    hello,
    i had a merlin gerin 5 kva 31 series model ups for 3 phase to 1 phase.
    the arrangement from company manual said that the optional isolation
    transformer shall be at output side of ups it means a single phase 1:1
    ratio xformer at ups output but by some ignorance i had a design as a
    3:3 phase isolation Xformer at UPS input. The fuses inside ups are
    10amp per phase and the battery is connected externally to have greater

    back up times and charged by external charger which takes three phase
    input from primary of isolation Xformer.
    Odd enough!


    the transfomrer burnt and this has to be investigated. the indications
    on ups diagnostics were
    unit was on static bypass
    units mains fuses were blown (we found r and b phase fuses were blown)
    units internal charger orand rectifier is/are damaged(internal charger
    was disabled i dont know how but internal ups battery and charger can
    support up to 8 mins so were disconneced by local supplier and this
    external battery with charger were added, battery was 60 amps each
    total 180 volts etc 12 * 15 may be)
    my Ac input is 440 volts delta and 230 volts in phase Neutral 50 hz.
    isolation Xformer is delta to star.
    the meger test showed insulation failure in Y phase for the Xformer
    primary and secondary.
    Dhananjay
     
  2. Art

    Art Guest

    Overload or a very nasty switching spike? Post your total diagnostics and
    required repair component information. Rather interesting.
     
  3. NSM

    NSM Guest

    Too many volts. Too many amps. Too few cycles. DC running through windings.
    Those are the reasons to look for.

    N
     
  4. Guest

    one more observation, the UPs systems do not take neutral etc and the
    three phsaes when have a fuse blown in any phase shall see a overload
    for other two and the protection device shall trip etc in my acse this
    did not happen and the two phases had a fused line still third y phase
    could take current so much as to make the transformer burn etc so it
    looks that it found path through neutral to complete the circuit etc
    the neutral if i do not use the ups shouldnt have taken current from y
    phase is it so?

    D
     
  5. DaveM

    DaveM Guest

    Dammmm what a run-on sentence!!! I'm not trying to be a grammar cop
    here, but that conglomeration of words made my eyes hurt while trying to
    piece together what you're trying to say.
    Please try again, but use a modicum of punctuation. You'll likely get more
    meaningful answers to your question (whatever it was).

    --
    Dave M
    MasonDG44 at comcast dot net (Just subsitute the appropriate characters in
    the address)

    Never take a laxative and a sleeping pill at the same time!!
     
Ask a Question
Want to reply to this thread or ask your own question?
You'll need to choose a username for the site, which only take a couple of moments (here). After that, you can post your question and our members will help you out.
Electronics Point Logo
Continue to site
Quote of the day

-