Soft starting a 1,200 HP 4160 volt motor

 
 
SimonLW
Guest
Posts: n/a
 
      06-20-2005, 02:40 PM
We have a very limited power from the utility. We can run the motor, but
can't start it. This motor turns a very large fan. Is it possible to start
without exceeding the run current? Since it is just a fan, the run-up time
can be longer. Thanks!


 
Reply With Quote
 
 
 
 
SQLit
Guest
Posts: n/a
 
      06-20-2005, 02:48 PM

"SimonLW" <(E-Mail Removed)> wrote in message
news:(E-Mail Removed)...
> We have a very limited power from the utility. We can run the motor, but
> can't start it. This motor turns a very large fan. Is it possible to start
> without exceeding the run current? Since it is just a fan, the run-up time
> can be longer. Thanks!


Sure this is done all of the time. Best check with your motor manufacture
first about this application.
Then call ABB, I have seen more of their medium voltage stuff than anyother
manufacture in this kind of application.

Seems pretty weird that your company would install equipment that they can
not start. Or is this something your looking to buy?


 
Reply With Quote
 
 
 
 
SimonLW
Guest
Posts: n/a
 
      06-20-2005, 03:17 PM
"SQLit" <(E-Mail Removed)> wrote in message
news:9HAte.8$(E-Mail Removed)...
>
> "SimonLW" <(E-Mail Removed)> wrote in message
> news:(E-Mail Removed)...
> > We have a very limited power from the utility. We can run the motor, but
> > can't start it. This motor turns a very large fan. Is it possible to

start
> > without exceeding the run current? Since it is just a fan, the run-up

time
> > can be longer. Thanks!

>
> Sure this is done all of the time. Best check with your motor manufacture
> first about this application.
> Then call ABB, I have seen more of their medium voltage stuff than

anyother
> manufacture in this kind of application.
>
> Seems pretty weird that your company would install equipment that they can
> not start. Or is this something your looking to buy?
>
>

Actually it is a client. It is a fan for a flash dryer and they are limited
by what the utility supplies. They are looking to install this equipment. We
normally don't deal with this aspect of the design.
Thanks -S


 
Reply With Quote
 
SQLit
Guest
Posts: n/a
 
      06-20-2005, 10:24 PM

"SimonLW" <(E-Mail Removed)> wrote in message
news:42b6de38$(E-Mail Removed)...
> "SQLit" <(E-Mail Removed)> wrote in message
> news:9HAte.8$(E-Mail Removed)...
> >
> > "SimonLW" <(E-Mail Removed)> wrote in message
> > news:(E-Mail Removed)...
> > > We have a very limited power from the utility. We can run the motor,

but
> > > can't start it. This motor turns a very large fan. Is it possible to

> start
> > > without exceeding the run current? Since it is just a fan, the run-up

> time
> > > can be longer. Thanks!

> >
> > Sure this is done all of the time. Best check with your motor

manufacture
> > first about this application.
> > Then call ABB, I have seen more of their medium voltage stuff than

> anyother
> > manufacture in this kind of application.
> >
> > Seems pretty weird that your company would install equipment that they

can
> > not start. Or is this something your looking to buy?
> >
> >

> Actually it is a client. It is a fan for a flash dryer and they are

limited
> by what the utility supplies. They are looking to install this equipment.

We
> normally don't deal with this aspect of the design.
> Thanks -S


If they are considering it. Then look into a axial fan and controls. The
motor starts with the fan blades closed so it is almost a "no load" start on
the motor. Then as time progresses the controls can open the blades and load
up the motor. Did this on a 480v 3phase motor for smoke removal. Starting
amps was an issue with the generator.


 
Reply With Quote
 
Brian
Guest
Posts: n/a
 
      06-21-2005, 12:27 AM
Try using a freq drive. That is if the motor will allow the freq change. Works great for chillers.


"SimonLW" <(E-Mail Removed)> wrote in message news:(E-Mail Removed)...
We have a very limited power from the utility. We can run the motor, but
can't start it. This motor turns a very large fan. Is it possible to start
without exceeding the run current? Since it is just a fan, the run-up time
can be longer. Thanks!




 
Reply With Quote
 
operator jay
Guest
Posts: n/a
 
      06-21-2005, 02:24 AM

"Brian" <(E-Mail Removed)> wrote in message
news:O9Jte.49470$oK.30814@okepread02...
> Try using a freq drive. That is if the motor will allow the freq change.

