    In lieu of a 3 phase mains feed, can 3 independent single phase feeds
    be applied to a 3 phase transformer?

    In this scenerio, there would be no power overlap as in conventional 3
    phase. All three phases would rise and fall, in unison, in phase with
    each other. The unit is a rated 575 volt 3 phase welder with plasma
    cutter.

    My question is, can the single phase feeds be applied in this manner
    without dire effect.
     
  2. Chris

    Chris Guest

    Hi, Randy. Not a very good idea, for many reasons. Not safe. Don't
    go there.

    Chris
     
  3. Randy Gross

    Randy Gross Guest



    I was asked this question by a curious owner. I don't know but, to
    reduce temptation, I think a solid answer is needed.

    rg
     
  4. There are parts of the core that bridge between the sections (legs)
    that have coils on them that carry flux from more than 1 coil. When
    the coils are excited with 3 phase, the coils, in effect, take turns
    using that bridging part of the core.

    If two coils are energized at the same time, there are two
    possibilities. Either their fields around the loop through those two
    legs adds, so that that loop has twice the rated peak flux, or they
    buck each other, putting twice the normal flux over through the third
    leg. In either case, at least you get the same volts per turn and
    (with voltage derating for the saturation taking place at least
    somewhere at half the rated volts per turn) it still acts like a
    transformer. This assumes that you can get to all the coil ends and
    wire then either in series or parallel, not delta or Y like they were
    connected for 3 phase.

    With 3 coils energized, simultaneously, either they all create field
    in the same direction so that there is no return path for all that
    flux, or two fields are in one direction and the third is in the other
    direction, so that the odd leg still has twice the flux of the other
    two. Since volts per turn are proportional to the peak to peak flux
    (for a given frequency) you either get twice the volts per turn on the
    odd leg, the same volts per turn on each coil, but no closed path, so
    very low inductance and very high magnetizing current and lots of
    fringing fields. I'll leave the first case as an exercise how you
    series parallel connect the coils to get some kind of transformer.
    The second case is just a low impedance reactor across the line.

    Is this what you were trying to picture?
     
  5. Randy Gross

    Randy Gross Guest



    This is exactly what I was looking for. I have never ran across anyone
    who has attempted to run an industrial welder from a residential
    service. The owner of the unit wanted to connect 220 across two of the
    windings, I stalled this attempt. Another vision that popped into my
    head was his walls bursting into flames the moment he flipped the
    switch. I have to admit that the question had me curious but, measure
    twice, cut once.

    I'll pass this information on, ver batum.

    Thanks John,

    rg
     