reliable service,
    | and the savings of over $15,000 a month for the company I worked for.
    You could have made a lot more contributions to the world if you had the
    ability to read English and did not have the attitude of distorting what
    people say so you gain the ability to make assertions that are really false
    and lets you blame it on them. I'm not going to play your penis length
    game. There's no way to verify the truth or significance in anything you
    say.
    Maybe you really did those things in the past and maybe they will work fine.
    But your brain is certainly not keeping up. Damaged?
    | If the battery size doesn't matter, then use eight AAA cells.
    You are a complete lunkhead if you haven't figured out by now that this is
    about comparing the SAME SIZE BATTERY with 2 different wiring schemes, one
    where the battery carries the full load, and the other where the battery
    carries half the load. If YOU can't figure out the basic concept that when
    a battery only carries half the load, it runs longer, then I guess I need
    notify NASA, ESA, NOAA, that they might some flawed engineering running and
    their missions are at risk of things like premature battery failure. That
    is, if you aren't lying.
    |> You said so.
    | I didn't try to design anything, because your concept is so flawed.
    | That is something you never see in the stupid crap you dream up. Your
    | stupid idea would be dropped in ten seconds in a design review, and you
    | would be told to clean out your desk.
    You think that the concept of running a battery at half load to extend its
    run time, relative to the same size battery running full load, is a flawed
    concept?
    Now I have to say it ... what an utter moron.
  5. Guest
    | wrote:
    | What we used to do to power 2 way radio systems for police and fire
    | systems is power the systems from batteries full time with a smart
    | charger that is big enough and well filtered enough to power both the
    | loads and charge the batteries. No switchover time, will charge the
    | batteries even in brownout conditions.
    Lots of AC to DC converters, chargers, and power supplies, can work on a
    wide range of voltage coming in. If it is rated 100-240 volts, as most
    computer power supplies are, then connecting it to a 240 volt circuit
    gives you a LOT of deep brownout range. Just be sure the circuit has
    amperage capacity for the low voltage scenerio.
    The question I have is whether it is something UPS makers can do. Based on
    ratings I have seen, they design for a limited amoutn of brownout. The ones
    in the Minuteman Endeavor series I was looking at had a low voltage cutout
    at 86 volts for the 120 volt models. That's not as much voltage range as
    computer power supplies. Maybe they could do better. Maybe it will cost
    $10 more and ruin their market advantage for the average consumer.
  6. Guest
    |> say.
    | Keep throwing your hissy fits, Phil. You can't design anything, and
    | continue to show the world what a fool you are.
    What did you think I designed?
    You're the one that doesn't understand how to extend the life of a battery
    by reducing its load.
    | That wasn't what you stated. You said the battery size doesn't
    | matter, not how the same size battery was used. You claim I can't read,
    | yet you can't even read what you wrote.
    And the statement is correct. The size does not matter for the principle
    to apply. If you understood what the principle is, maybe then you would
    understand that it works no matter what size of battery is involved. If
    the load on the battery is reduced, it will last longer.
    |> |> You said so.
    |> concept?
    | I never said that. I stated that a properly sized battery was need
    | but as usual, you can't read and comprehend anything. Properly sized
    | means that it has a reasonable reserve, and in exchange will give you a
    | longer run time, if needed before the power is restored, or a backup
    | generator comes on line. A larger battery is more reliable than the
    | Rube Goldberg crap you come up with. You need to learn the KISS method
    | if you want things to keep working.
    Whatever size you have, if the load is reduced, the battery runs longer.
    If you do ever need it to run that long, maybe you got a too large battery.
    The real world involves UPSes that in most cases have limitations on the
    battery size, while the market wants longer run times. The "proper sizing"
    is just not something that is easily doable. That's a concept that applies
    when setting up large scale batteries with separate chargers and inverters.
    And I've done that for two mainframe data centers.
    | We know you're a moron.
    You've proven your ignorance.
  7. Guest
    |> |> say.
    | Absolutely nothing that has ever worked.
    With respect to this thread, I did not design anything. So I guess you
    have actually made a statement that would evaluate as true.
    | Bullshit. I stated several times in this thread about choosing the
    | proper capacity which isn't using them at 99% of their rated capacity.
    | I am a firm believer in properly de-rating a design so it is never
    | stressed beyond reason, but your blind ignorance forces you to ignore
    | what anyone tells you.
    When have you ever designed a UPS that is in commercial production?
