I have posted to my web site a document describing a novel thermal
scheme for a solar heated house for a cold climate.
Drawings, graphs, and calculations may be seen at the web site. Text
below.
See
<http://geocities.com/davidmdelaney/thermal-cs/thermal-crawl-space-1.html>
I would be grateful for comments.
David Delaney, Ottawa
Start of text from web document
Thermosyphon solar air heater and overhead thermal crawl space for
100% solar heating
David Delaney [email protected] Ottawa, November 2004
keywords: solar air heater, thermosyphon, natural convection, flow
organiser, flow organizer, thermal crawl space, thermal closet, heat
store, passive solar, solar fraction, solar thermal energy, bed of
stones, bin of stones, rock bed, damper
A house in Ottawa, Ontario (45.3N, 75.6W, continental climate) can get
100% of its winter space heat from a solar air heater that operates by
natural convection to charge a heat store in an overhead thermal crawl
space. The house uses common materials, simple components, simple
control, and simple building techniques, but needs a stronger
structure than an ordinary house to support the weight of the
overhead thermal mass. There are no dampers requiring daily operation.
The only parts that move every day are the blades of a conventional
ceiling fan.
The heavily insulated thermal crawl space, lies above the living
space, and extends above a thermosyphon solar air heater that forms
the south facade of the house. When the sun shines, heating the air
heater, air moves by natural convection from the air heater to the
thermal crawl space and back. When the sun stops shining, air stops
moving between the air heater and the thermal crawl space, because the
air in the heater is then colder and denser than the air in the
thermal crawl space above it.
The flow organizer (flow organiser) allows the sheet of hot air rising
from the air heater to cross through the sheet of cool air moving
south along the floor of the crawl space. The sheet of cool air
eventually falls through an east-west slit in the floor of the crawl
space, then falls through the air heater against the glazing,
keeping the rising hot air away from the cold glazing.
A massive but relatively thin layer of small smooth river stones
provides heat storage. The stones are from 1-1/2" to 2-1/2" (35 mm
to 65 mm) in diameter. The stone layer is suspended one or two feet
above the floor of the crawl space on a wire mesh. There is a one
foot air space above the stone layer so that hot air from air heater
can spread out above the stones. The stone layer extends above the
whole of the habitable space below. The stones present an enormous
surface area for heat transfer between stone and air. There is very
little resistance to convective vertical flow through the stone bed
because of its very large horizontal cross sectional area. To match
the volume flow rate of air coming up from the air heater, air will
move down through the stones at a volume rate equal to the volume rate
of the air rising from the flow organiser. The rate of descent
through the stones will be the volume rate divided by the effective
duct area of the stones. The effective duct area of the stones will be
approximately the product of the void fraction and the area of the top
of the stone bed. Given that the stone bed extends over the whole of
the living area, the velocity of air descending through the stones
will not exceed about a twentieth of the velocity of the air rising
by natural convection through the flow organiser. As a result,
resistance to the flow through the stone bed should be extremely
small. 100 lb of stone per square foot of ceiling area (490 kg/m2)
is about right to produce the desired thermal capacity. 100 lb/ft2
corresponds to a 1 ft (0.3 m) depth of stone with a 40% void fraction.
The crawl space extends 3 to 4 ft (0.9 to 1.2 m) from its floor to
its ceiling.
A ducted ceiling fan moves hot air from above the stone layer down
into the living space. A conventional 4 ft (1.2 m) diameter ceiling
fan is located in the lower end of a 4.5 (1.4 m ) diameter circular
duct that runs from the ceiling of the living space up through the
crawl space and the stone layer to the top of the stone layer. The
ceiling fan operates at reduced speed, and consumes 50 watts or less
when running. It might be powered by a small area of solar
photovoltaic panel. Control of the temperature of the living space
can be very simple: a thermostat that turns on the fan when the
living space is colder than desired.