Works great for chillers.
>
>
> "SimonLW" <(E-Mail Removed)> wrote in message

news:(E-Mail Removed)...
> We have a very limited power from the utility. We can run the motor, but
> can't start it. This motor turns a very large fan. Is it possible to start
> without exceeding the run current? Since it is just a fan, the run-up time
> can be longer. Thanks!
>
>
>
>



A huge frequency drive on a high impedance system could give voltage
distortion problems. And maybe even liability problems.

j


 
Reply With Quote
 
SimonLW
Guest
Posts: n/a
 
      06-21-2005, 11:45 AM
"SimonLW" <(E-Mail Removed)> wrote in message
news:(E-Mail Removed)...
> We have a very limited power from the utility. We can run the motor, but
> can't start it. This motor turns a very large fan. Is it possible to start
> without exceeding the run current? Since it is just a fan, the run-up time
> can be longer. Thanks!
>
>

Thanks for all the replies. We looked at VFDs, spinning it up with smaller
motors and even uglier ideas. We finally told the client to talk to the
utility. The problem is the supply to the plant is inadequate and the
utility is complaining about the expense of the miles of wire and equipment
to deliver the power.


 
Reply With Quote
 
Bob
Guest
Posts: n/a
 
      06-29-2005, 03:51 AM
On Tue, 21 Jun 2005 07:45:07 -0400, "SimonLW" <(E-Mail Removed)> wrote:

>"SimonLW" <(E-Mail Removed)> wrote in message
>news:(E-Mail Removed)...
>> We have a very limited power from the utility. We can run the motor, but
>> can't start it. This motor turns a very large fan. Is it possible to start
>> without exceeding the run current? Since it is just a fan, the run-up time
>> can be longer. Thanks!
>>
>>

>Thanks for all the replies. We looked at VFDs, spinning it up with smaller
>motors and even uglier ideas. We finally told the client to talk to the
>utility. The problem is the supply to the plant is inadequate and the
>utility is complaining about the expense of the miles of wire and equipment
>to deliver the power.
>


The utility will most likely not be of much help. They tend to tell
users to either cough up a ton of money to upgrade the feed to their
new system, or they tell them to limit the starting kVA. Along those
lines, there are 3 choices.

1) A VFD, but at 4160V you will be looking at $250,000 by the time it
is all said and done. The advantage: a VFD can start the load at 100%
FLA, and since you alrerady know the system can handle 100% FLA, you
know in advance that the VFD will work.

2) Pony motor starting. This is the suggestion from above wherein you
can use a small motor to get the fan moving, then switch over to the
main motor after it is already spinning. Theoretically it could work,
but when the 4160V motor is connected, there is still a massive inrush
even if the fan is already moving, just smaller by a few percent. This
is very expensive to experiment with only to find out it didn't work!
They also tend to add mecahnical safety issues to the problem.

3) Reduced Voltage Starting. This is what was mentioned above as
either Autotransformer (RVAT) starting or Solid State (RVSS) starting.
In this HP size the RVAT will be slightly cheaper (if you ignore motor
protection issues), but riskier and very big and heavy in comparison.
Risky because again, you are not 100% sure it will work until you try
it. RVSS is going to cost more up front, however most RVSS starters
now come with protection systems comparable to Multilin Relays
built-in, so if you add the cost of that to an RVAT, it comes out
even. The best part is that RVSS manufacturers will often do a
Transient Motor Starting analysis for you for free if you can provide
all the motor, power system and load data to them. I used Motortronics
on 3 projects last year and every one of them came out dead on to the
TMS analysis they did prior to my purchasing them. So I knew in
advance that it would work before I purchased them. On a 4th project,
the utility restrictions were too severe so I had to use a VFD.
Motortronics ran the TMS study for me and told me that any RVSS would
not work, so essentially they lost the order. So at $25,000 each for
the RVSS's and $250,000 for the VFD, I looked at it as though
Motortronics saved me $225,000 each on 3 projects! The Motortronics is
the one sold by ABB as well as mentioned above. The first ones I used
5 years ago came from ABB as part of a package deal, and I would still
go that way again if the project called for it, but when I just wanted
the starters alone, I went directly to the manufacturer.

If you want to get more opinions on this, try logging onto
http://eng-tips.com and go to the Electric Motors and Controls forum
to post a question. Great resource, free as long as you register, and
they DO NOT sell your email address.
 
Reply With Quote
 
SQLit
Guest
Posts: n/a
 
      06-29-2005, 06:49 PM

"Bob" <(E-Mail Removed)> wrote in message
news:(E-Mail Removed)...
> On Tue, 21 Jun 2005 07:45:07 -0400, "SimonLW" <(E-Mail Removed)> wrote:
>
> >"SimonLW" <(E-Mail Removed)> wrote in message
> >news:(E-Mail Removed)...
> >> We have a very limited power from the utility. We can run the motor,

but
> >> can't start it. This motor turns a very large fan. Is it possible to

start
> >> without exceeding the run current? Since it is just a fan, the run-up

time
> >> can be longer. Thanks!
> >>
> >>

> >Thanks for all the replies. We looked at VFDs, spinning it up with

smaller
> >motors and even uglier ideas. We finally told the client to talk to the
> >utility. The problem is the supply to the plant is inadequate and the
> >utility is complaining about the expense of the miles of wire and