    Guess what. They don't do this. They can't. The reason they can't
    is because needs vary so widely. The best they can do is make a
    range of designs and let the buyer select what will most closely fit
    their needs.
    | As you can see a few lines down I stated : Then the battery is too
    | small, or too old. An overly complex design isn't the answer to crappy
    | maintenance. then you tell me I would chose too small of a battery,
    | once again proving you have zero comprehension of anything you read.
    What I stated is a fact that follows across all sizes, ratings, and ages
    of common batteries. Your statements don't even address it at all. You
    have no comprehension of what is being discussed. As I have said before
    in other past threads, your difficulty is comprehending English well enough
    to realize what people are talking about.
    | Sigh. You can't even tell there is anything outside the box, can
    | you?
    Specify what box you are referring to.
    | Whoopee. Two whole jobs. Get back to me when you know what your
    | trying to do. y starting with say 50% extra batter capacity, they will
    | last longer, and still be usable as they start to degrade, as well as
    | handle surges if something has to be restarted while the system is
    | running on the UPS.
    I never said anything about "50% extra batter capacity". Your failure to
    understand what you read is in play, again.
    I referred to reducing the load on the battery by 50%. That means a battery
    with linear runtime characteristics (a hypothetical battery that merely
    approximates real life battery performance) would run twice as long. That
    isn't "50% extra batter capacity". It *IS* effective a 100% extra UNIT
    capacity when considering one unit with the feature I suggested against a
    unit without, when they each have the same battery.
    Of course real batteries are non-linear with respect to runtime, and vary
    with other factors like aging, wear (number of cycles), temperature, and
    rate of usage (the power drawn from it).
    | Phil, you are a world class ignoramus who lives to put layer after
    | layer of cheap lipstick on the pigs you dream up. Your other hobby is
    | separating fly shit from pepper, under a broken microscope.
    | Keep showing everyone what a fool you are. Some people enjoy watching
    | you go down for the third time, so they can toss you a concrete life
    | preserver.
    | No one expect you to ever learn anything or to admit what a fool you
    | really are. You make Roy look smart, by comparison.
    I'm only showing what a fool you are.
  8. Guest
    |> their needs.
    |> | you?
    | You are so stupid that you hav enver hear of "Thinking outside the
    | box"?
    You are quite creative. You have that going for you.
    I know about "Thinking outside the box". But you didn't specify that
    box as the one you were referring to before I asked you to.
    |> | running on the UPS.
    | No, I SAID THAT I WOULD USE A BATTERY BANK 50% MORE THEN THE MINIMUM
    | TO EXTEND ITS LIFE.
    With some UPSes you can do that. With others, you can't.
    I *AM* talking about a redesign (without yet doing that redesign) of the
    charging (AC to DC) component of the UPS so that it will get whatever
    power it can get from a deep brownout condition, and use that to charge
    the battery or supplement the use of the battery.
    It is PLAUSIBLE to do this because switch mode power supplies, which are
    devices that convert AC to DC at one or more DC output voltages, can
    readily and easily be made to operate over a voltage range greater than
    2:1. Most computer power supplies now do 100 to 240 volts AC continuous,
    without needing one of those "115/230" switches. Almost all my wall
    warts do this, too. If it can be done for 100 to 240, it could also be
    done for 50 to 120, and thus be within the range for the class of deep
    brownout I have seen about half the time. Or a 240 volt class UPS can
    be left at the 100 to 240 volt range. What will need to be done to
    accomodate this is to be sure the current at the low voltage can be
    handled, or be restricted/limited.
    So really, I don't even need to design this. It has already been done.
    |> | preserver.
    | Tell me, Phil, how low of a line voltage do you expect your fantasy
    | UPS to work, without being completely on batteries?
    At least one existing UPS can go down to 86 volts or lower for a 120 volt
    system. Switch mode power supplies are readily available for the 100 to
    240 volt range (check your own computer(s) and see). Just build one big
    enough to drive the inverter and charge the battery. Front end it with a
    120 volt to 240 volt transformer if you want to power it on 120 volts. Or
    just connect it to a 240 volt circuit.
    If a switch mode power supply can be made to operate over a 100 to 240 volt
    range, then a similar design for a smaller voltage could do 50 to 120 volts
    if that is the desired system voltage.
    Note that the 100 to 240 volt range is nominal. They do have a wider range
    to accomodate voltage variations of 5% or even 10%. Power supply specs I
    have seen often say they work down to 90 volts. And this is without looking
    for wider range ones. I bet a real electrical engineer would know how to
    make one handle 45 to 305 volts input AC with a reasonbly constant DC output
    at some voltage.
  9. Guest
    |> | box"?
    | Lame excuse.