A large solar air heater, super insulation, and thermally efficient
windows that are not too large, are required to get all needed space
heat from the sun in Ottawa Ontario. Ottawa has a difficult December,
with 1483 F heating degree days below 64.4F, (824 C heating degree
days below 18 C) (according to NASA). The average December temperature
is 14F (-10C). In December, a total of 2.16 kWh per day of solar
radiation falls on each square meter of a south facing vertical
surface (NASA). Design calculations are currently based on the
assumption that the air heater can transfer 50% of the December
incident solar energy into the thermal crawl space as heat.
Dimensions and suitable R values for a small bungalow in Ottawa,
Ontario: Living space: 40 ft (12.2m) east-west, 30 ft (9.1 m)
north-south, 1200 square feet (112 m2). Insulation: ceiling of crawl
space: R 100 (RSI 17.6); walls of crawl space: R 57 (RSI 10); walls of
living space R 50 (RSI 8.8); underslab: R20 (RSI 3.5). Windows:
window R-value: R 4 (RSI 0.7 ); window area: 120 square feet (11.1
m2). Fresh air: 45 ft3/min (21 l/s) The air heater must have an area
of 430 ft2 (40 m2), which could be achieved with an east-west glazing
40 ft (12.2 m) long and 11 ft (3.4 m) high. These air heater
dimensions are based on the assumption that the air heater can
transfer 50 per cent of the energy of the solar radiation that falls
on the exterior of its glazing into the crawl space. The
calculations to justify these specifications, and to create the graphs
below, may be seen in 100% Solar heated house for Ottawa, Ontario,
with overhead thermal crawl space. (PDF)
AT 430 ft2 (40 m2) the air heater is sufficient for December space
heat, but 30% larger than is needed for either November or January,
the next most demanding months. The surplus heat available in the
less demanding winter months might be used to heat domestic hot water.
The air-water heat exchanger might be placed in the top of the thermal
crawl space directly above the air heater, where it would be
accessible for maintenance and repair.
A stone layer area of 1100 ft2 (102 m2) at 100 lb (45.5 kg) of stone
per square foot provides a thermal capacity of 22,000 Btu/F (11.6
kWh/C). Assume a non solar heat gain of 600 W, of which 200 W is due
to two human bodies. If the temperature of the stones is 100 F (38 C)
and the outdoor temperature is 14 F (-10 C) when the sun ceases to
shine for several days, and the fan is controlled to maintain a
desired temperature of 70 F (21 C), the temperature of the habitable
space will not fall below that desired temperature until after 120
hours of darkness, and will fall to 59.8F after 168 hours of darkness,
and to 39.1 F (4 C) after 20 days of darkness. This calculation is
quite conservative. In Ottawa, a prolonged period of no-sun days is
almost always accompanied by relatively warm weather, say around 32 F
(0 C). When the temperature descends to 14F ( -10 C) , as in this
calculation, or lower, there is almost always some clear sky each day.
The 430 ft2 (40 m2) air heater specified above can maintain the
average temperature of the heat store (the thermal crawl space) at 110
F (43 C) and the habitable space at 70 F (21 C) during an Ottawa
December of infinite duration but typical temperatures and sun. (with
600 W non-solar heat gain).
If the utility electricity fails in a typical December, but there is
PV power to run the fan, the temperature of the habitable space will
not fall below the desired temperature unless there is a long string
of no-sun days. (Assuming a 200 W non-solar heat gain, just the two
human bodies). As the graph to the right shows, the heat store (the
thermal crawl space) even in the absence of dark days, the
temperature falls to equal (a comfortable) habitable space
temperature, making it impossible to maintain this temperature during
multiple dark days. Backup heat might be desired to anticipate
multiple dark days during a prolonged December electrical utility
failure. Backup heat would not be needed for prolonged electrical
failures in other months. A wood or propane cooking stove would
provide sufficient backup heat.
If there is a failure of the fan or of the electricity supply that
drives the fan, a door, a window, or a special opening in the south
wall of the house may be opened during the day, producing the flow
pattern through the house and air heater shown to the right. The air
heater will be less efficient in this configuration, and much of the
benefit of the crawl space thermal mass will be lost, but substantial
solar heat gain will still occur. The thermal mass will still keep
the thermal crawl space hot, providing some heat at night by
radiation to the living space below and eliminating heat loss from
the living space through its ceiling.
