Perrin wrote:
>
> Hi SQLit and Paul Hovnaian P.E.
>
> Thanks to both of you for the speedy answers.
> I hope you don't mind me answering both of your questions in one reply.
>
> The distance of 250m I hate to say is not to the end of the transformer
> run - it still goes on a bit.
> We are not the only household feeding off this transformer - it feeds
> more than eleven houses - not sure how many down a side street. All
> were given 3 phase connections since they needed the higher voltage for
> boreholes long ago before there was a piped water supply (boreholes now
> for garden irrigation).
>
> Where do I live - in good old Johannesburg, South Africa (normally
> sunny, but not this morning ;-)
>
> A geyser I think is called a hot water cylinder in the States (a tank
> of water heated by an electric element - for the household hot water
> supply). It is a single phase load of 3KW, so around 13 amp.
>
> We have a multiple earth neutral system in place - an earth connection
> is made at the service connection, and the neutral and earth of the
> house are connected together at this point. There are also several
> connections to the metal water pipes and an additional earth rod near
> the borehole.
> The neutral from outside to the service box is functioning, and has a
> parallel earth helping to carry current. The clamp of the neutral to
> the overhead cable outside has been replaced last month by City Power
> when I found out that there was no current flowing in the neutral, but
> all flowing back through the parallel earth (checked with clamp
> ammeter). All seems in order.
>
> Load imbalance - it is definitely the neighbours causing this
> imbalance. I have been adjusting the balancing between phases - so far
> we only run pretty much at around 25 to 30 Amp per phase maximum
> (obviously we may go slightly over at times). The service breaker per
> phase is rated 60A (5KA).
> Unfortunately, City Power has not checked to see how unbalanced the
> load is from the transformer.
>
> By the way, I have been looking for a formula to calculate the voltage
> drop that I should be expecting - do either of you have one?
>
> Thanks again for your help - it is much appreciated.
> Regards,
>
> Pierre
I ran a quick calculation from your original post of the drop caused by
a 3 Kw single phase load. The calculation for balanced 3 phase balanced
loads are similar, but there is no current (and no drop) on the neutral.
185mm˛ Aluminum is close to our 350 kcmil Aluminum, which has R = 0.20
ohms/Km
16mm˛ Copper is close to our #6 Cu, which has R = 1.7 ohms/Km
For a 250 m run of 185mm˛ Al plus 60 m of 16mm˛ Cu, R = (0.25)*(0.20) +
(0.06)*(1.7) = 0.152 ohms
per conductor (there are two for single phase, the phase plus the
neutral). A 3 Kw, 230 volt load draws 13 amps.
Vdrop = 2 * (0.152 ohms) * 13 A = 3.95 volts
A guestimate of the transformer bank resistance per phase is about 5 to
10 milliohms, so a 3 Kw (13 A) load adds negligible additional drop.
This is close to what you measured. It wasn't clear if your voltages
were measured at the service entrance or at the water heater, which will
add the drop of the branch circuit to the above figures.
It appears that your 7 volt drop figure may not be too far off from
calculations.
--