I helped a friend upgrade an extremely modest cabin system, and while
I was at it, threw in a refurbished Samlex 600W isolated output MSW
inverter to replace a non-isolated Statpower 250W.
The inverter primarily runs a string of four CFL's. One bulb is OK,
but when a second bulb is turned on, the additional (non-linear,
highly capacitive of course) load is seen by the Samlex as an
overload. It limits the current, tries again, limits the current,
tries again et cetera ad infinitum. Net result is a very lousy strobe
effect.
Not surprisingly, throwing a single incandescent bulb (or just about
any other load) into the mix swamps the effect of the ugly CF bulb
loads and we can turn 'em all on no problems.
We could simply switch back to the other inverter but the idea was
that I wanted my friend to have enough inverter juice to run a few
small kitchen appliances. Annoying to put in a larger inverter only to
have a problem running 26W of light.
I'm looking for a cheap and simple fudge that does not compromise
safety or use significantly more power.
As in the past, Samlex was very helpful and forthcoming with my
original inquiry, though all they've done so far is confirm my
suspicions. I'm awaiting a response to this follow-up question that I
thought I'd post here as well:
Mightn't we resolve this with a little series inductance, and if so,
what would a good experimental value be? I don't have the junk
collection that I used to, so I'd probably have to order something. I
might have something with a PI RFI filter on the AC input...
BTW, the bulbs in use at present are 13W Sylvanias. We're going to go
over their next time with a bunch of our no-name generic brand CFL's
to see if we get lucky with a different ballast design. This is very
much "on the edge" e.g. just the manufacturing variables between the
different Sylvanias is enough to cause inverter cycling or not
depending on the order you turn them on.
(Wiring's good BTW.)
-=s
I was at it, threw in a refurbished Samlex 600W isolated output MSW
inverter to replace a non-isolated Statpower 250W.
The inverter primarily runs a string of four CFL's. One bulb is OK,
but when a second bulb is turned on, the additional (non-linear,
highly capacitive of course) load is seen by the Samlex as an
overload. It limits the current, tries again, limits the current,
tries again et cetera ad infinitum. Net result is a very lousy strobe
effect.
Not surprisingly, throwing a single incandescent bulb (or just about
any other load) into the mix swamps the effect of the ugly CF bulb
loads and we can turn 'em all on no problems.
We could simply switch back to the other inverter but the idea was
that I wanted my friend to have enough inverter juice to run a few
small kitchen appliances. Annoying to put in a larger inverter only to
have a problem running 26W of light.
I'm looking for a cheap and simple fudge that does not compromise
safety or use significantly more power.
As in the past, Samlex was very helpful and forthcoming with my
original inquiry, though all they've done so far is confirm my
suspicions. I'm awaiting a response to this follow-up question that I
thought I'd post here as well:
Mightn't we resolve this with a little series inductance, and if so,
what would a good experimental value be? I don't have the junk
collection that I used to, so I'd probably have to order something. I
might have something with a PI RFI filter on the AC input...
BTW, the bulbs in use at present are 13W Sylvanias. We're going to go
over their next time with a bunch of our no-name generic brand CFL's
to see if we get lucky with a different ballast design. This is very
much "on the edge" e.g. just the manufacturing variables between the
different Sylvanias is enough to cause inverter cycling or not
depending on the order you turn them on.
(Wiring's good BTW.)
-=s