    Factually accurate. Look back at what you posted (and did not include
    in your last post ... how convenient). It could have been any box.
    |> | TO EXTEND ITS LIFE.
    | We were talking a new design so that is a lame answer. Do I have do
    | define 'Lame' as well?
    Maybe a new design. But I never said I designed it. I never even gave
    a design. Yet you acted as if I have provided a design.
    Existing designs can be used if full power conversion is acceptable over
    the full voltage range, either 100 to 240 volts for a 240 volt system,
    or 50 to 120 volts for a 120 volt system. Power supplies (chargers, AC
    to DC converters, by any other name) are already designed with this wide
    of an input voltage range. The only change in design that might be
    needed is model specifics, such as a particular capacity or form factor.
    This is stuff electrical engineers frequently do, as evidenced by the
    myriad of products like this on the market.
    Where a theoretical design change would be needed is when it is desired
    to have an upper limit on the current being drawn. At lower voltages
    this would mean less power is drawn. That would be needed, for example,
    when a nominal power of 1000 watts is working on a 120 volt circuit, and
    it is desired to limit the current at 12 amps to operate within the 80%
    single dedicated device rating on a 15 amp circuit. Down to 83.333
    volts, the full power can be sustained. Below that voltage, the power
    level must be reduced to stay within the 12 amp limit. So at 50 volts,
    the power would be only 600 watts. If the load being powered is 1000
    watts, then 400 watts has to come from the battery. But that's only 40%
    of what the battery could carry. If the load being powered is only 600
    watts, then the battery has no load at all.
    The above figured are based on a hypothetical 100% efficiency ONLY for
    the purpose of simplified explanation. In reality efficiency levels
    would vary around 90% to 96%. It would complicate the explanation to
    use those figures, and make it harder for some people to see what is
    going on. In a real product design case, it would be more complicated.
    That's the job of the engineer doing the actual design.
    | Really? Then go buy it.
    I already have many such power supplies. What is not available is such
    a power supply in an integrated UPS.
    |> at some voltage.
    | Is this fantasy supply for a single computer, or for a room full of
    | servers? It makes a huge difference.
    It will make a difference when one is being selected for deployment.
    While the concept would work across a wide capacity range, it would only
    be economical for a smaller scale. I estimate the practical limit would
    be around the 6kVA to 10kVA per room or building.
  10. Guest
    | wrote:
    |> |> | box"?
    |> | Lame excuse.
    | Bull shit.
    The creativity, again.
    |> |> | TO EXTEND ITS LIFE.
    | No, I didn't. In fact, you can't even write a decent set of
    | specifications. That is the whole point. You post stupid ideas, with
    | no groundwork.
    You said I designed it wrong. That is the same as you saying I designed it.
    | The wide range units switch the input configuration, depending on the
    | input voltage and under the control of a custom IC. It isn't a single
    | wide range.
    Actually, it is a single wide range. This was verified directly with
    one of the manufacturers that offered both full range and switched range
    models. One thing they said is that extra cost of full range is so low,
    now, that it is reaching the savings of having fewer models. There is
    some threshold switching that takes place in many models to change
    characteristics to make it more optimal at different parts of the range.
    For one model I asked about, that change happens at 166 volts RMS.
    | You have that backwards. The switching supply is designed to output a
    | fixed voltage, and the lower the input voltage, the higher the input
    | current. Also, it may be higher than expected, due to a distorted
    | waveform at the AC input. It will attempt to provide the power required
    | by the load, as the input current goes up. That is the major flaw in
    | your half assed concept.
    Again with the inability to read.
    I previously in that same post described the normal case of a lower
    input voltage having a higher input current. Then I described here the
    special case of a current limit. Do you even understand what a current
    limit is? Maybe not.
    When the current input is limited, and has reached the limit, then the
    power input goes down as the voltage goes down. Common power supplies
    just shut down at this point. As I said, this case is a "theoretical
    design change". But I guess you didn't read those words or even
    understand what they meant.
    | the losses also depend on operating temperature, battery condition,
    | and the percentage the load represents of the UPS design allows. The
    | harder you push it, the hotter it runs, and the higher the losses.
    I didn't intend to list everything. Thank you for adding to the list so
    others who read this have a more complete list.
    | Then it doesn't exist, and you lied.
    The wide range power supplies do exist. So no new design is needed for
    the simple case of operating at 60 volts on a 120 volt system, other
    than scaling it down from 100-240 to 50-120, which would not be hard.
    The slightly harder design, which I am sure any experienced power supply
    designer can do, is the current limiting design. But you don't even
    understand what current limiting is, so you are way way out of the
    running for being able to design such a thing.
    |> |> at some voltage.
    | Really? Do you have any ideas what is required to build that
    | abomination? I do know, and you won't like the answers.