End of text from web document
scheme for a solar heated house for a cold climate.
Drawings, graphs, and calculations may be seen at the web site. Text
below.
See
<http://geocities.com/davidmdelaney/thermal-cs/thermal-crawl-space-1.html>
I would be grateful for comments.
David Delaney, Ottawa
Start of text from web document
Thermosyphon solar air heater and overhead thermal crawl space for
100% solar heating
David Delaney [email protected] Ottawa, November 2004
keywords: solar air heater, thermosyphon, natural convection, flow
organiser, flow organizer, thermal crawl space, thermal closet, heat
store, passive solar, solar fraction, solar thermal energy, bed of
stones, bin of stones, rock bed, damper
A house in Ottawa, Ontario (45.3N, 75.6W, continental climate) can get
100% of its winter space heat from a solar air heater that operates by
natural convection to charge a heat store in an overhead thermal crawl
space. The house uses common materials, simple components, simple
control, and simple building techniques, but needs a stronger
structure than an ordinary house to support the weight of the
overhead thermal mass. There are no dampers requiring daily operation.
The only parts that move every day are the blades of a conventional
ceiling fan.
The heavily insulated thermal crawl space, lies above the living
space, and extends above a thermosyphon solar air heater that forms
the south facade of the house. When the sun shines, heating the air
heater, air moves by natural convection from the air heater to the
thermal crawl space and back. When the sun stops shining, air stops
moving between the air heater and the thermal crawl space, because the
air in the heater is then colder and denser than the air in the
thermal crawl space above it.
The flow organizer (flow organiser) allows the sheet of hot air rising
from the air heater to cross through the sheet of cool air moving
south along the floor of the crawl space. The sheet of cool air
eventually falls through an east-west slit in the floor of the crawl
space, then falls through the air heater against the glazing,
keeping the rising hot air away from the cold glazing.
A massive but relatively thin layer of small smooth river stones
provides heat storage. The stones are from 1-1/2" to 2-1/2" (35 mm
to 65 mm) in diameter. The stone layer is suspended one or two feet
above the floor of the crawl space on a wire mesh. There is a one
foot air space above the stone layer so that hot air from air heater
can spread out above the stones. The stone layer extends above the
whole of the habitable space below. The stones present an enormous
surface area for heat transfer between stone and air. There is very
little resistance to convective vertical flow through the stone bed
because of its very large horizontal cross sectional area. To match
the volume flow rate of air coming up from the air heater, air will
move down through the stones at a volume rate equal to the volume rate
of the air rising from the flow organiser. The rate of descent
through the stones will be the volume rate divided by the effective
duct area of the stones. The effective duct area of the stones will be
approximately the product of the void fraction and the area of the top
of the stone bed. Given that the stone bed extends over the whole of
the living area, the velocity of air descending through the stones
will not exceed about a twentieth of the velocity of the air rising
by natural convection through the flow organiser. As a result,
resistance to the flow through the stone bed should be extremely
small. 100 lb of stone per square foot of ceiling area (490 kg/m2)
is about right to produce the desired thermal capacity. 100 lb/ft2
corresponds to a 1 ft (0.3 m) depth of stone with a 40% void fraction.
The crawl space extends 3 to 4 ft (0.9 to 1.2 m) from its floor to
its ceiling.
A ducted ceiling fan moves hot air from above the stone layer down
into the living space. A conventional 4 ft (1.2 m) diameter ceiling
fan is located in the lower end of a 4.5 (1.4 m ) diameter circular
duct that runs from the ceiling of the living space up through the
crawl space and the stone layer to the top of the stone layer. The
ceiling fan operates at reduced speed, and consumes 50 watts or less
when running. It might be powered by a small area of solar
photovoltaic panel. Control of the temperature of the living space
can be very simple: a thermostat that turns on the fan when the
living space is colder than desired.
