    I just took out a dead Panasonic lead acid battery form my UPS and
    trying to understand the specifications written on it

    Voltage Regulation
    Cycle use : 14.5 - 14.9V
    Initial current : less than 2.8A
    Standby use : 13.6 - 13.8V

    Will anybody please explain it?

    TIA
     
  2. Lord Garth

    Lord Garth Guest

    When you charge the battery, limit the applied voltage to between 14.5 and
    14.9 volts DC
    and limit the current to no more than 2.8 Amperes. As the battery charges,
    the current will fall.
    If you wish to 'top off' the battery or trickle charge it, keep the applied
    voltage between
    13.6 and 13.8 volts DC.

    Beware that hydrogen gas forms during charging so vent the area.
     
  3. John Fields

    John Fields Guest

    ---
    How about Panasonic?

    First, go to:

    http://www.panasonic.com/industrial/battery/oem/chem/seal/index.html


    and then click on:

    VRLA Charge Methods
     
  4. Jack// ani

    Jack// ani Guest

    Thanks Lord. BTW this battery is sealed form every where( as I can
    see), so where does the Hydrogen escapes??
     
  5. Byron A Jeff

    Byron A Jeff Guest

    That's a bit high for standard gel cels. They usually want 14.4V.
    Correct. A fully depleated battery can draw a lot of current if you allow
    it to.
    Correct. The basic 3 stage charging algorithm for lead acid batteries are:

    1) Bulk charge with highest allowable voltage and current until battery
    reaches 2.4V/cell (14.4V for a 12V battery).

    2) You then fix the voltage to 14.4V and start watching the current. Continue
    in this phase until the current draw drops to C/100, where C is the Amp-Hour
    capacity of the batter. So for example with my 33 AHr battery, C/100 would be
    330 mA.

    3) Then go into float/trickle/top off voltage discussed below.
    This voltage is safe indefinitely without venting.

    If a sealed lead acid gel cell is venting, then you have big problems.
    It's one of the reasons why the specifications listed on the battery are
    in place.

    BAJ
     
  6. Lord Garth

    Lord Garth Guest

    There is likely a hidden vent that opens if the pressure gets too high.
    If that happens, I'd guess the electrolyte would either leak or evaporate.
    That's pretty standard for a *sealed* battery.
     
  7. Jack// ani

    Jack// ani Guest

    Thaks all. A little doubt left..... is there any relation between
    maximum charging current and ampere-hour rating of the battery?

    Like maximum charging current above was 40% of the AH rating!

    Thanks again
     
  8. Depends on the battery. For most flooded lead-acid batteries, a
    maximum charge rate of 1/5 of the AH rating is generally suggested.
    Some gel and AGM batteries can be charged at higher rates.
     