A couple circuit breaker questions

J

John

Jan 1, 1970
0
1) I know you can only put two wires in a breaker that is designed for it;
but do they say they can hold two, or do they say they can only hold one;
which way does it work? If it can hold only one, I can just still use
two circuits in one breaker with a jumper, can't I? (I have two outdoor
outlets on their own circuits. One has never been used, and the other just
has some low voltage lighting on it and a few christmas lights in season.
Since I need some space in the panel, it seems reasonable to consolidate
them. If I can't use the jumper, I guess I will just abandon the unused
outlet; but that seems wrong somehow.)

2) Do GFCI breakers require power before you can set them on, like GFCI
outlets? I have a circuit that is flaky, and everything but the GFCI
breaker seems okay. When I swapped the breaker with a spare, it is okay, so
I figure it must be the breaker. It will stay in the on position when
disconnected; does that mean it is bad? The spare is 20a, and it should be
15a, so I need to buy a new one if the old 15a is broken. (I figure the
chances of a 20a breaker being a fire hazzard on a lightly used #14 circuit
for a few days is extremely small, no?)

Thanks.
 
J

jim

Jan 1, 1970
0
John said:
1) I know you can only put two wires in a breaker that is designed for it;
but do they say they can hold two, or do they say they can only hold one;
which way does it work? If it can hold only one, I can just still use
two circuits in one breaker with a jumper, can't I? (I have two outdoor
outlets on their own circuits. One has never been used, and the other
just has some low voltage lighting on it and a few christmas lights in
season. Since I need some space in the panel, it seems reasonable to
consolidate
them. If I can't use the jumper, I guess I will just abandon the unused
outlet; but that seems wrong somehow.)
The only issue with putting more than one wire (or a very large wire) into a
breaker is it will affect the trip time. The wire acts as a heat sink.
The bigger the wire, the slower the breaker.
Putting two #12 wires in a 20 amp breaker or 2 #14 in a 15 amp is not a
problem. It may be against some local codes.
Jumpering the one wire from the breaker to two circuits is not a big deal
either. This would probably violate code though. The wiring areas for
panels are not sized considering their use as a junction box, but one
splice isn't going to hurt. If you make the splice outside the panel,
there is no violation (unless of course you overload the circuit, but it
doesn't seem likely from your description.
 
J

John

Jan 1, 1970
0
The only issue with putting more than one wire (or a very large wire) into a
breaker is it will affect the trip time. The wire acts as a heat sink.
The bigger the wire, the slower the breaker.
Putting two #12 wires in a 20 amp breaker or 2 #14 in a 15 amp is not a
problem. It may be against some local codes.

I thought it had to do with making contact with two wires at once rather
than with just once.

The breaker in question, a 20a GFCI, says it can accept #8 wire, so it
shouldn't have any heat problems with 2 #12s.
Thank you.
 
D

daestrom

Jan 1, 1970
0
2) Do GFCI breakers require power before you can set them on, like GFCI
outlets? I have a circuit that is flaky, and everything but the GFCI
breaker seems okay. When I swapped the breaker with a spare, it is okay, so
I figure it must be the breaker. It will stay in the on position when
disconnected; does that mean it is bad? The spare is 20a, and it should be
15a, so I need to buy a new one if the old 15a is broken. (I figure the
chances of a 20a breaker being a fire hazzard on a lightly used #14 circuit
for a few days is extremely small, no?)

Of the GFCI's I've seen, they mechanically latch/reset. So you can reset
them with them in your hand (no power). If it won't reset in your hand, it
is definitely bad.

They need power to trip/test, so it must be installed to 'test' the GFCI
tripping. If you install it in the panel (and the 'pigtail' to the neutral
bus), but leave the circuit 'hot' and 'neutral' wires off, it should not
trip. If it keeps tripping then (with no downstream circuit connected), it
must be bad. If it stays 'on' under those conditions, connect the circuit
'hot' and 'neutral'. If it keeps tripping and won't stay reset then (with
circuit connected), you may have a ground on the circuit.

Some GFCI's will trip if the neutral is grounded downstream, others will
not. Some have a 'signal generator' that puts a minute signal on the
neutral (and hot) and looks for current flow downstream side of neutral,
return through Equipment Grounding Conductor (EGC) back to neutral bus.
Others (older??) don't have this feature.

So before you scrap it, be sure your circuit's neutral isn't connected to
ground somewhere besides through the GFCI.

daestrom
 
J

John

Jan 1, 1970
0
So before you scrap it, be sure your circuit's neutral isn't connected to
ground somewhere besides through the GFCI.
I have replace it with a plain breaker and a GFCI breaker. Haven't had a
nuisance trip in 3 days; however, maybe the old one looked for a the the
neutral to ground connection and the new one doesn't. I will put it in
another circuit to see if it fails there also.
Thanks.
 