4-20mA to ohms coverter

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
Hi everyone, im after some help with integrating a PT100 sensor into my alarm panel (its a pretty smart alarm panel, just not quite smart enough to take a 4-20mA reading and convert it to temperature)

Basically I have a PT100 probe, and a 4-20mA converter for it, what I need to do is accurately convert the 4-20mA signal back to a known resistance change so the alarm panel can read it, preferably with the following increments (these resistances are what the panel recognises as the temperature)

10C - .229vdc - 99ohms
14C - .310vdc - 131.4ohms
18C - .399vdc - 170ohms
22C - .489vdc - 210ohms
24C - .523vdc - 226.9ohms
27C - .579vdc - 254ohms
30C - .653vdc - 287.5ohm
33C - .704vdc - 313.2ohm
36C - .755vdc - 338ohm
38C - .806vdc - 363.6ohm

This is the probe, and the transmitter -
http://www.kiatronics.com/temperature-sensor/temperature-probe-pt100-stainless-steel.html
http://www.kiatronics.com/temperature-sensor/temperature-sensor-4-20ma-transmitter-code-70692.html


Thank you all for any help & ideas you might have.

Cheers

Shey
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
I get most of that apart from the panel recognises the resistance. How is your panel measuring these resistances or does it just see the voltage as an input? Does the convertor put out 160uA per degrees centigrade rise in temperature?
Adam
 

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
I get most of that apart from the panel recognises the resistance. How is your panel measuring these resistances or does it just see the voltage as an input? Does the convertor put out 160uA per degrees centigrade rise in temperature?
Adam

Thanks for your reply Adam,

The alarm panel works purely by measuring resistance, the inputs dont measure the analog measurements like4-20mA or as far as im aware the voltage, to get the measurements I listed i literally sat there with a variable resistor and watched the temperature rise / fall. - Im not sure if this answers your question or not..

I cant find much information on the device, however I am more than happy to measure it for you, ive found some similar products that give all sorts of specifications, but dont appear to have a amperage vs degrees measurement, heres the sheets I was looking at, is there anything helpful you can see?

http://www.wika.co.nz/upload/US_DS_TE2401_en_us_18902.pdf

Thanks again for your help :)

Shey
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
So what are you doing? Connecting the resistor across the transmitter and then measuring the voltage? For something to know the resistance value of a resistor either the voltage or current to it must be fixed. And then either the voltage or current is measured to work out the resistor value. Do you have any diagrams of your setup?
Adam
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
The easiest option for standard 4-20 loop current measurement is to use a 250R resistor which will give you a range of 1-5 Volts. So each degree rise would be an extra 50 mV. I don't understand why your voltages are so precise at whole values of temperature.
Adam
 

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
So what are you doing? Connecting the resistor across the transmitter and then measuring the voltage? For something to know the resistance value of a resistor either the voltage or current to it must be fixed. And then either the voltage or current is measured to work out the resistor value. Do you have any diagrams of your setup?
Adam

Ok, so at the moment I have no way of connecting the PT100 & transmitter to the panel, if I feed the current through the two terminals, the panel doesnt understand, all it wants to see is that change of resistance (and therefore i guess a change of voltage as the resistance changes) - so what I need is something that I connect the 4-20mA loop into, then it outputs a change of resistance as per the list. I can draw up a diagram for you soon :)
 

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
The easiest option for standard 4-20 loop current measurement is to use a 250R resistor which will give you a range of 1-5 Volts. So each degree rise would be an extra 50 mV. I don't understand why your voltages are so precise at whole values of temperature.
Adam

The reason is that the alarm panel has various templates for interpreting the signal it recieves, the one im working with needs those resistances / voltages to read the temperature, to get those measurements I literally sat there with a multimeter and measured the voltage across the variable resistor, and then disconnected the vr from the panel to read its ohms value.
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
Can you change the input levels to measure different voltages like 1 to 5 volts or are you fixed at the voltages in your first post.
 

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
Can you change the input levels to measure different voltages like 1 to 5 volts or are you fixed at the voltages in your first post.
I just tried wiring it to take a 1-5V measurement, it ended up thinking I was trying to arm the house. Go figure. Turns out I need to supply it the voltage/resistance as above to get it to read my temp :(
 

Shey Malcolm

Jul 19, 2014
6
Joined
Jul 19, 2014
Messages
6
Not sure if this clarifies anything, other than the magical device i see fixing the issue
 

Attachments

  • image.jpg
    image.jpg
    119.2 KB · Views: 130

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
I am struggling to work out a simple solution for you and unless the other guys can come up with something this is going to need some more thought. The only thing I can think of is a circuit to sequentially switch in the different resistors. So are you looking for only those temps shown and those voltage values? Do you just ignore anything else.
Adam
 

Sinewave

Feb 15, 2013
129
Joined
Feb 15, 2013
Messages
129
You can buy those converters, they're not cheap though. I may even have some spare.
 

Laplace

Apr 4, 2010
1,252
Joined
Apr 4, 2010
Messages
1,252
Screenshot-23.png
Here I extended the table of measured resistance values with the calculated current for each temperature point. It appears that the panel measures the sensor resistance by using a constant current source of 2.3 mA. Also included the standard PTC100 sensor resistance for the temperatures to be measured. Note the wide variation of the resistance expected by the panel, whereas the the PTC sensor (which operates to 450˚C has a very small variation in resistance over the temperature range of interest. It would seem that the panel expects direct connection of a particular type of thermistor and the PTC100 is the wrong sensor to use. Using the PTC100 sensor over a narrow temperature range will cause any errors to be magnified, and using a current converter which will need a current to resistance conversion will be a fertile source of signal errors. Is there any way to use the proper thermistor instead?
 

Arouse1973

Adam
Dec 18, 2013
5,178
Joined
Dec 18, 2013
Messages
5,178
Nice one Laplace.
Could the OP at least supply details of the panel and any instruction he has so at least we can get a better understanding.