Maker Pro
Maker Pro

advice powering a LED installation

camilozk

Apr 20, 2014
122
Joined
Apr 20, 2014
Messages
122
Hi!

I need to power a led installation.

3298 leds * 60ma = 200A // 12v // 2400W

I have 4x 12V 60A power supplies for this. (see photo)

There are 13 different led strips lines, with different amount of led's per line. The idea is to connect them to each power supply so that the power requirement is distributed as even as possible.

Do you have some feedback on this?
Should I add a switch-on current limiter? in which case, how do I calculate which one to use?

thank in advance for the feedback!

141448745_532069731086054_6624031774150332703_n-jpg.50643
 

Attachments

  • 141448745_532069731086054_6624031774150332703_n.jpg
    141448745_532069731086054_6624031774150332703_n.jpg
    451.8 KB · Views: 30
Last edited by a moderator:

Harald Kapp

Moderator
Moderator
Nov 17, 2011
13,700
Joined
Nov 17, 2011
Messages
13,700
Do you have some feedback on this?
You can connect them in any combination as long as each power supply is loaded with max. 60 A or less.
Should I add a switch-on current limiter?
Where would you add this?
  • Not required on the secondary (LED) side as LEDs do not draw an excessive inrush current (quite different from incandescent lamps).
  • On the primary side? If the power supplies are well designed they have an internal inrush current limiter. If not, what do you intend to use as inrush current limiter?
 

camilozk

Apr 20, 2014
122
Joined
Apr 20, 2014
Messages
122
  • On the primary side? If the power supplies are well designed they have an internal inrush current limiter. If not, what do you intend to use as inrush current limiter?

The thing is that I already connected this system to a regular 220V 16A (EU) socket, and the circuit breaker tripped. That is the reason I though somehow add a current limiter to the system
 

Harald Kapp

Moderator
Moderator
Nov 17, 2011
13,700
Joined
Nov 17, 2011
Messages
13,700
Turn the power supplies on one after another. This will limit inrush current.
 

camilozk

Apr 20, 2014
122
Joined
Apr 20, 2014
Messages
122
Turn the power supplies on one after another. This will limit inrush current.

got that, but the system should be plug and play, so I will not manually turn them on one after the other. Then I would have to add some kind of component that does this for me. Doesnt it then make sense to simply add the current limiter?
 

Harald Kapp

Moderator
Moderator
Nov 17, 2011
13,700
Joined
Nov 17, 2011
Messages
13,700
Doesnt it then make sense to simply add the current limiter?
Again, what do you want to use as current limiter?
There is a risk that with limited current the power supplies won't start up properly.
Look up mains power sequencer: your problem seems to so ubiquitous in large event setups that such sequencers are offered by many vendors.
 

Harald Kapp

Moderator
Moderator
Nov 17, 2011
13,700
Joined
Nov 17, 2011
Messages
13,700
Max load 200 VA. Not suitable for your 2.4 kW setup.
Even with one limiter for each power supply it needs to be rated for > 750 VA (assuming an efficiency of 80 %& for the power supply).
 
Top