Current Transformer to 0-10 Volts
Discussion in 'Electronic Design' started by Tom, Feb 5, 2007.
  1. Tom
    Tom Guest
    I want to take a current measurement of 0 to 20 Amps AC using a
    current transfomer, and then convert the current siginal to input into
    a Analog input of a PLC (programmable logic controller). I know they
    sell current transducers that do this alreay, but I want to make about
    20 of these.
    The PLC will take 0-10V DC, or 4-20mA
    I was thinking about using a 50:5 Current Transformer, and a 5 ohm
    resistor.
    20 Amps ----> 50:5 ----> 2 Amps
    Voltage = 5 * 2 = 10 V
    Am I on the right track or does the current transformer output a
    sinusoidal value.
    Tom, Feb 5, 2007
    #1
    1. Advertisements
  2. "Tom" <> wrote in message
    news:...
    Yes.
    > or does the current transformer output a sinusoidal value.
    Yes.
    Be careful. An open secondary on a CT is a nasty thing. Take no chances -
    ask an expert if you are unsure.
    Homer J Simpson, Feb 5, 2007
    #2
    1. Advertisements
  3. Tom
    scada Guest
    news:...
    > 20 of these.
    > resistor.
    > sinusoidal value.
    The 5 ohm resistor may be to big. You need to match or be less than the CT
    secondary "Burden" rating. Typically that value is less than 1 ohm. The
    voltage developed across that resistance is then amplified by a wide band
    fixed gain amp., thus the signal conditioner. As Homer pointed out, do not
    run the secondary into an open circuit or at high impedance. It will then
    act as a PT possibly creating thousands of volts, doing all kinds of nasty
    things!
    scada, Feb 5, 2007
    #3
  4. Tom
    scada Guest
    "scada" <> wrote in message
    news:OnOxh.274$...
    > news:...
    > > 20 of these.
    > > resistor.
    > > sinusoidal value.
    > things!
    Also keep in mind, the secondary waveform will be the actual current
    waveform, AC. If you need RMS, or DC output you further need to refine that
    in your signal conditioner.
    scada, Feb 5, 2007
    #4
  5. Tom
    john jardine Guest
    news:...
    > 20 of these.
    > resistor.
    > sinusoidal value.
    It's all AC and variable waveshapes must be considered.
    You'll need an additional power supply and some electronics to rectify,
    smooth and amplify the signal to 0-10Vdc.
    E.g. 100:1 CT to a 1ohm resistor, then to an AD737 true RMS converter, then
    to a x50 opamp, then to the PLC.
    john
    Posted via a free Usenet account from http://www.teranews.com
    john jardine, Feb 5, 2007
    #5
  6. Tom
    Rich Grise Guest
    > 20 of these.
    > resistor.
    > sinusoidal value.
    Well, I'm not a CT guy, but I'd think that the output current would
    look a lot like the input current, like in any transformer.
    I'd use a big resistor - 2A at 10V is 20 watts! =:-O
    Good Luck!
    Rich
    Rich Grise, Feb 5, 2007
    #6
  7. Tom
    Tom Bruhns Guest
    > 20 of these.
    > resistor.
    > sinusoidal value.
    Note that 10V at 2A is 20 watts you'll be dissipating in the load
    resistor! I'd suggest that you go to a much higher turns ratio.
    100:1 (500:5) might be reasonable. Then the output is 0.2A. You could
    use an even higher ratio. If the transformers are easy to get, I'd
    look at even 1000:1, though you may have some trouble finding those.
    If you used your original 10:1 ratio, the ten volt drop would reflect
    back as a 1 volt drop in your line, which is way more than you need to
    allow. A ten volt output at 1000:1 reflects only ten millivolts drop
    along the monitored line--actually somewhat more because of less than
    perfect coupling, but still not a lot. A ten volt output at 1000:1 or
    even 100:1 is also much more likely to be a reasonable burden for the
    transformer. At 1000:1, a ten volt output with 20A in the primary is
    20mA secondary current and 200mW dissipation.
