Beachcooler said:
You're right, to a point. According to ICP data, HSPF is based on
operation in frost, 80% occluded coil surface with temp of 30 degrees and
50% RH for 10 minutes. There is no mention of the defrost cycle though.
http://a257.g.akamaitech.net/7/257/...s.gpo.gov/cfr_2004/janqtr/pdf/10cfr430.27.pdf
Scrolling down to the 87th page in the pdf (reads 212 at the bottom of the
page though), 3.2.1.3 'Frost Accumulation test conditions'. This is the
section describing the testing required for air source heat pumps in order
to calculate their HSPF.
"....The Frost Accumulation Test requires that the unit undergo a defrost
prior to the actual test. The test then begins at defrost termination and
ends at the next defrost termination.. Defrost termination occurs when the
controls normally installed within the unit are actuated to cause it to
change defrost operation to normal heating operation. ..."
So the test explicitly *includes* the defrost cycle. Section 5.2 then goes
into detail of how the heating for a defrost cycle is converted to a heating
capacity. The calculation of Q(T) for 17 < T < 45 uses the heating capacity
from the 'Frost Accumulation Test'. So obviously, it depends on which
climate region you're calculating the HSPF for, but it does seem to have the
defrost part of the cycle in there.
There is some good information in this appendix as well. For example, later
in section 6.2, there is a chart of HLH (Heating Load Hours). It's kind of
interesting to note that although the Pacific Northwest is in zone VI and
has 2750 HLH, and the upper midwest as well as NY and parts of New England
have only 2250 HLH. *BUT* the temperature profile for the Northwest is
almost all above 30 F, while region IV and V have a significant portion of
temperatures much colder. So a heat pump that works well in Oregon with
2750 HLH would probably perform very poorly in parts of NY and PA.
daestrom