    You've shown you don't even understand many of the concepts. How could
    you possibly be able to design these things if you don't even understand
    what it is supposed to do? Yeah, I won't like the answer that you can't
    accomplish it, if I were in the business of making UPSes. I'd have to
    hire a different engineer.
    | Show us you know what you claim by describing what has to be done to
    | make it operate the way you want, or admit that you are the moron you're
    | know to be.
    I've already described what it needs to do. It needs to keep supplying
    DC power in such a way that the inverter fully operates at up to the
    rated inverter load, using all the DC power available from the
    converter, and gets else is needed (but no more than this) from the
    battery. I'm not talking about the circuit details. Those things have
    already been done in other things besides UPSes. This is just a product
    design (that's not the same as circuit design) and integration issue.
  11. Guest
    |> remaining power from the battery? ?By drawing less from the battery, and the
    |> the battery can last longer than it otherwise would. ?Is it too complex or
    |> costly to make an AC to DC conversion (basically apower supply) section that
    |> would operate on these lower voltages? ?
    | Yes. UPSes are designed as cheap as possible. Some have seen how
    | cheap. Replacing a UPS is sometimes less expensive than replacing its
    | battery. Why make it more complex and more expensive?
    | Second, UPS battery is charged by a power supply equivalent to a
    | wall wart. To accomplish what you have suggested means that battery
    | charging power supply must be larger: increased costs. Or it must
    | have an even larger operating input voltage - again increased costs.
    | Just another reason why it is not done.
    How much larger does it get just to extend its lower voltage range?
    How much larger does it get to make that extended lower voltage come
    with a constant current level at a certain current limit?
    | Third, AC utilities providing voltages at that low level is a
    | specification violation. It rarely happens. If detected, utility
    | typically cuts all power off due to defects that might cause such low
    | voltages. IOW a more complex UPS circuit and the larger battery
    | charger would rarely prosper from such a condition. Better is to get
    | you to buy a larger (more expensive) UPS - and keep this UPS as cheap
    | as possible.
    Utility equipment is also done on the cheap. I've seen the half voltage
    scenario ssveral times in different places. In one instance it persisted
    for over 4 hours. In theory, a phase loss detector in a transformer should
    signal an upstream cutoff. It doesn't always happen.
    This is one reason (there are others, too) I'm wanting to run my computers
    directly on 240 volts. If there's a deep brownout, they can still run in
    that condition. The impediments to doing this include finding the right
    surge protection (easy for entrance protectors, hard for point of use) and
    the fact that existing UPSes defeat the ability to operate over the wide
    voltage range (why I raised this issue to begin with).
    A battery charger (in a UPS or as part of a separate component system)
    that can be set to specific power or current limits can also be useful
    in using small generators to supplement the battery in a total loss of
    power.
    | Fourth, if a low voltage condition exists, unstable AC power is best
    | disconnected from equipment anyway. Maintaining voltage too low can
    | be harmful to electric motors and to the distribution system.
    | Therefore, when that defect is detected, reliability says better is to
    | disconnect.
    For anything that increases the current, and is not rated for that increase
    in current. That's why my idea of making the power supply component have a
    current limit and just scale down its power intake, stretching the battery
    run time.
    | Fifth, a UPS is for saving data. Making the UPS more complex for a
    | rare type of failure is not useful. If a UPS needed to operate
    | longer, then the UPS is too small anyway. Better is to get you to buy
    | the more expensive UPS with a bigger battery.
    What the UPS is for depends on the scenario. In many cases I have seen,
    especially for ISPs and web services, it's to ride out power outages.
    The sizing is done by CFOs. Batteries are the biggest part of the cost.
    | Those UPSes are designed to sell mostly on price - as cheap as
    | possible. Why do anything to make its price higher? Five different
    | reasons why the suggestion is not useful.
    An increase in charger cost, that can provide longer batter run time than
    an the increase in battery capacity of the same cost, provides more run
    time for the dollar.
    This is why I often have the desire to just build a UPS from separate
    components. I'm not an electrical engineer. At best I am an electrical
    hobbyist.
    | Michael is a technician. He knows what a technician knows - what to
    | do. He often does not know why - what an engineer learns. Therefore
    | he has a repeat habit of attacking others because he does not know
    | why. Attacking others is trick often used to mask the posters
    | technical naivety. Unfortunately it works because others see the
    | insults and then believe the insulter. Rather than learn the facts,
    | many instead believe the first one to post insults. It is also how
    | Rush Limbaugh operates.