A large solar air heater, super insulation, and thermally efficient
windows that are not too large, are required to get all needed space
heat from the sun in Ottawa Ontario. Ottawa has a difficult December,
with 1483 F heating degree days below 64.4F, (824 C heating degree
days below 18 C) (according to NASA). The average December temperature
is 14F (-10C). In December, a total of 2.16 kWh per day of solar
radiation falls on each square meter of a south facing vertical
surface (NASA). Design calculations are currently based on the
assumption that the air heater can transfer 50% of the December
incident solar energy into the thermal crawl space as heat.
Dimensions and suitable R values for a small bungalow in Ottawa,
Ontario: Living space: 40 ft (12.2m) east-west, 30 ft (9.1 m)
north-south, 1200 square feet (112 m2). Insulation: ceiling of crawl
space: R 100 (RSI 17.6); walls of crawl space: R 57 (RSI 10); walls of
living space R 50 (RSI 8.8); underslab: R20 (RSI 3.5). Windows:
window R-value: R 4 (RSI 0.7 ); window area: 120 square feet (11.1
m2). Fresh air: 45 ft3/min (21 l/s) The air heater must have an area
of 430 ft2 (40 m2), which could be achieved with an east-west glazing
40 ft (12.2 m) long and 11 ft (3.4 m) high. These air heater
dimensions are based on the assumption that the air heater can
transfer 50 per cent of the energy of the solar radiation that falls
on the exterior of its glazing into the crawl space. The
calculations to justify these specifications, and to create the graphs
below, may be seen in 100% Solar heated house for Ottawa, Ontario,
with overhead thermal crawl space. (PDF)
AT 430 ft2 (40 m2) the air heater is sufficient for December space
heat, but 30% larger than is needed for either November or January,
the next most demanding months. The surplus heat available in the
less demanding winter months might be used to heat domestic hot water.
The air-water heat exchanger might be placed in the top of the thermal
crawl space directly above the air heater, where it would be
accessible for maintenance and repair.
A stone layer area of 1100 ft2 (102 m2) at 100 lb (45.5 kg) of stone
per square foot provides a thermal capacity of 22,000 Btu/F (11.6
kWh/C). Assume a non solar heat gain of 600 W, of which 200 W is due
to two human bodies. If the temperature of the stones is 100 F (38 C)
and the outdoor temperature is 14 F (-10 C) when the sun ceases to
shine for several days, and the fan is controlled to maintain a
desired temperature of 70 F (21 C), the temperature of the habitable
space will not fall below that desired temperature until after 120
hours of darkness, and will fall to 59.8F after 168 hours of darkness,
and to 39.1 F (4 C) after 20 days of darkness. This calculation is
quite conservative. In Ottawa, a prolonged period of no-sun days is
almost always accompanied by relatively warm weather, say around 32 F
(0 C). When the temperature descends to 14F ( -10 C) , as in this
calculation, or lower, there is almost always some clear sky each day.
The 430 ft2 (40 m2) air heater specified above can maintain the
average temperature of the heat store (the thermal crawl space) at 110
F (43 C) and the habitable space at 70 F (21 C) during an Ottawa
December of infinite duration but typical temperatures and sun. (with
600 W non-solar heat gain).
If the utility electricity fails in a typical December, but there is
PV power to run the fan, the temperature of the habitable space will
not fall below the desired temperature unless there is a long string
of no-sun days. (Assuming a 200 W non-solar heat gain, just the two
human bodies). As the graph to the right shows, the heat store (the
thermal crawl space) even in the absence of dark days, the
temperature falls to equal (a comfortable) habitable space
temperature, making it impossible to maintain this temperature during
multiple dark days. Backup heat might be desired to anticipate
multiple dark days during a prolonged December electrical utility
failure. Backup heat would not be needed for prolonged electrical
failures in other months. A wood or propane cooking stove would
provide sufficient backup heat.
If there is a failure of the fan or of the electricity supply that
drives the fan, a door, a window, or a special opening in the south
wall of the house may be opened during the day, producing the flow
pattern through the house and air heater shown to the right. The air
heater will be less efficient in this configuration, and much of the
benefit of the crawl space thermal mass will be lost, but substantial
solar heat gain will still occur. The thermal mass will still keep
the thermal crawl space hot, providing some heat at night by
radiation to the living space below and eliminating heat loss from
the living space through its ceiling.
End of text from web document