Ademco 128bp misc issues

J

John

Jan 1, 1970
0
Hi

Wondering if theres anyone out there who could pass on a little knowledge to
a 128 newbie?

System is a 128bp. 2 -6160 kp, 1-6150rf with panic fob, 1 symhony kp. 1
zone expander

1-getting a fault 801. I belive this 8XX is a keypad error, but theyre all
correctly addressed.

2-cant seem to adderess the rf keypad.

Any ideas?
 
M

Mark Leuck

Jan 1, 1970
0
John said:
Hi

Wondering if theres anyone out there who could pass on a little knowledge to
a 128 newbie?

System is a 128bp. 2 -6160 kp, 1-6150rf with panic fob, 1 symhony kp. 1
zone expander

1-getting a fault 801. I belive this 8XX is a keypad error, but theyre all
correctly addressed.

2-cant seem to adderess the rf keypad.

Any ideas?

801 would be a fault on an ECP supervised zone, whatever you have set as
address 01 is causing the problem
 
N

Nick Markowitz

Jan 1, 1970
0
if you do not have a device set for 01 then you must disable zone 801 in
zone programming.

--
Nick Markowitz Jr.
Owner
Markowitz Electic Protection
Private Industry Fire Investigator.
Qualified Electrical- Fire Alarm Contractor
Registered EPA Freon Recovery

Contributing Editor Pa. Firemans Magazine
Staff Editor www.securitymission.com
Senior Correspondant www.1strespondernews.com
Exclusive Correspondant www.nbfd.us
Contract Broadcast Engineer WAVL 910 AM apollo Pa.

"To error is human to realy foul things up requires a computer"

Irish Diplomacy

The ability to tell a man to go to hell and he tells you how much he is
going to enjoy the trip.
 