    I've known many technicians (and engineers). I've also listened to a few
    radio talk show hosts, and watched equivalent ones on TV (such as Glen Beck).
    Most manage to remain respectable. There are exceptions like Michael and
    Rush.
    I've learned years ago that when I see someone insulting someone else online,
    and not just on Usenet, that it more likely means the insulter is upset at
    something. I've also learned that it can be hard to find out just what that
    is because so many cases are merely a misunderstanding somewhere.
  12. Don Kelly
    Don Kelly Guest
    As an engineer, (and retired EE professor) , I have learned to listen to
    technicians and gain from doing so. I have tried to teach future
    engineers to recognize that they can find the difference between those
    with many years of experience and those with one year's experience,
    repeated many times- and learn from the former.
    I am not impressed with those who say "I am an engineer and he is <just>
    a technician'. Such a statement says more about the deficits of the
    "engineer" than those of the "technician".
    Both you and Phil have useful things to say. Neither needs to hurl
    insults. I don't agree with all either of you have to say, nor do you
    agree with me on everything. Fair enough- unfortunately, on the net it
    is difficult to sit down and have a beer together and sort things out
    properly.
  13. Guest
    | That depends on how much you want to supplement the batteries, and if
    | it is even possible to draw the additional current from the AC line in a
    | brownout condition. Every thing in the input stage has to be larger,
    | including the circuit supplying power to the UPS & computers. The
    | switching supply will need larger electrolytics, heavier rectifiers,
    | more switching transistors, and a bigger switching transformer for the
    | charger. You will need to add fans, or use huge heatsink. Some UPS
    | use the same transformer to charge the batteries and for the output
    | transformer, so you would need a complete new charging circuit.
    So you are questioning the ability to draw current when the voltage is
    at half level? If you can't, then that means there is a systematic
    impedance change. Do you have in mine where that change is? Or are you
    just trying to be difficult.
    Not everything has to be larger.
    If it is a limited power device, then the current could double for half
    the voltage. Components dealing with the incresaed current will need to
    be larger. Once the device has the voltage at a fixed working level to
    derive other voltages, then part is just the same size.
    If it is a limited current device, then very little will need to be
    increased in size. There will have to be added the circuitry to limit
    the current when it reaches a certain level.
    | High current supplies like that can catch on fire. The Northern
    | Telecom PBAX telephone system we had at Microdyne caught fire and smoked
    | damaged 80,000 square feet of office, engineering, production and
    | storage space. It took over three months to repair the offices near the
    | fire, and you could still smell the smoke a year later. Our insurance
    | paid for all the repairs, then sued the OEM. The damage came close to
    | putting us out of business. Luckily, the phone room was in the
    | engineering department, and some of the people could work from home, but
    | it dropped productivity quite a bit. If any part of that system was
    | home brewed, we would have had to pay for the repairs ourselves. The
    | system was in a locked room, and caught fire late one night. if someone
    | who was driving through that industrial park hadn't noticed the orange
    | glow, we would have lost all the offices, both stockrooms and all of the
    | engineering department.
    If we are dealing with a constant power device, then a 1000 watt model
    will have current levels at half voltage similar to a 2000 watt model at
    nominal voltage. Are you saying that the 2000 watt model is more of a
    fire risk than the 1000 watt model ... AND is so much more of a risk
    that such current levels should be avoided?
    If we are dealing with a constant current device, then "high current" is
    a constant.
    |> | as possible.
    | Phase loss detection is the customer's problem, and is solved by using
    | a PLM and either drive an alarm, or use it to shut down equipment that
    | is easily damaged. There was a company in Leesburg, Florida making
    | them. They were small enough to hold in your hand and made to mount
    | with typical industrial relays and timer modules. if you lose a phase,
    | but have some large 3 Phase AC motors running at the time, they will
    | continue to run, but draw the additional current from the other phases,
    | causing the motor to run hotter. Look up 'Rotary Phase Converter'
    If a phase loss results in nominal voltage on 2 phases and zero on a
    third phase, then that would be a phase loss to the customer. However,
    if the utility wires things in such a way that a phase loss upstream
    results in half voltage to SINGLE PHASE customers for an extended period
    of time, then that is a utility problem.
    | Take a careful look at the power supplies you are considering,
    | because a lot have a dead band between the two voltage ranges. All they
    | do is sense the input and select 120 or 240 range to keep the costs
    | down I see them specified as 90-130 & 180-260, leaving a dead band
    | between 130-180 volts where operation isn't guaranteed.
    Many are that way. Many more are full range. Full range is becoming
    more and more common. Maybe you should take the careful look.
    |> power.
    | if you buy a small generator, get one with an accurate governor, or
    | that is a DC/inverter package like some of the Hondas.
