    Wondering if theres anyone out there who could pass on a little knowledge to
    a 128 newbie?

    System is a 128bp. 2 -6160 kp, 1-6150rf with panic fob, 1 symhony kp. 1
    zone expander

    1-getting a fault 801. I belive this 8XX is a keypad error, but theyre all
    correctly addressed.

    2-cant seem to adderess the rf keypad.

    Any ideas?
     
  2. Mark Leuck

    Mark Leuck Guest

    801 would be a fault on an ECP supervised zone, whatever you have set as
    address 01 is causing the problem
     
  3. if you do not have a device set for 01 then you must disable zone 801 in
    zone programming.

    --