    You'll need to rectify the output; an op-amp precision rectifier is
    appropriate. Then you need to convert the output to whatever the PLC
    wants. The precision recitifer can easily be made to put out 0-10
    volts, even if the input is only 1 volt instead of 10, but then you
    need power to run the op amps. If you _know_ that your circuit will
    always have some minimum current in it and the ratio between min and
    max isn't too great, you could probably arrange to run the op amps on
    the current transformer output, but that's not a wonderful idea from
    the standpoint of precision, since the amplifier power will appear as
    additional transformer load. A better idea would be to use the 4-20mA
    loops, especially if these sensors will be some distance from the
    PLC. You can find example 4-20mA circuits in op amp manufacturers'
    data sheets. I believe that Linear Technology is one good source for
    such circuits. Try their ap notes, too.
    Too bad you didn't have this need a year or so ago. Marlin P. Jones
    had some nice split-core 4-20mA AC current transducers with a jumper
    for, um 10A, 20A and 50A full scale as I recall, for about $10 each.
    But even if you have to pay $100 or more each for them, you'll
    probably be better off buying them. I have a feeling from the last
    sentence of your posting that you'll be in trouble trying to build
    them.
    Cheers,
    Tom
    Tom Bruhns, Feb 5, 2007
    #7
  8. Tom
    Tim Dunne Guest
    news:
    > current transfomer,
    > sinusoidal value.
    You need a module from LEM. They're current transformers with built in
    signal conditioners (often self powered) giving a PLC analog compatible
    signal - 0-10, 0-5 or 4-20mA
    http://web4.lem.com/hq/en/component...sk,displayserie/serie,AK ££ AKR/output_type,/
    HTH
    Tim
    Sent from Birmingham, UK... Check out www.nervouscyclist.org
    'I find sometimes it's easy to be myself, but sometimes I find it's
    better to be somebody else.' - Dave Matthews 'So Much To Say'
    My 'reply to' address is valid, mail to the posting address is dumped
    Tim Dunne, Feb 5, 2007
    #8
  9. Tom
    jasen Guest
    > 20 of these.
    > resistor.
    And 20 Watts!
    there's not (m)any CTs with that sort of output. a 20VA 60Hz transformer weighs a
    few kilograms...
    typicaly curent transformers produce milliwatts.
    aim for the sort of current you can feed to an op-amp
    eg: a 1000:1 transformer into a virtual earth or a small resistor.
    then you probably want rectify and average it
    (if you want RMS that'll add complexity)
    > sinusoidal value.
    it sure does.
    Bye.
    Jasen
    jasen, Feb 6, 2007
    #9
  10. "Tom" <> wrote in message
    news:...
    > 20 of these.
    > resistor.
    > sinusoidal value.
    You can get CTs with 100 mA rated output. There are also high ratio PCB
    mounted (or not) CTs with primaries from 10 to 200 amps, and output up to
    10 VRMS. Digikey has them TE1020-ND for $7.80, or you can get a wide range
    of CTs from CR Magnetics:
    http://www.crmagnetics.com/8300.pdf
    They also have transducers that might do what you need.
    Paul
    Paul E. Schoen, Feb 6, 2007
    #10
  11. On 6 Feb 2007 08:05:44 GMT, in sci.electronics.design jasen
    >> 20 of these.
    snip
    LTC1967 and it is simple, and cheap
    >> sinusoidal value.
    >it sure does.
    >Bye.
    > Jasen
    martin
    martin griffith, Feb 6, 2007
    #11
  12. Tom
    Tom Guest
    Thanks for the info. I still can't justify the overpriced
    transducers. I was looking at analog.com at some of their power
    metering IC's like the ADE7757. Are there other products like this to
    simplify getting the info into some form analog signal or
    communication protocol like RS232?
    > > 20 of these.
    > > resistor.
    > > sinusoidal value.
    > them.
    > Cheers,
    > Tom- Hide quoted text -
    > - Show quoted text -
    Tom, Feb 6, 2007
    #12
  13. Tom
    DaveM Guest
    "jasen" <> wrote in message
    news:eq9cso$fq5$-a-geek.org...
    >> 20 of these.
    >> resistor.
    > And 20 Watts!
    > weighs a
    > few kilograms...
    >> sinusoidal value.
    > it sure does.
    > Bye.