    And regulator.
    |> | disconnect.
    |> run time.
    | You can't limit it very much and have anything useful.
    With limited current, you can have half power at half voltage. That may
    only be half as useful, but it can be useful. For example, if the UPS
    is fully loaded, half the power needed to run the loads can be drawn
    from AC and the other half from the battery ... instead of all from the
    battery.
    | If the CFO is so cheap that he is willing to use home brew backup
    | power, its time to find another job. The costs to get a custom system
    | through UL approval will buy several lifetimes worth of batteries. Do
    | you have a PE willing to sign off on your modifications? Will you be
    | able to find fire insurance for the business that will pay a claim after
    | a fire?
    The CFO sets the price limit. It's called a budget. Engineering can
    sometimes wiggle this some. But not always. Or not generally by a
    great deal.
    So, where batteries are the substantial cost, and there is the real
    possibility of getting half the voltage for some reason, then a UPS
    system that works this way and provide more run time on that fixed
    battery capacity.
    There is a valid market issue. Is there a market for such a device?
    Probably not. Can it be designed? I think it can. The components have
    already been done.
    | Not if it isn't legal to use. If the fire inspector sees a homebrew
    | UPS during any visit, he is allowed to have the power to the building
    | turned off till it is removed. You still don't see the big picture,
    | Phil. Its one thing to homebrew a power supply to use at home, but for
    | a business, it is a huge liability.
    If it is an engineered custom design, this is not true. Businesses have
    various kinds of systems custom designed for them all the time.
    |> hobbyist.
    | Do the math, Phil. The extra hardware costs, plus the testing &
    | added liability costs quickly wipe out any possible savings. An
    | properly sized generator with an automatic transfer switch is cheaper
    | than getting a custom UPS approved for commercial use. if the generator
    | is propane powered, it won't have a problem with the fuel going bad
    | while in storage.
    If YOU have done the math on the hardware component costs, then YOU have
    done a design.
    |> Rush.
    | Why? Because I tell you something is flawed, and you never listen?
    It's more a case of not believing you because you have a track record of
    saying some of the dumbest things I've heard online.
    | I have worked in electronics my whole life, including manufacturing of
    | power supplies. I also qualified new suppliers for the few switching
    | power supplies we bought, and dequalifed multiple vendors when the
    | shipped product didn't match the build quality of the test samples. One
    | of the TV stations I worked at had 500 KW diesel generators for backup
    | power, and the only UPS was for the video automation computer. A few
    | battery powered emergency lights were mounted around the walls, but if
    | the three generators didn't start, two UHF TV stations, five 50 KW FM
    | stations, trunked business radios and multiple government agencies were
    | without power for their equipment.
    You've told us about some of your experiences, before.
    | The only way to get some people's attention is to resort to insults
    | and you are know for hurling your share of insults, as well.
    I go to extra effort to avoid using insults. For a few people like you,
    that gets to be very hard to do, and sometimes it just has to happen.
    But check your own posts. You'll see insults generally begin with your
    first followup post in the original thread.
  14. Guest
    | Sigh. Do it. Design it, build it, and use it. Then see what
    | happens during a brownout.
    I'll buy it when it comes out as an integrated product.
    | Give details on what doesn't need modified, since you have all the
    | answers.
    It's an integration project. Just put a wide range power supply in
    place of the narrow range power supply, and change the control logic to
    allow wide range operation.
    | If it is current limited, it will be of little use. The existing
    | charger may take up to 24 hours for a complete charge, and would give
    | you less than 10% of the battery's A/Hr rating. Think about it: 24
    | hours to fully charge, and 15 minutes to run them down.
    The current limit is for operation at lower voltage, reduced power. One
    doesn't recharge the battery unless there is sufficient input power
    available to do that. Many current UPS designs use about 1 amp input to
    recharge after a long usage. Rapid recharge is not much of a demand.
    It could be done, but as you know, you'll need a larger circuit for it.
    | Constant load, maybe, but there is the law of 'Conservation Of
    | Energy', and all your dancing can't get yo around that. You have losses
    | every time a conversion is made, which adds to the heat load for the
    | building. If you don't remove the heat, the equipment dies a lot
    | faster, adding to the capital equipment costs.
    So you think there is more heat produced at lower power?
    |> a constant.
    | The only constant current is into the load. if there isn't enough
    | available, you get data errors, or crashes.
    The idea is to provide a constant voltage to the load, and shutdown when
    not enough power is available to do that.
    |> |> | as possible.
    | It is their responsibility to make quick repairs, it is up to the
    | customer to protect their equipment.
