Palindr☻me wrote:
> ehsjr wrote:
>
>>
>> Here's the likely cause of the problem: the original installer
>> wired the receptacles by "backstabbing" - stuffing the wire into
>> a hole in the back of the receptacle. That is a legitimate method,
>> but time has shown that circuits wired with that method are far
>> more prone to the kind of failure you describe than circuits where
>> the receptacles are wired by twisting the wire into a loop around
>> a screw, and then tightening the screw.
>>
>>
>> If only part of the circuit is failing, the problem is
>> located at either the last receptacle on the circuit that
>> works, or the first one that fails, like this:
>> ok ok ok F F F
>> panel===[R]===[R]===[R]===[R]===[R]===[R]
>> The defect is here >| | between the lines
>>
>> If the whole circuit is failing, the defect is from the
>> panel to the first receptacle, inclusive.
>>
>> If there are multiple defects, they can be anywhere.
>>
>> Ed
>
>
> It would help, of course, to know the OP's country! None of that you
> ahve written above would apply in the uk. The OP, IIRC, also mentioned
> that the sockets were failing one by one..until several/all stopped
> working.
>
The poster said it's the US in a post on 8/23 at 10:01.
Also said, in the original: > The breaker didn't blow, but eventually
all the plugs
> on the circuit have quit working.
which leads one to think it was a one by one failure.
And that may be true, but otoh I've encountered that
description a number of times, where the description is
wrong. What happens in those cases is that they encounter
a failure in one receptacle (#1), and plug in elsewhere to
receptacle #2. A day or a week or whatever passes, and they
plug into a 3rd receptacle (#3), and it's dead, too. So they
plug in elswhere (receptacle #4). It happens again, with the
same scenario (receptacle #5 bad, and receptacle #6 good, and
they describe the failure to the electrician as one by one
failures, when actually all three receptacles (#'s 1, 3, 5) died
at the same time, but the discovery sequence made it seem
like it was one failure after another. 100% (minus
a very small fraction) of the people do NOT know which
receptacles "belong" to a circuit. If the pattern was known
at the time of the first failure, and if there was a circuit
map showing the odd #'s on one circuit and the even #'s on
another, it's a lot more obvious.
Ed
|