    > Jasen
    You can get the Triad CSE187L current Xfmr from Mouser for $2.47 ea in qty of
    10.
    http://www.mouser.com/search/ProductDetail.aspx?R=CSE187Lvirtualkey55310000virtualkey553-CSE187L
    It has 1:500 turns ratio, current range of 0.1A - 30A. More details at
    http://www.triadmagnetics.com/subcategory/xref.asp?formid2=opart&reference=CSE187L&Submit=SUBMIT
    Dave M
    MasonDG44 at comcast dot net (Just substitute the appropriate characters in the
    address)
    Some days you're the dog, some days the hydrant.
    DaveM, Feb 6, 2007
    #13
  14. Tom
    Tom Bruhns Guest
    > > > 20 of these.
    > > > resistor.
    > > > sinusoidal value.
    > > them.
    > > Cheers,
    If measuring the average absolute value of the waveform is acceptable
    (that is, if you don't need "true RMS"), and if the input resistance
    of the PLC's 0-10V input is high (say >100kohms), there's an easy way
    to do this, and the accuracy will be quite good, even down to currents
    under an amp, for 20A full scale.
    You need to get current transformers (CTs) that can output a fairly
    high voltage--at least 12 volts RMS. Expect these will have a high
    turns ratio. For example, the 2000:1 CR8350-2000 from CR Magnetics
    (thanks, Martin, for the link) should do the job. The catalog page
    lists the effective turns ratio, Te, as 2037:1. We'll be detecting
    the average of the absolute value of the waveform. Assuming it's a
    sine, the average is about 0.900 times the peak (2*sqrt(2)/pi). We'll
    put a resistive load on the CT, such that 20A RMS sinewave in the
    monitored wire results in 10.0V average magnitude across the
    resistor: 10V*2037/(20A*0.900) = 1131 ohms. Actually, we'll make it
    a bit more, and add a way to trim it down to the right value to
    calibrate it: say 1.21k ohms 1%, paralleled with (10k fixed in series
    with a 20k trimmer). We won't connect that load directly to the CT
    output, but rather through a bridge rectifier. There is some
    advantage to using Schottky diodes, but it's minor, and you can just
    as well use 1n4148 or similar silicon diodes. The resistive load goes
    across the bridge output. Since the CT looks like a current source,
    the diode voltage drop is unimportant, so long as it's not so large
    the CT can't put out the voltage. Now we just need to average the
    output; what's across the load is the absolute value of a (nominally)
    sine wave. We could just put a capacitor across the load, but that
    requires the CT output to slew quite a few volts rapidly; better to
    isolate the capacitor with at least a resistor, and even better, an
    inductor. For the very low DC current involved, you can use the
    winding of a small audio transformer to get high inductance, tens of
    henries for a nominal "20k ohm" winding. Then use something like a
    47uF cap at the output to smooth out the voltage. You may want to add
    a little resistance in series with the inductance to reach critical
    damping; then the response of the circuit will be reasonably "crisp"--
    much more so than if you just use a resistor instead of the inductor.
    After construction, calibrate it: put a known 20A through the
    monitored wire, read the voltage on the PLC, adjust the trimpot so it
    reads 10.00V. Now reduce the current to 10A, and make sure the PLC
    reads 5.00V. Check the linearity further by putting in, say, 1A, and
    checking for 0.500V from the PLC. If it's not as linear as you'd
    like, consider applying a calibration in the PLC. But with the
    rectifier connected to the CT and the load to the rectifier output,
    you've removed a significant source of nonlinearity.
    Cheers,
    Tom
    Tom Bruhns, Feb 8, 2007
    #14
    1. Advertisements
Similar Threads
  1. Rob \ the nut \
    120 House Current Volts down to 1.5 volts How?
    Rob \ the nut \, Jun 7, 2004, in forum: Electronic Basics
    7
    1,756
    Rob \ the nut \
    Jun 9, 2004
  2. gmcjetpilot
    8
    2,277
    gmcjetpilot
    Mar 30, 2010
  3. aidan
    low current high voltage (~280 volts) from 6 volts DC
    aidan, Apr 12, 2012, in forum: General Electronics Chat
    523
    aidan
    Apr 13, 2012
  4. cphus
    Conversion from [-10,10]V to [0,5]V range
    cphus, May 1, 2012, in forum: General Electronics Chat
    15
    1,259
    Wabajig
    May 3, 2012
  5. Supercap2F
    Whats the difference -volts and GND (0 volts)
    Supercap2F, Mar 22, 2014, in forum: General Electronics Chat
    18
    666
    Supercap2F
    Mar 24, 2014
Loading...