    That doesn't always happen, for many reasons.
    | I have, and I don't like the specifications on a lot of them. Too
    | much ripple, and other problems. Look at the efficiency of some when
    | not operated near the two nominal voltages, as well. There are no idiot
    | proof designs, but overly complex designs will come back to cause major
    | problems, more often.
    I have found that computer power supplies of the 100-240 volt design do
    run more efficiently at 240 volts. Is that what you are referring to?
    |> |> power.
    |> And regulator.
    | Show me any commercially available genset designed for autostart &
    | transfer switch that isn't regulated properly.
    Use your own Google.
    |> |> | disconnect.
    |> |> run time.
    |> battery.
    | Like I said several times before, the waveform is less than ideal during
    | brownout conditions. Do you monitor the line voltage with a true RMS
    | meter, or a cheap DVM? You need to look at the AC line with a scope
    | during brownouts, and other problems to see what crap the equipment has
    | to deal with.
    I'll let you know.
    |> | a fire?
    |> great deal.
    | A budget is a goal. Some are reasonable, some aren't. Sometimes you
    | have to walk away from the CFO and let them find out for themselves.
    | BTDT. They told me I was unreasonable with my costs, then found out
    | everyone else wanted three to ten times as much. In some cases they
    | spent the money. in others, they had to scale down their plans, or
    | delay them till more money was available. A CFO operates on greed.
    | Engineers operate on logic.
    And what do you techs operate on?
    |> battery capacity.
    | SO what? Either you can afford to be in business, or you can't. It
    | sounds like a shoestring operation that is about to close its doors.
    Or a startup. Or in survival mode. Businesses do pull through when
    money has a dry spell.
    |> already been done.
    | Give links to the available equipment, the additional material costs,
    | labor, and costs for rent for the floor space for the additional
    | equipment, the extra air conditioning costs, preventative maintences
    | costs, stocking spare parts for the custom equipment, documenting the
    | project, and estimated service life before it needs a major overhaul, or
    | complete replacement. Then compare that to the battery costs for a
    | decent genset & switch plus fuel. Then figure out what would happen if
    | you needed to increase the capacity, say another 20% because the new
    | servers needed it. You never want to design a system too close to the
    | limits, like I have pointed out before. A proper de-reating is needed.
    | If you do get extended time for the servers, what happens when they
    | overheat because there is no AC?
    I'm suggesting that it be designed, not suggesting that it already exists.
    | If it is custom engineered and can affect employee safety, someone is
    | liable if it has a catastrophic failure.
    And?
    |> |> hobbyist.
    |> | while in storage.
    |> done a design.
    | I have doe it before, and it never made sense. I don't have the
    | numbers in front of me to do a full design, but you should, even before
    | considering a custom system.
    So you have had a NEED to make a UPS like I suggested?
    |> |> Rush.
    | Funny. I heard that, and more about you.
    Maybe my suggestion is a dumb one. But you've not yet given a sane
    argument why it would be. Your posting style is more along the lines of
    giving dumb answer and making insults without details. I'll continue to
    think outside the box and come up with ideas. There will be dumb ones.
    Those are supposed to be shot down on merit, or just ignored. Your
    past reactions have been some combination of insult and ignore. You're
    not useful.
    | So have you, but you seem to always omit any details needed to help
    | you.
    Where the details would be relevant, I'll provide them.
    | You still haven't given anything useful, other than your usual wish
    | list. No good design starts with a dart board or 'magic 8 ball'.
    | Solid, reasonable specifications are always the first step. Without
    | those, it is a complete waste of time.
    Yes, I do toss out wish list items. Now you're recognizing that. And
    of course some will be usless in the market and others impractical to
    make. You seem to have a lack of ability to properly recognize either
    reason.
  15. Guest
    | Don't hold your breath.
    | Then do it.
    That's for the product integrator to do.
    | Reducing the current during a brownout? Right. Where did I mention
    | recharging during a brownout?
    I didn't say reduce it. I said limit it. That is, do not let it rise
    above the maximum current that can be handled safely for either the
    device or the supply circuit that feeds it. This would be a POWER
    reduction. As for the charging, I'm explaining to you that UPS battery
    charging is just a small portion of the current drawn. A rapid bettery
    charge would draw a lot of current. UPS batteries are not generally
    intended for rapid recharging, anyway.
    | Sigh. Read it again, in context. You can't get something for
    | nothing, TANSTAAFL, COE. They all mean that you can't add current to
    | the input of the output inverter if you limit it to a useless level.
    | With your wide range line input concept, as the line voltage goes down
    | the current has to go up to provide the same VA. If you limit the
    | additional VA, you gain nothing. If you do provide enough to help, the
    | I/R losses will be higher, you will put a lot more stress on the input
    | stage of the power supply, as well as the switching transistors. You
    | can have Fast, Cheap, or Efficient. Pick any two.