equipment
> >to deliver the power.
> >

>
> The utility will most likely not be of much help. They tend to tell
> users to either cough up a ton of money to upgrade the feed to their
> new system, or they tell them to limit the starting kVA. Along those
> lines, there are 3 choices.
>
> 1) A VFD, but at 4160V you will be looking at $250,000 by the time it
> is all said and done. The advantage: a VFD can start the load at 100%
> FLA, and since you alrerady know the system can handle 100% FLA, you
> know in advance that the VFD will work.
>
> 2) Pony motor starting. This is the suggestion from above wherein you
> can use a small motor to get the fan moving, then switch over to the
> main motor after it is already spinning. Theoretically it could work,
> but when the 4160V motor is connected, there is still a massive inrush
> even if the fan is already moving, just smaller by a few percent. This
> is very expensive to experiment with only to find out it didn't work!
> They also tend to add mecahnical safety issues to the problem.
>
> 3) Reduced Voltage Starting. This is what was mentioned above as
> either Autotransformer (RVAT) starting or Solid State (RVSS) starting.
> In this HP size the RVAT will be slightly cheaper (if you ignore motor
> protection issues), but riskier and very big and heavy in comparison.
> Risky because again, you are not 100% sure it will work until you try
> it. RVSS is going to cost more up front, however most RVSS starters
> now come with protection systems comparable to Multilin Relays
> built-in, so if you add the cost of that to an RVAT, it comes out
> even. The best part is that RVSS manufacturers will often do a
> Transient Motor Starting analysis for you for free if you can provide
> all the motor, power system and load data to them. I used Motortronics
> on 3 projects last year and every one of them came out dead on to the
> TMS analysis they did prior to my purchasing them. So I knew in
> advance that it would work before I purchased them. On a 4th project,
> the utility restrictions were too severe so I had to use a VFD.
> Motortronics ran the TMS study for me and told me that any RVSS would
> not work, so essentially they lost the order. So at $25,000 each for
> the RVSS's and $250,000 for the VFD, I looked at it as though
> Motortronics saved me $225,000 each on 3 projects! The Motortronics is
> the one sold by ABB as well as mentioned above. The first ones I used
> 5 years ago came from ABB as part of a package deal, and I would still
> go that way again if the project called for it, but when I just wanted
> the starters alone, I went directly to the manufacturer.
>
> If you want to get more opinions on this, try logging onto
> http://eng-tips.com and go to the Electric Motors and Controls forum
> to post a question. Great resource, free as long as you register, and
> they DO NOT sell your email address.


Reduced voltage starters that I have worked on will not limit the current
much. Starting current values on our 4160 chillers are 3/4 of full load.
'course that could be the operators. I just look at the load data once a
month.

No one ever said that medium voltage was inexpensive.

One other thing that you should be aware of,
Unless the technology has gotten a lot better in the last couple of years.
Medium voltage motor controls really do not like heat. I know of a water
pumping plant in N. Phoenix that has a 10 ton air conditioner sitting on top
of their medium voltage VFD's. In the summer time the room runs constantly
at about 85-90 F. So if your application in in a warm place best check with
the manufacture before going very far. Eaton/Cutler-Hammer used to produce
low voltage VFD's and Softstarts that were rated at 40 C. When I called they
thought I was crazed until I sent the temp information for my desert. We
ended up ducting a/c directly into the bottom of the vfds to keep them
running in the summer months.



 
Reply With Quote
 
operator jay
Guest
Posts: n/a
 
      06-30-2005, 12:58 AM

"SQLit" <(E-Mail Removed)> wrote in message
news:c3Cwe.44$(E-Mail Removed)...
>


>
> Reduced voltage starters that I have worked on will not limit the current
> much. Starting current values on our 4160 chillers are 3/4 of full load.
> 'course that could be the operators. I just look at the load data once a
> month.
>


Across the line starting current is normally given as 600% or so of full
load current. Often soft starters limit current to 300% of full load
current, or maybe 150% of full load. Dropping starting current to 75% of
full load sounds very low. There are instances where this wouldn't even
produce enough torque to get the motor running.

j


 
Reply With Quote
 
 
 
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
'Soft starting' a DC motor djgyro General Electronics Chat 9 05-10-2011 09:21 AM
motor surge current limiting or soft starts Mark Harriss Electronic Design 20 01-08-2007 07:11 AM
can I run a 6 volt motor with a 7.2 or 9.6 volt battery pack? buddy Electronic Design 3 10-14-2006 07:53 PM
Ademco 4160 any one ever see one before? Nick Markowitz Security Alarms 3 03-04-2006 04:07 AM
Is it ok to run a 24 volt trolling motor on a 12 volt battery to test the motor to see if it actually runs? SDNomad General Electronics 5 10-10-2003 05:56 PM