    The same VA from the DC-AC inverter would draw part from the battery and
    part from the AC-DC converter. The AC-DC converter would NOT be
    providing the same VA as if it were supplying all the power the load
    needs.
    The rest of that paragraph is irrelevant since it assumes facts not true.
    | How do you plan to maintain the voltage, when you limit the current?
    | (Think: Ohm's law)
    The DC-AC inverter is operating from a constant voltage from the battery
    and the AC-DC power supply. The power supply can produce a constant DC
    voltage out over a wide range of AC input voltages.
    | Really? Then you are either in a bad location, or there has been a
    | disaster and trying to squeeze a few more minutes out of the batteries
    | isn't going to help in either situation.
    All the brownout scenerios I have experienced were from common storm
    damage. Power companies are often slow to respond to this kind of
    damage because each incident is not particularly expected on a long term
    basis, as compared to something like a Hurricane. People have to come
    in to work, get prepared, load up trucks, and head out to known problem
    locations. In the case of transmission line voltage work, this could
    involve significant travel distance and time.
    | No. Look at the specifications and see for yourself. The efficiency
    | peaks around the two designated line voltages, and slopes down on either
    | side.
    Many do have dips in the middle, but they are not severe. Most have a
    higher peak at the 240 volt level than at the 120 volt level. Computers
    do work in places like Afghanistan where the "voltage of the day" is a
    crap-shoot between 160 and 210 volts.
    | It was your claim that you needed to add a regulator to
    | specifications, so its up to you to prove me wrong.
    You are the one that wanted a commercially available genset design.
    | How long is a string? Could you be a little bit more vague? What
    | kind of tech? What budget? How high in the company is he or she? Are
    | there company guidelines setting time limits or material cost? How old
    | is the equipment? How critical is it? Is it company owned, or your
    | customer's property? Is it under warranty or a service contract? Can
    | it be replaced for a reasonable multiple of the repair costs? Can a
    | replacement be found in time? Is it worth the cost to repair, or so
    | unreliable that it is N.E.R.?
    You seemed to explain the CFO and engineer roles in some single words.
    I was expecting something equally simple (e.g. one word) for techs.
    Since you are one, I'd think you'd know.
    | If a startup can't afford the equipment it needs, its chances of
    | survival are almost zero. The same goes for survival mode. If a
    | company finds itself in that mode without being ready, it should die.
    | Businesses can and do survive a dry spell, as long as they are well run
    | and can pay their bills on time.
    There are boundary conditions even in business. Have a look at the top
    20 big banks in the USA right now. There are banks where some infusion
    of cash can make the difference. The only reason we would give them any
    is because them failing would drag everything else down with them like
    radiating dominoes.
    | Anything can be 'designed'. Rube Goldberg is proof of that.
    Fine. Maybe someone will do it.
    |> And?
    | Liability. Look it up. See what the insurance costs are. See if
    | the building and zoning department will let you play Frankenstein in a
    | location not designated heavy industry, or if they will knowingly
    | respond to a fire or explosion at your location because you use non
    | approved equipment. Did you ever wonder why paper mills, and some other
    | industries not only have sprinkler systems, but a trained crew and a
    | fire truck?
    So you are saying custom engineering has no place in commerce?
    | No, anyone who doesn't agree 100% with you is not useful to you.
    There have been others that don't agree with me, and even find something
    I said that was wrong, and simply pointed it out. They pointed at the
    specific point of disagreement or error, instead of just making a
    personal attack.
    | No, I've seen it from the beginning, but you don't pay attention to
    | what people tell you. Blue sky is pretty to look at, but useless in
    You just get upset when people don't agree with you, and you call it not
    paying attention. I'm quite open minded. But it takes real information
    to change my mind. Personal attacks don't achieve that.
    |> reason.
    | Right. I can take a look at an idea and make a good decision on
    | whether it is practical with current technology. You post vague ideas,
    | then get upset when people don't offer you millions for your brilliance.
    No. I get upset when someone makes a personal attack, or makes an
    assumption in error about what I said.
    | You should go over to and debate electric cars and
    | spiral plowing farms with tethered electric powered farm tractors with
    | Bret Cahil. All of his ideas are blue sky, so you two have a lot in
    | common.
    No way. I'm keeping my perpetual motion machine all to myself!